Default Disturbing news from my HVAC guy

An HVAC tech was at my mothers home doing a routine maintenance when his elbow brushed against the ac line. He received a shock and started to investigate. He found the outer casing of the AC was reading 105 VOLTS????

after removing everything giving a load he still could not find out why? but he replaces a single pole lennox a the shut off with a double pole. That seemed to mostly fix the problem. There is still some minor voltage , i think he said 15volts. We dont know why the breaker did not trip. Obviously one of the legs is making contact with something it shouldnt.

Has anyone encountered a similar situation? This guy and another veteran of HVAC were baffled.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
Find an InterNACHI certified California Home Inspector (and anywhere else in North America)
  #2  
Old 10/7/09, 10:41 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Disturbing news from my HVAC guy

Does this compressor have a heater?



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
  #3  
Old 10/7/09, 10:42 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Disturbing news from my HVAC guy

Probably leakage from a conductor in the compressor to the case along with poor bonding of the case to ground. I would also verify proper connections in the panel for this circuits equipment ground.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #4  
Old 10/7/09, 10:51 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: Disturbing news from my HVAC guy

Quote:
Originally Posted by dedwards View Post
Does this compressor have a heater?
nope, just a outdoor ac unit.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #5  
Old 10/7/09, 10:53 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: Disturbing news from my HVAC guy

Quote:
Originally Posted by bking View Post
Probably leakage from a conductor in the compressor to the case along with poor bonding of the case to ground. I would also verify proper connections in the panel for this circuits equipment ground.
The panel is a Wadsworth, I haven't been there to look it over but im still puzzled why it would not trip?




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #6  
Old 10/7/09, 10:57 PM
Andrew Shick's Avatar
Andrew Shick Andrew Shick is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Grain Valley, MO
Posts: 633
Default Re: Disturbing news from my HVAC guy

Quote:
Originally Posted by jtribuzio View Post
The panel is a Wadsworth, I haven't been there to look it over but im still puzzled why it would not trip?
Plastic condensor pad?



“Of liberty I would say that, in the whole plenitude of its extent, it is unobstructed action according to our will. But rightful liberty is unobstructed action according to our will within limits drawn around us by the equal rights of others. I do not add 'within the limits of the law,' because law is often but the tyrant's will, and always so when it violates the right of an individual.” - Thomas Jefferson
Reply With Quote
  #7  
Old 10/7/09, 11:01 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Disturbing news from my HVAC guy

Quote:
Originally Posted by jtribuzio View Post
The panel is a Wadsworth, I haven't been there to look it over but im still puzzled why it would not trip?
Voltage caused by leakage can have very little current capability available but it sounds like a bad breaker trip level could be present also..

Ever notice how a 14/3 or 12/3 cable will have 30-40 volts on the red wire when it is not connected to anything? This is "crosstalk" or simply leakage along the length of the cable from the black wire induced into the red wire. If you put even a very small load on that stray voltage it will disappear.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 10/7/09, 11:28 PM
Joseph Tribuzio's Avatar
Joseph Tribuzio Joseph Tribuzio is offline
InterNACHI Member
 
Join Date: Jul 2007
Location: Harwood Heights, IL 60706
Posts: 708
Default Re: Disturbing news from my HVAC guy

Andrew, YEAH it is on a plastic pad.
Bruce, I'm going to take a closer look at that breaker and the grounding/bonding.
The crosstalk sounds like a factor too.




Joseph Tribuzio 708 453 8447
Tribuzio Home Inspection Services

CHICAGOLAND, ILLINOIS
www.thishomeinspector.com

ID# NACHI07062507

IL Lic#450.003128

Radon lic# RNIT2008216
Home Inspector Pro Software

HIP Web Hosting


Reply With Quote
  #9  
Old 10/8/09, 7:23 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,226
Default Re: Disturbing news from my HVAC guy

Check the ground rod also
Reply With Quote
  #10  
Old 10/8/09, 7:37 AM
rcook1 rcook1 is offline
InterNACHI Member
 
Join Date: Oct 2008
Posts: 7
Default Re: Disturbing news from my HVAC guy

Check to see if the capaciter is not starting to short out.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inspecting Furnaces. Please proof this new inspection article. gromicko Inspecting HVAC Systems 4 9/15/09 9:54 PM
Bad News--Good News jwilliams4 Miscellaneous Discussion for Inspectors 27 8/21/09 11:29 AM
Access to Electrical Panel in Ontario by HVAC Contractors Nalliah Thayabharan Canadian Inspectors 10 5/21/07 3:01 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM


All times are GMT -4. The time now is 6:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts