Default How does the furnace work?

My furnace works like this: Burners come on, then blower comes on. They stay on until it makes my thermostat setting, say 74.

On some inspections, the furnace does this: the burners come on, then the blower, but after a few minutes the burners go off and the blower stays running. It continues this way until it reaches the set temp. This is on old furnaces.

My question is: Is this a case of "short cycling", or on old furnaces is this the way they were designed to run?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 11/28/06, 10:19 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: How does the furnace work?

An indication of short cycling is if the burner comes on, blower comes on, the burner goes off, the blower stays on, burner comes back on again, burner goes back off again, blower keeps running. It may or may not reach set point.
Reply With Quote
  #3  
Old 11/28/06, 10:22 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 2,834
David A. Andersen .
Default Re: How does the furnace work?

The older version furnace, has a bimetal fan/limit control that heats up and turns on the blower. When the burner shuts off when the thermostat reaches set point, the blower remains on until the heat exchanger where the fans/limit control is installed, cools down. This has a "purge" affect, which is a desirable function and is incorporated even in electronically controlled blower controllers.
Reply With Quote
Old 11/28/06, 10:25 AM
Michael R. Boyett
This message has been deleted by mboyett.
  #4  
Old 11/28/06, 11:38 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 444
Greg Veal is generally well trusted
Default Re: How does the furnace work?

Mark,

There are various scenerio's for what you are describing.
David gave a good explanation on (2) coun

I think Equipment age, maintenance, visible condition, location, and type (ie: Gas, Electric, Ht.Pump, H.W./Steam, etc.) all play a part in the final analysis by the Pro.

I think you list your observations and recommend further analysis by a Pro.
Reply With Quote
  #5  
Old 11/28/06, 12:57 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is online now
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,319
Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted Bruce M. Graham, III is well trusted
Default Re: How does the furnace work?

If it has an older tstat, the anticapater may not be set causing the short cycle.



Bungalows to Mansions
Professional Inspection Services, LLC
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
NACHI05091592
ICC 5268478
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 11/28/06, 1:28 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,403
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: How does the furnace work?

A couple of thoughts to add.

1. This may or not be a real problem but some troubleshooting is in order.

2. The plenunm control may be misadjusted and set too low.

3. The air flow could be restricted by a clogged filter, clogged A-coil or the registers and any damperes not open alowing the plenumn temp to rise to the limit of the control.

4. The blower may not be at the cottect speed for the application by malfuction or blwoer speed setting.

4. An oversized furnace may also short cycle.
Reply With Quote
  #7  
Old 11/28/06, 4:07 PM
Robert J. OConnor, P.E.'s Avatar
Robert J. OConnor, P.E. Robert J. OConnor, P.E. is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 739
Robert J. OConnor, P.E. is often very helpful Robert J. OConnor, P.E. is often very helpful
Default Re: How does the furnace work?

Quote:
Originally Posted by mtimpani
On some inspections, the furnace does this: the burners come on, then the blower, but after a few minutes the burners go off and the blower stays running. It continues this way until it reaches the set temp. This is on old furnaces.
Older and lower efficiency systems will run the blower for a while after the system satisfies the T-stat to purge as previously indicated.

Do you turn the T-stat all the way up, so that it should run for quite a while before the T-stat is satisfied, or do you just turn it up enough to fire the heating system?

I would turn the T-stat all the way up, so the system should run for quite a while before reaching the set point (and bake the people inside so they remember the heat was working "at the time of the inspection") ...

JMO



Robert O'Connor, PE
Eagle Engineering & Inspections
Adjunct Professor
NACHI Education Committee
www.reporthost.com/eagleengineering

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #8  
Old 11/29/06, 9:52 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,413
Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful
Default Re: How does the furnace work?

All the way up...




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #9  
Old 11/29/06, 11:05 AM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,301
Richard L. Bennett .
Default Re: How does the furnace work?

All the above could be the cause

Number one in my book is a dirty air filter

Lack of air through the heat exchanger will cause the hi temp safety to shut down the gas

rlb
Reply With Quote
  #10  
Old 11/30/06, 8:51 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,413
Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful
Default Re: How does the furnace work?

So it is short cycling ? The older furnaces were not set up to run that way correct?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #11  
Old 11/30/06, 9:49 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI
Posts: 12,403
Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute Michael Larson has a reputation beyond repute
Default Re: How does the furnace work?

Quote:
Originally Posted by mtimpani
So it is short cycling ? The older furnaces were not set up to run that way correct?
Mark,

We just can't tell from here.

Please review the following links for tips on this issue.

http://toad.net/~jsmeenen/anticipator.html

http://www.rd.com/content/openConten...ontentId=18229

http://www.hvacoracle.com/cgi-bin/pu...=133&s=heating

http://masterplumber.net/Furnace_Questions.htm

Hope this helps, good luck and be careful.

Of course you could always refer to a quaified HVAC techincian for evaluation and repair as needed.
Reply With Quote
  #12  
Old 11/30/06, 6:30 PM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 347
Darrell B. Hadler is generally well trusted
Default Re: How does the furnace work?

Mark, if you turn the stat up all the way and the flame shuts off before it reaches its designated temp. I will always consider that short cycling and recommend servicing. I ususally check the filter first, try removing it and to see if that corrects the problem or not. Some of the high end filters will even restrict the air flow enough to cause this, even if they are clean.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!

Last edited by dhadler; 11/30/06 at 6:33 PM.
Reply With Quote
  #13  
Old 12/1/06, 10:11 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,413
Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful Mark A. Timpani is almost always very helpful
Default Re: How does the furnace work?

Thank you Darrell, very concise and to the point.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Not Responding vsantos HVAC 4 9/18/07 9:00 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph HVAC 2 6/6/07 3:56 PM
Correct connect at Furnace tmartens Plumbing 2 5/1/07 10:33 PM


All times are GMT -4. The time now is 5:34 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics