Does this Heater vent need a heat collar?

http://i187.photobucket.com/albums/x296/dawlita/Nachi/chris197.jpg

http://i187.photobucket.com/albums/x296/dawlita/Nachi/chris198.jpg

Yes, a ceiling support/firestop and insulation dam (if attic) is needed.

Example: http://www.cciccweb.org/files/duravent_bventmanual-2-25-08.pdf

Thanks for the info and link.

If it’s a single wall vent it needs a vent thimble (heat collar). Double wall vent can be installed either with a thimble or with adequate clearances to combustibles without a thimble.