Default Does this scare you

For those that just operate a electric furnace from its thermostat this is not as dangerous as removing the dead front on a electric panel especially a FP panel. Looks like a mess of wiring but it is basically very simple four elements in this furnace denoted by the yellow thermal overloads. I have harped on this many times but again the only way to determine if all 4 elements are operating is to use a amp meter on each element.

OMG here comes the SOP guys
Attached Thumbnails
does-scare-you-28-old-post-rd-enid-3-15-11-062.jpg   does-scare-you-28-old-post-rd-enid-3-15-11-063.jpg   does-scare-you-28-old-post-rd-enid-3-15-11-064.jpg   does-scare-you-28-old-post-rd-enid-3-15-11-065.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/25/11, 8:40 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Does this scare you

Quote:
Originally Posted by cbottger View Post
For those that just operate a electric furnace from its thermostat this is not as dangerous as removing the dead front on a electric panel especially a FP panel. Looks like a mess of wiring but it is basically very simple four elements in this furnace denoted by the yellow thermal overloads. I have harped on this many times but again the only way to determine if all 4 elements are operating is to use a amp meter on each element.

OMG here comes the SOP guys
Don't the have a HVAC Repairman MB where you post this stuff Charley?
Reply With Quote
  #3  
Old 3/25/11, 11:38 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Does this scare you

Quote:
Originally Posted by bkelly2 View Post
Don't the have a HVAC Repairman MB where you post this stuff Charley?
Nope was not repairing was operating is that not what a HI is suppose to do or do they just use the SWAG system in AZ



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 3/26/11, 12:00 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Does this scare you

Quote:
Originally Posted by cbottger View Post
For those that just operate a electric furnace from its thermostat this is not as dangerous as removing the dead front on a electric panel especially a FP panel. Looks like a mess of wiring but it is basically very simple four elements in this furnace denoted by the yellow thermal overloads. I have harped on this many times but again the only way to determine if all 4 elements are operating is to use a amp meter on each element.

OMG here comes the SOP guys
So they all have bright yellow stickers have 4 elements and carry 21 amp draws.
Great, I will do this check every time.Never knew it was so simple.
Reply With Quote
  #5  
Old 3/26/11, 12:07 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Does this scare you

Quote:
Originally Posted by belliott View Post
So they all have bright yellow stickers have 4 elements and carry 21 amp draws.
Great, I will do this check every time.Never knew it was so simple.
No its like painting by numbers simple yes



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #6  
Old 3/26/11, 12:45 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Does this scare you

Quote:
Originally Posted by cbottger View Post
No its like painting by numbers simple yes
What happens when the amp draw is unbalanced and by how much is where I have a problem Charlie.
Reply With Quote
  #7  
Old 3/26/11, 6:46 AM
ROBERT V. YOUNG's Avatar
ROBERT V. YOUNG ROBERT V. YOUNG is online now
InterNACHI Member
 
Join Date: Mar 2010
Location: Montreal.
Posts: 5,050
Default Re: Does this scare you

Great point BOB.
More of those units coming into Montreal area with energy retro fitting and Hydro Quebec being a clean source of energy.
What about drop testing.
Pro's, con's of stay away no need ?
Dam more and more reason to buy an IR camera.



montrealbuildinginspectionservice.com
montreal-home-inspection-services.com
home-inspections-montreal.com
homeinspectionsservicesmontreal.com
ROBERT YOUNG'S MONTREAL HOME INSPECTION SERVICE INC.
Certified Inspecteur Professionnel Certifié en Bâtiment membre de InterNACHI ACHI , Chapters - OntarioAchi et du M.I.C.Q (CPI) - (CHI)
OFFICE (514) 489-1887 MOBILE (514) 441-3732 TOLL FREE 1- 855-819-1816
Reply With Quote
  #8  
Old 3/26/11, 8:24 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Does this scare you

How long does it take to do this on a furnace .
What % have a burned out element .

I am an retired Electrician and no longer check elements .
I found very few burned out and the times spent was not worth the effort.
If a client was to call about a burned out element I missed
( Never happened yet ) I will pay to get it fixed .



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #9  
Old 3/26/11, 8:52 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Does this scare you

Quote:
Originally Posted by belliott View Post
What happens when the amp draw is unbalanced and by how much is where I have a problem Charlie.
Bob mostly find 10 KW and 15 Kw heat strips a 15 kw strip pulls 20 to 21 amps every time. I don't concern myself with a unbalanced load specifically as that would generally be a loose connection with burnt wire which is very visible. I look for open circuits no amps is the most common problem. If the thermostat is cranked up several degrees to ensure the second stage heat is energized all elements should have a amp draw and they will read basically the same



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 3/26/11, 9:20 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Does this scare you

Quote:
Originally Posted by rcooke View Post
How long does it take to do this on a furnace .
What % have a burned out element .

I am an retired Electrician and no longer check elements .
I found very few burned out and the times spent was not worth the effort.
If a client was to call about a burned out element I missed
( Never happened yet ) I will pay to get it fixed .
Roy it takes me no longer than 5 minutes or less to check the amp draw on a furnace the one in the pic had 6 screws the same amount as a 200 amp dead front. I don't work on % one is to many I can understand as a electrician you did not find many, most people call a HVAC Tech for a electric furnace that was not heating not a electrician. I can very well understand you not getting a call about one missed element that was not operating because the home owner would not know it was not operating they would not know anything was amiss until all 4 elements stopped operating. That is not my point when I leave a job I know all the elements are performing as intended. I don't see a large amount of electric furnaces down here this is oil and gas country and natural gas is by far the name of the game.

Roy I have been in this business a long time and have built a very profitable business by being a perfectionist doing what others don't. You don't see me on this board whining about Lowballers whining about licensing whining about everything under the sun. I am out doing inspections not whining about crap on this MB



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 3/26/11, 10:17 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Does this scare you

Still good info even if I may or may not do this check as I see few Electrical units and they are mainly in a handful of condo units a year so far for me.
Reply With Quote
  #12  
Old 3/26/11, 11:50 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is online now
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 8,234
Default Re: Does this scare you

would it not be as easy to take a reading at the panel?



Wayne Wilson
East TN Home Inspections LLC
Knoxville, Oak Ridge, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.
865-256-1490

http://site.myhomeinspection.net

Reply With Quote
  #13  
Old 3/26/11, 12:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Does this scare you

Quote:
Originally Posted by wwilson3 View Post
would it not be as easy to take a reading at the panel?
Yes if you knew how many elements were in use only kicker is one would not know which one was not working if the amps did not match up with the amount of elements. Plus I like to do a visual on the wiring in general inside the cabinet. More room in the furnace to get the amp meter on than most main panels just they way I prefer to do things



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in North Carolina? Check out InterNACHI's listing of North Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 3/26/11, 6:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Does this scare you

Quote:
Originally Posted by wwilson3 View Post
would it not be as easy to take a reading at the panel?
Hmmm,smart guy.(pick two)yeyeye.PlUcK
Reply With Quote
  #15  
Old 3/26/11, 6:13 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,569
Default Re: Does this scare you

doesn't anybody use the lick test anymore?



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Scare Tactics for Licensing in Ontario acavdek Canadian Inspectors 54 11/23/09 11:07 PM
Obama says we'll be "allowed" to keep our insurance. Allowed? Huh? gromicko Miscellaneous Discussion for Inspectors 4 6/27/09 11:41 PM
Why Obama is scary... jwilliams4 Miscellaneous Discussion for Inspectors 54 6/21/09 7:20 PM


All times are GMT -4. The time now is 11:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts