Default domestic hot water also providing heat?

domestic-hot-water-also-providing-heat-pex-piping-2nd-floor-bathroom-intended-heat.jpgThis is new to me: Found hot and cold water lines from basement (tapped in area of oil-fired water heater) run to 2nd story bathroom with PEX tubing. The two lines were connected together "temporarily," with the intention of using them to feed and return from a baseboard heater for the bathroom(heater not present). No circulator present, or allowed for. The real question for me- is it appropriate to use domestic hot water for space heat? This is not an isolated loop, the water used for heat is the same water that would be used bathing, dish washing etc. I know it can't work without a circulator, but the whole idea doesn't seem right to me. All opinions are welcome.



Wendell F. Cook
271 Washington Blvd.
Hudson, NY 12534
518-828-0191
www.homeinspectionshudson.com
wfchomeinspections@verizon.net
Secretary, New York Capital Region Chapter of NACHI
Instructor, C.A.T.S. of Albany Home Inspection School

"Life is what happens to you while you're busy making other plans." John Lennon
Reply With Quote
Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America)
  #2  
Old 9/24/09, 4:37 PM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,021
Default Re: domestic hot water also providing heat?

How big (gallons) is the water heater?

If it's just one baseboard, there would need to be some sort of zone control installed on this particular supply line in order to circulate the heated water.

I don't see an issue with this as long as it is only one baseboard supply. An electric baseboard would have worked just as well.
Reply With Quote
  #3  
Old 9/24/09, 4:40 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 930
Default Re: domestic hot water also providing heat?

Im by no means an expert on this, but I wouldnt recommend it. I dont see it as a health hazard, as long as there is no openings in the system. Have the pipes EVER been used for anything other than potable water? Circulation will happen as long as there is an up and down pipe, and it will distribute some heat, inefficiently.


David beat me...
Reply With Quote
  #4  
Old 9/24/09, 4:45 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,826
Send a message via AIM to sstanczyk
Default Re: domestic hot water also providing heat?

That almost looks like PB instead of PEX. Where were these stubbed out in the bathroom? I have a similar set up but it is just a loop for heated towel rods and not a baseboard unit.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #5  
Old 9/24/09, 4:49 PM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,021
Default Re: domestic hot water also providing heat?

Quote:
Originally Posted by sstanczyk View Post
That almost looks like PB instead of PEX. Where were these stubbed out in the bathroom? I have a similar set up but it is just a loop for heated towel rods and not a baseboard unit.

PB? oh oh.....
Reply With Quote
  #6  
Old 9/26/09, 2:44 AM
C. Scott Justason C. Scott Justason is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Rowley, Iowa
Posts: 172
Default Re: domestic hot water also providing heat?

u sure u wernt looking at a domestic hw recirc loop? Any body runs pex for heating loop is off.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need Help On Chimney Liners Nick Scibetta Exterior 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 6:53 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts