I know that I have run across this before and never thought about it, but yesterday I ran across 3 draft fan induced furnaces and a gravity vent water heater connected to the same flue. The flue size looked OK (was bigger at each connection). It got me thinking though, that couldn't the draft fans cause a back draft at the water heater draft diverter. I don't recall ever hearing that you cannot connect both kinds to the same flue.
P1027511.JPG Thanks "An expert is a person who has made all the mistakes that can be made in a very narrow field" Niels Bohr "Learn all you can from the mistakes of others. You won't have time to make them all yourself" Alfred Sheinwold
|
|
#2
|
||||
|
||||
|
Gravity vented appliances and induced-vent appliances can share the same flue system.
|
|
#3
|
||||
|
||||
|
Shouldn't the smallest appliance (water heater) be "above" the others? This one seems to be "after" the others, but not "above" them. I'm not arguing the point, because I don't know, but it does look like the furnaces could push their exhaust down to the water heater.
|
|
#4
|
||||
|
||||
|
As long as the appropriate fittings are used, and the vents are sized and sloped properly, there's not an issue.
|
|
#5
|
||||
|
||||
|
Jeff,
Do you know what the proper slope should be? I don't recall. M. |
|
#6
|
||||
|
||||
|
1/4 inch per foot minimum rise. . .
|
|
#7
|
||||
|
||||
|
Did you check for back drafting?
The flue pipe must be the diameter of the largest appliance plus 50% of the other attached appliances. I don't like the looks of galvanized gas pipe or the extension cord power supplies to the furnaces that are not protected. Or the number of unsupported fittings in the flue configuration. |
|
#8
|
||||
|
||||
|
Every one of the furnaces also had flexible hose through the enclosure too.
I did check for any obvious back drafting at the water heater when at least two of the furnaces were running. Thanks for the replies. "An expert is a person who has made all the mistakes that can be made in a very narrow field" Niels Bohr "Learn all you can from the mistakes of others. You won't have time to make them all yourself" Alfred Sheinwold
|
![]() |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Air admittance valves everywhere | apfaff | Plumbing | 13 | 4/16/07 10:17 AM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Misc. Discussion | 8 | 1/25/07 6:22 PM |
| Direct vent WH with draft hood | dpeterson | Plumbing | 9 | 12/30/06 4:35 PM |
| Gravity vent | dmacy | Plumbing | 5 | 8/1/06 2:47 PM |