Default Draft fan & gravity vent

I know that I have run across this before and never thought about it, but yesterday I ran across 3 draft fan induced furnaces and a gravity vent water heater connected to the same flue. The flue size looked OK (was bigger at each connection). It got me thinking though, that couldn't the draft fans cause a back draft at the water heater draft diverter. I don't recall ever hearing that you cannot connect both kinds to the same flue.

draft-fan-and-gravity-vent-p1027511.jpg

Thanks
Reply With Quote
  #2  
Old 1/3/08, 12:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Draft fan & gravity vent

Gravity vented appliances and induced-vent appliances can share the same flue system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/3/08, 12:53 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Draft fan & gravity vent

Shouldn't the smallest appliance (water heater) be "above" the others? This one seems to be "after" the others, but not "above" them. I'm not arguing the point, because I don't know, but it does look like the furnaces could push their exhaust down to the water heater.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #4  
Old 1/3/08, 1:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Draft fan & gravity vent

As long as the appropriate fittings are used, and the vents are sized and sloped properly, there's not an issue.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/3/08, 1:28 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Draft fan & gravity vent

Jeff,
Do you know what the proper slope should be? I don't recall.
M.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #6  
Old 1/3/08, 2:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Draft fan & gravity vent

1/4 inch per foot minimum rise. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 1/4/08, 12:41 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Draft fan & gravity vent

Did you check for back drafting?

The flue pipe must be the diameter of the largest appliance plus 50% of the other attached appliances.

I don't like the looks of galvanized gas pipe or the extension cord power supplies to the furnaces that are not protected. Or the number of unsupported fittings in the flue configuration.
Reply With Quote
  #8  
Old 1/4/08, 8:19 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Draft fan & gravity vent

Every one of the furnaces also had flexible hose through the enclosure too.

I did check for any obvious back drafting at the water heater when at least two of the furnaces were running.

Thanks for the replies.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 9:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Direct vent WH with draft hood dpeterson Plumbing Inspections 9 12/30/06 3:35 PM
Gravity vent dmacy Plumbing Inspections 5 8/1/06 1:47 PM


All times are GMT -4. The time now is 6:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts