Do you consider this dryer vent a problem. I reported that this unsupported duct dipping down could collect lint and possibly become clogged. And that a clogged vent line would restrict the air flow from the dryer and if was restricted bad enough that it could possibly cause a dryer fire.
The seller had a local building inspector look at this and he told them that is was not a problem. I just felt that this vent line should be supported or replaced with a metal duct to prevent it from dipping. Is this a problem worth reporting?
Attached Images
File Type: jpg DSCN0188.JPG (60.2 KB, 74 views)
Reply With Quote
  #2  
Old 11/29/06, 1:20 PM
Henry Valenzano, CMI's Avatar
Henry Valenzano, CMI Henry Valenzano, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Colorado Springs, CO
Posts: 1,517
Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information
Send a message via MSN to hvalenzano
Default Re: Dryer vent

you did your job. if they ever have a problem in the future they can go back on the building inspector and not you



Henry Valenzano CMI (Hank)
Double Check Home Inspection LLC.
Membership Development Director
Master Inspector Certification Board
www.DCHI.com
Hank@DCHI.com
719-635-6425

The Inspector's Forum :New name same quality CMI educational classes.
http://www.certifiedmaster.com/forum/index.php
Reply With Quote
  #3  
Old 11/29/06, 1:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 3,991
Jeffrey R. Pope .
Default Re: Dryer vent

Yes, it's a problem and a potential fire hazard.

Is this a concealed space (crawlspace)? If so, building codes do not allow this type of duct in concealed spaces.

Absolutely call this out as a potential fire hazard, regardless of where it is. I don't believe a building inspector ever saw this and said it was okay.



Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
http://www.MyInspector.net
Reply With Quote
  #4  
Old 11/29/06, 1:32 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,844
phinsperger is almost always very helpful phinsperger is almost always very helpful phinsperger is almost always very helpful phinsperger is almost always very helpful phinsperger is almost always very helpful phinsperger is almost always very helpful
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vent

With something like 20,000 dryer related fires each year I would bet that some of them were due to vents such as you have there.
Reply With Quote
  #5  
Old 11/29/06, 3:28 PM
Matthew M. Berman Matthew M. Berman is offline
New User
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 68
Matthew M. Berman hasn't had much positive or negative feedback
Default Re: Dryer vent

I recommend smooth metal pipe,no screws at joints and well supported.Matt.
Reply With Quote
  #6  
Old 11/29/06, 8:01 PM
jinvernizzi jinvernizzi is offline
New User
 
Join Date: Jun 2006
Location: Washington, PA
Posts: 33
jinvernizzi hasn't had much positive or negative feedback
Please Note: jinvernizzi is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Dryer vent

Is that non-metallic (plastic or vinyl) flex duct?

If it is, does the dryer manufacturer state that it is OK to use this? I've seen instructions (statements) on dryers that state the warranty is void if anything other than metal is used.
Reply With Quote
  #7  
Old 11/29/06, 11:12 PM
Henry Valenzano, CMI's Avatar
Henry Valenzano, CMI Henry Valenzano, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Colorado Springs, CO
Posts: 1,517
Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information Henry Valenzano, CMI is very trusted source of information
Send a message via MSN to hvalenzano
Default Re: Dryer vent

On the new LG steam unites they are requires to have a mechanical 90 off the back or the warranty is void.



Henry Valenzano CMI (Hank)
Double Check Home Inspection LLC.
Membership Development Director
Master Inspector Certification Board
www.DCHI.com
Hank@DCHI.com
719-635-6425

The Inspector's Forum :New name same quality CMI educational classes.
http://www.certifiedmaster.com/forum/index.php
Reply With Quote
  #8  
Old 11/29/06, 11:29 PM
Joe D. Funderburk's Avatar
Joe D. Funderburk Joe D. Funderburk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Rock Hill, SC
Posts: 2,087
Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information Joe D. Funderburk is very trusted source of information
Send a message via Yahoo to jfunderburk
Default Re: Dryer vent

"The dryer vent in the crawl space was corrugated, flexible ducting. Today's standards for new construction specify that corrugated pipe may be used only within the first 8 feet and may not be concealed within construction. The concealed ducts should be rigid metal ducts or equivalent, vented to the exterior of the home. This is recommended for fire safety reasons."



Joe Funderburk
Alpha & Omega Home Inspections, LLC
Hickory Grove, SC
NACHI ID: NACHI05120170
www.aohomeinspection.com
Reply With Quote
  #9  
Old 11/30/06, 11:21 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Dryer vent

I'm in full agreement with Jeff.

Quote:
Originally Posted by jfunderburk
"The dryer vent in the crawl space was corrugated, flexible ducting.
Add "plastic" to that (i.e., plastic corrugated, flexible ducting). Plastic is even worse than metal cor-flex.



  • Need a positive networking site? Click here to join Active Rain, a networking community of 125,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #10  
Old 11/30/06, 11:39 AM
Robert J. OConnor, P.E.'s Avatar
Robert J. OConnor, P.E. Robert J. OConnor, P.E. is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 739
Robert J. OConnor, P.E. is often very helpful Robert J. OConnor, P.E. is often very helpful
Default Re: Dryer vent

Quote:
Originally Posted by jfunderburk
"The dryer vent in the crawl space was corrugated, flexible ducting. Today's standards for new construction specify that corrugated pipe may be used only within the first 8 feet and may not be concealed within construction. The concealed ducts should be rigid metal ducts or equivalent, vented to the exterior of the home. This is recommended for fire safety reasons."
Quote:
Originally Posted by rray
Add "plastic" to that (i.e., plastic corrugated, flexible ducting). Plastic is even worse than metal cor-flex.
I completely agree with both of those statements. Poor dryer exhausts is a common cause of fires.

Also add that it needs to be smooth inside metal duct, with joints in the direction of flow, and no protruding sheet metal screws.

Check out this classic one on a brand new +$1,000,000 home ...

.
Attached Images
File Type: jpg DryerDuct-NG.JPG (53.6 KB, 65 views)



Robert O'Connor, PE
Eagle Engineering & Inspections
Adjunct Professor
NACHI Education Committee
www.reporthost.com/eagleengineering

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 11/30/06 at 11:45 AM.
Reply With Quote
  #11  
Old 11/30/06, 12:08 PM
Brian R. Sumpter Brian R. Sumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 234
Brian R. Sumpter has had a little positive feedback
Default Re: Dryer vent

How is this amalgam for a narrative?:

Quote:
The dryer vent in the crawl space was corrugated, flexible ducting. Today's standards for new construction specify that corrugated pipe may be used only within the first 8 feet and may not be concealed within construction and this is recommended for fire safety reasons. The concealed ducts should be rigid metal ducts or equivalent, vented to the exterior of the home. First Call Home Inspections recommends smooth metal pipe, with no screws at joints and well supported.

It has been reported that there are approximately 20,000 dryer related fires each year due to use of unapproved materials and poor connection techniques.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #12  
Old 12/1/06, 7:21 AM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,332
William E. Siegel is often very helpful William E. Siegel is often very helpful
Default Re: Dryer vent

Underwriters Laboratories standards 560 and 2158 for clothes dryers require that all dryers listed must specify all metal dryer venting unless otherwise tested. A UL 181 label does not apply to dryer venting. Underwriters Laboratories Inc., an independent testing agency that helps set national safety standards, requires that dryer manufacturers
"include explicit instructions specifying that only rigid or flexible metal duct should be used for exhausting, unless the appliance has been investigated for use with nonmetallic duct."


Maytag and other major dryer manufacturers recommend against the use of plastic flexible duct.
Although plastic flexible duct (cheap and easy to install) might seem like just the thing for exhausting a dryer, it isn't. This type of exhaust duct, which resembles a plastic-covered slinky toy, is not recommended for several reasons.


The Consumer Products Safety Commission estimates there are 24,000 clothes dryer fires each year in the United States, amounting to $96,000,000 in estimated property damage. Lack of maintenance is the leading cause of dryer fires, and LINT is the leading material to ignite. These fires can be caused by failure of mechanical and/or electrical parts within the dryer itself, improper materials being put into the dryer, and insufficient airflow as a result of improper installation.
Clothes dryers can be a source of home fires. Be sure to check your dryer vent and vent hose regularly for lint accumulation. Lint is an excellent source of ignition for a fire. Vents should be made of rigid metal, because flexible vents can be damaged by heat, age and contact with other objects. All vents need to discharge directly to the home’s exterior.
SAFE USE OF HOUSEHOLD CLOTHES DRYERS
  • North American-style household clothes dryers are required by manufacturers to be vented to the outdoors using a short length of rigid or flexible metal ducting. Manufacturers recommend that the maximum length of the metal ducting, which varies depending on the number of bends, should not be exceeded. This is clearly stated in the manufacturers installation instructions and the appliances are certified according to this requirement.
  • It is strongly recommended that plastic ducting not be used. Plastic ducts often collapse causing blockage and lint build up within the dryer. This type of plastic ducting can ignite or melt and will not contain a fire within the dryer
Reply With Quote
  #13  
Old 12/3/06, 2:13 PM
Keith Swift, PhD. Keith Swift, PhD. is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Northridge, CA
Posts: 1,372
Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information Keith Swift, PhD. is very trusted source of information
Default Re: Dryer vent

The following narrative, prints automatically in all of my reports. (Of course, I can turn it off when necessary).
Faulty dryer vents have been responsible for thousands of fires, hundreds of injuries, and even deaths. The best vents are a smooth-walled metal type that travels a short distance; all other types should be regarded as suspect, and should be inspected bi-annually to ensure that they do not contain trapped lint or moisture.
Regardless, I identify and comment on very dryer vent, including where it discharges.




InterNACHI Vice President, InterNACHI Editor-in-Chief, co-founder CalNACHI

Reply With Quote
  #14  
Old 12/3/06, 2:53 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 15,860
Russel Ray .
Default Re: Dryer vent

Quote:
Originally Posted by kswift
The following narrative, prints automatically in all of my reports. (Of course, I can turn it off when necessary).
Faulty dryer vents have been responsible for thousands of fires, hundreds of injuries, and even deaths. The best vents are a smooth-walled metal type that travels a short distance; all other types should be regarded as suspect, and should be inspected bi-annually to ensure that they do not contain trapped lint or moisture.
Regardless, I identify and comment on very dryer vent, including where it discharges.
I like it, but I would probably rewrite the first sentence thusly so that you don't have to check on the statistics and change "hundreds of injuries" to "thousands of injuries" when the time comes (think McDonalds--no longer is it "84 billion hamburgers served"--just "billions of hamburgers served"):

Faulty dryer vents and improper installations have been responsible for fires, injuries, and deaths in our homes.

Or something like that.



  • Need a positive networking site? Click here to join Active Rain, a networking community of 125,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #15  
Old 12/3/06, 6:07 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 9,699
Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute
Default Re: Dryer vent

A few things to know;

http://fixitnow.com/appliantology/dr...t_ultimate.htm

http://www.cpsc.gov/CPSCPUB/PUBS/5022.html

http://www.dryerbox.com/dryer_venting_guide.htm

http://www.diynetwork.com/diy/ha_ins...277638,00.html

Marcel



Cyr Home Inspections
IAC2 Certified
NACHI04070211

http://co.nachi.org/inachiawards/inachiawards551.html
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On