Default Dryer vent

Should the dryer vent that passes through an attic be insulated in an unconditioned space? Can you see the condensation line in the insulation?

Thanks!
Attached Thumbnails
dryer-vent-100_7127.jpg   dryer-vent-100_7131.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
Find an InterNACHI certified Georgia Home Inspector (and anywhere else in North America)
  #2  
Old 7/27/09, 7:36 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Dryer vent

Yes, exactly for the reason you stated.
Reply With Quote
  #3  
Old 7/27/09, 7:38 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Dryer vent

No need to insulate a dryer vent.

Is that penetrating the roof surface? If so, the shingles must be full of lint.

I like to see these penetrating the soffit area.

Reply With Quote
  #4  
Old 7/27/09, 8:14 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Dryer vent

The dryer vent is on the roof. I think the other problem is not enough attic ventilation. The only vents noted where roof vents, no gable or soffit vents.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #5  
Old 7/27/09, 8:48 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Dryer vent

Quote:
Originally Posted by dvalley View Post
No need to insulate a dryer vent.

Is that penetrating the roof surface? If so, the shingles must be full of lint.

I like to see these penetrating the soffit area.
Funny, I would write that one up as improper if I saw it used as dryer vent. Improper vent material (supposed to be smooth, not corrugated) and the termination should not have a screen. Also the vent material looks like it would require inside / out assembly (i.e., downstream piece inside rather than outside the upstream piece).



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #6  
Old 7/27/09, 10:08 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Dryer vent

Quote:
Originally Posted by dvalley View Post


I like to see these penetrating the soffit area.

"M1502.2 Duct termination. Exhaust ducts shall terminate on
the outside of the building. Exhaust duct terminations shall be
in accordance with the dryer manufacturer’s installation
instructions. Exhaust ducts shall terminate not less than 3 feet
(914 mm) in any direction from openings into buildings.
Exhaust duct terminations shall be equipped with a backdraft
damper. Screens shall not be installed at the duct termination."



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 7/27/09, 11:01 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Dryer vent

Quote:
Originally Posted by cevans View Post
Funny, I would write that one up as improper if I saw it used as dryer vent. Improper vent material (supposed to be smooth, not corrugated) and the termination should not have a screen. Also the vent material looks like it would require inside / out assembly (i.e., downstream piece inside rather than outside the upstream piece).
So would I. I see that accordion-type junk all the time, plastic and foil, when looking at the outside vent it's always packed full of lent just waiting to burn. Screens add more problems.

Overheated Clothes Dryers Can Cause Fires



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 7/28/09, 12:00 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Dryer vent

http://www.nachi.org/dryer-vent-safety.htm



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #9  
Old 7/28/09, 3:38 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Dryer vent

When a dryer vent terminates on the roof... I've rarely seen the required damper/backdraft protection installed.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #10  
Old 7/28/09, 9:42 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Dryer vent

Quote:
Originally Posted by tspargo View Post
When a dryer vent terminates on the roof... I've rarely seen the required damper/backdraft protection installed.
And that is exactly the problem!

Condensation can only occur when BTUs are removed to a point where a change of state from water vapor to liquid can occur. This will not occur when the dryer is pumping out hot air, or if stack affect (hot air rising up the pipe) is occurring in most cases. You must lower the temperature of the pipe not raise it for condensation to occur.

I would venture to say that there is a negative pressure in the house and cold air from the outdoors is being back drafted down the pipe cooling it off and the improperly ventilated attic space has sufficient water vapor to cause considerable condensation.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 7/28/09, 9:50 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Dryer vent

Remember, Buck is in Kansas. Hot summers and cold winters. Betcha the condensation problem only occurs in the winter. Thus the reason to insulate the vent pipe passing through the unconditioned attic space.
Reply With Quote
  #12  
Old 7/28/09, 10:38 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,567
Default Re: Dryer vent

Thanks! for all the information.



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
  #13  
Old 7/28/09, 7:06 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Dryer vent

Quote:
Originally Posted by jjonas View Post
Remember, Buck is in Kansas. Hot summers and cold winters. Betcha the condensation problem only occurs in the winter. Thus the reason to insulate the vent pipe passing through the unconditioned attic space.

We have many freezing winters here in Massachusetts and insulating a vertical dryer vent (that is penetrating through the roof) is not helping matters any.

As I stated above....the vent needs to be re-directed towards the soffit area under the existing insulation.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dryer Vent Repair Delaware County nhagarty Ancillary Inspection Services & Additional Topics 1 1/31/11 8:03 AM
Mr. Dryer Vent / Clean, Repair, Install nhagarty Ancillary Inspection Services & Additional Topics 5 1/15/09 12:17 PM
Dryer Vent Repair Montgomery County nhagarty Ancillary Inspection Services & Additional Topics 0 1/12/09 9:22 PM
Dryer Vent Repair Chester County nhagarty Ancillary Inspection Services & Additional Topics 0 1/12/09 9:21 PM
Dryer Vent Cleaning Philadelphia PA nhagarty Ancillary Inspection Services & Additional Topics 0 1/11/09 12:24 PM


All times are GMT -4. The time now is 11:40 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts