Default Duct from above furnace in laundry room.....

Duct above furnace in laundry room extends through ceiling into attic and terminates there. Is this allowed for proper air flow into laundry for furnace?
Attached Thumbnails
duct-above-furnace-laundry-room-tfroehle-037.jpg   duct-above-furnace-laundry-room-tfroehle-038.jpg  




Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 6/30/09, 7:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,469
Default Re: Duct from above furnace in laundry room.....

Quote:
Originally Posted by shand View Post
Duct above furnace in laundry room extends through ceiling into attic and terminates there. Is this allowed for proper air flow into laundry for furnace?

It is acceptable to bring combustion air in from the attic provided the attic is adequately vented.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 7/1/09, 12:49 AM
Travis Hirst Travis Hirst is offline
New User
 
Join Date: May 2009
Posts: 1
Please Note: Travis Hirst is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Duct from above furnace in laundry room.....

Ok same situation but it is a water heater in a hallwya closet. Vented into the attic the same way so that's ok but does it need to have a self closing door and a weatherseal on that door as opposed to the normal closet door?
Reply With Quote
  #4  
Old 7/1/09, 1:18 AM
Scott A. Hand's Avatar
Scott A. Hand Scott A. Hand is offline
InterNACHI Member
 
Join Date: May 2008
Location: North Liberty, IA
Posts: 387
Default Re: Duct from above furnace in laundry room.....

Good..thought so. Wanted to make sure. I love this message board!

Thanks




Reply With Quote
  #5  
Old 7/1/09, 8:18 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is online now
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,648
Default Re: Duct from above furnace in laundry room.....

Quote:
It is acceptable to bring combustion air in from the attic provided the attic is adequately vented.
I didnt know that, Have never seen it done that way. Thanks Larry
Reply With Quote
  #6  
Old 7/1/09, 10:53 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Duct from above furnace in laundry room.....

Quote:
Originally Posted by lkage View Post
It is acceptable to bring combustion air in from the attic provided the attic is adequately vented.
Agree.

Usually see one near the ceiling and another near the floor.

Note the bold.

For more see...

http://www2.iccsafe.org/states/orego...tion%20Air.pdf
Reply With Quote
  #7  
Old 7/1/09, 11:58 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Duct from above furnace in laundry room.....

It's not right for todays standards, but better than nothing!
Upgrades are not required!

As for the weather sealed door. Makeup air can create an efficiency loss concern.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Common wall of garage is Laundry room / firewall ? dnasser Interior Inspections 14 6/27/09 12:57 AM
6X6 room gas furnace and hot water tank mnicholet Inspecting HVAC Systems 2 6/13/08 1:53 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
furnace return air duct vwood Inspecting HVAC Systems 5 6/19/07 2:18 PM
Exhaust fan in room with gas water heater and furnace jweinberg Inspecting HVAC Systems 7 2/18/06 2:23 PM