Default Electric air handler wiring

Newer Rheem electric air handler in attic. Breaker in electrical for panel was 100 amp. There were 2 breakers/disconnects on side of unit- 60 amp. The boiler plate says maximum overcurrent protection 70/80. The 100 amp breaker would be to large, correct? Or do the 60 amp breakers on the unit suffice? Thanks in advance.
Reply With Quote
Need a home inspection in Maryland? Check out InterNACHI's listing of Maryland certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/16/10, 8:23 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Electric air handler wiring

Anyone??? I'm trying to get this report out of the way so me & the wife can get outta dodge and enjoy our 5th anniversary!! Thanks.
Reply With Quote
  #3  
Old 7/16/10, 8:26 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Electric air handler wiring

Quote:
Originally Posted by jfrederick View Post
Newer Rheem electric air handler in attic. Breaker in electrical for panel was 100 amp. There were 2 breakers/disconnects on side of unit- 60 amp. The boiler plate says maximum overcurrent protection 70/80. The 100 amp breaker would be to large, correct? Or do the 60 amp breakers on the unit suffice? Thanks in advance.
The 100 amp breaker is protecting the conductors to the remote disconnect on the side of the unit not the unit itself.


So from the info you have given it looks OK.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #4  
Old 7/16/10, 9:08 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Electric air handler wiring

Quote:
Originally Posted by mlarson View Post
The 100 amp breaker is protecting the conductors to the remote disconnect on the side of the unit not the unit itself.


So from the info you have given it looks OK.
So what should the breaker, in the main electrical panel, be sized at??
Reply With Quote
  #5  
Old 7/16/10, 9:11 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Electric air handler wiring

Quote:
Originally Posted by jfrederick View Post
So what should the breaker, in the main electrical panel, be sized at??
For the size of the wire between the panel and the remote disconnect.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Evaluating your home's wiring system mcyr Electrical Inspections 0 12/30/09 1:31 PM
Electric air handler wiring jfrederick Inspecting HVAC Systems 5 10/24/09 8:41 PM
Electrical Safety Media Center jtedesco1 Electrical Inspections 1 3/15/08 8:18 AM


All times are GMT -4. The time now is 11:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts