Default Electrical Device at interior refrigerant lines.

What is the purpose of the electrical device at the interior refrigerant lines?
Attached Thumbnails
electrical-device-interior-refrigerant-lines-114908-058-small-.jpg.jpg
Views:	81
Size:	56.5 KB
ID:	19863  
Reply With Quote
  #2  
Old 3/26/08, 4:11 PM
rramsey rramsey is offline
New User
 
Join Date: Jan 2007
Location: Bertram, Tx
Posts: 46
Please Note: rramsey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Device at interior refrigerant lines.

Liquid line solenoid valve. When valve closes, pressure builds up in line and a high pressure switch at outdoor unit turns off compressor and refrigerant flow.
Reply With Quote
  #3  
Old 3/26/08, 8:02 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Electrical Device at interior refrigerant lines.

Quote:
Originally Posted by rramsey
Liquid line solenoid valve. When valve closes, pressure builds up in line and a high pressure switch at outdoor unit turns off compressor and refrigerant flow.
You had the name correct but not its function.

Some times we refer to the liquid line solenoid valve as a pump down valve both names mean the same.

The thermostat operates the solenoid valve not the compressor contactor when these are in place. The valve is normally closed with no power from the thermostat or when the thermostat satisfies. Thus creating low pressure at the A/C condensing unit where a low pressure switch is installed that is wired in series to the compressor contactor. The low pressure switch actually becomes the operating control for the compressor.

Basic operation for this type system thermostat opens the solenoid valve increases pressure to the outside unit the low pressure switch closes on pressure increase and starts the compressor.

Your statement about the pressure building up when the solenoid valve closes is out of tune with reality. In Reality when the valve does close the head pressure actually decreases because it is located in the liquid line. If this solenoid valve was installed in the high pressure vapor side of the unit and it closed, the pressure would definitely increase and you would blow out the discharge valves within the compressor and if installed a high pressure cut out switch would shut the unit down.

Keep in mind a high pressure switch is never ever used as a operating control only as a safety switch and usually has a manual reset button.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 3/26/08, 8:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Electrical Device at interior refrigerant lines.

pumpdown solenoid.


Must be a high-end system.
Reply With Quote
  #5  
Old 3/27/08, 1:05 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Electrical Device at interior refrigerant lines.

This older version may not be a "pump down".

Depending on the location of the condenser, these valves were used to stop migration of liquid refrigerant during the off cycle. They just shut when the compressor shuts down.

It prevents overloading of the compressor at start up.

This requirement was later handled by a Thermostatic Expansion Valve that did not have an internal equalizer.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 3:58 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM


All times are GMT -4. The time now is 11:02 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts