Default Excessive moisture in exhaust pipe.

I've seen exhaust pipes like this (in the winter) with ice on the exterior. I believe this is a home-made job to keep the moisture from getting that far.
Does any one have any ideas of what causes this?

Thank you.
Attached Thumbnails
excessive-moisture-exhaust-pipe-033.jpg  



Tim Wendorff
Triple B Home Inspection, LLC
www.triplebhi.com
262-224-4420

A Southeastern Wisconsin home inspector specializing in residential home inspections and radon testing!
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/5/11, 4:19 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Excessive moisture in exhaust pipe.

Two thoughts one being you live up there with Santa Clause it appears some one has excessive moisture traveling back down the exhaust flue either from condensate in the winter or if there is no 180 degree fitting on the exterior side rainwater could be entering the pipe in any event someone is draining the system before it gets inside the furnace cabinet for what reason I know not



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 8/5/11, 5:16 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Excessive moisture in exhaust pipe.

I'd like to know where that drain tube "drains to". Seems to me it is high risk for CO being reintroduced into the home.
Reply With Quote
  #4  
Old 8/5/11, 5:23 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Excessive moisture in exhaust pipe.

Quote:
Originally Posted by jjonas View Post
I'd like to know where that drain tube "drains to". Seems to me it is high risk for CO being reintroduced into the home.
The tube has a trap



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 8/5/11, 5:33 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Excessive moisture in exhaust pipe.

I'd bet you 'dollars to doughnuts' come wintertime in Wisconsin, that trap don't perform as well as it should, and it goes dry. Then what? Hope there's a CO detector nearby to wherever it terminates.

JMHO, and I'm entitled to it!
Reply With Quote
  #6  
Old 8/5/11, 5:38 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Excessive moisture in exhaust pipe.

For draining flue gas condensation on a HE unit. Looks site made, which might be OK depending on mfr instructions. The loop is intentional (as Charlie indicates it is a trap). Pay attention to where it drains as the water will be corrosive due to combustion byproducts.

I usually see them tapped off of a concentric vent.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #7  
Old 8/5/11, 6:07 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Excessive moisture in exhaust pipe.

Quote:
Originally Posted by jjonas View Post
I'd bet you 'dollars to doughnuts' come wintertime in Wisconsin, that trap don't perform as well as it should, and it goes dry. Then what? Hope there's a CO detector nearby to wherever it terminates.

JMHO, and I'm entitled to it!
I will raise you two dollars against a dog terd and I will hold the stakes in my mouth that the furnace is a high efficiency producing water in the winter with the loop sealed



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 8/5/11, 6:41 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Excessive moisture in exhaust pipe.

Quote:
Originally Posted by cbottger View Post
I will raise you two dollars against a dog terd and I will hold the stakes in my mouth that the furnace is a high efficiency producing water in the winter with the loop sealed
Ewww, GROSS !!!

So basically you are endorsing this, and have no concerns what-so-ever?

Just trying to understand and learn (I ain't too old yet).
Reply With Quote
  #9  
Old 8/5/11, 7:14 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Excessive moisture in exhaust pipe.

Quote:
Originally Posted by jjonas View Post
Ewww, GROSS !!!

So basically you are endorsing this, and have no concerns what-so-ever?

Just trying to understand and learn (I ain't too old yet).
No endorsement without seeing the big pic need to know where it is discharging and whether the exterior line has a 180 degree fitting installed.

As for a health concern IMHO no CO would get past the loop trap but yes it is a Piss poor way of getting from point A to Point B if properly installed the flue pipe is designed to slant back toward the factory drain hoses within the furnace cabinet and with a 180 degree exterior fitting there should be no rain water to deal with



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 8/5/11, 7:15 PM
Timothy R. Wendorff Timothy R. Wendorff is offline
InterNACHI Member
 
Join Date: May 2010
Location: Hartford, WI
Posts: 67
Default Re: Excessive moisture in exhaust pipe.

That tube connects with the normal condensate tube coming off of the furnace.



Tim Wendorff
Triple B Home Inspection, LLC
www.triplebhi.com
262-224-4420

A Southeastern Wisconsin home inspector specializing in residential home inspections and radon testing!
Reply With Quote
  #11  
Old 8/5/11, 7:26 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Excessive moisture in exhaust pipe.

Quote:
Originally Posted by twendorff View Post
That tube connects with the normal condensate tube coming off of the furnace.
And where does the normal condensate line from the furnace discharge to.

My guess is the Wye fitting and the hose is used to compensate for rain water because the contractor did not choose to use a 180 degree fitting on the exterior. Hot flue gases rise I don't see them making a 90 degree turn into the hose connection even if the hose trap was dry



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Single wall exhaust pipe nrichards Plumbing Inspections 3 4/15/09 8:09 PM
Radon Exhaust Noise Neighbor Brian Sampson Ancillary Inspection Services & Additional Topics 1 4/12/09 9:52 PM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Excessive AC Condensation Problem kweiss Inspecting HVAC Systems 8 8/6/07 9:15 AM
Insulation around Exhaust Pipe rchewning Plumbing Inspections 4 6/18/06 9:01 AM


All times are GMT -4. The time now is 11:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts