Default Exhaust fan in room with gas water heater and furnace

Inspected a townhouse with a laundry room that has an exhaust fan and also has the gas water heater and gas furnace in the same room. There appears to be sufficient combustion air (through vent to crawl space) and draft air (through vent to attic).

My question is.....

doesn't the running of the exhaust fan while the water heater and/or furnace are operating (burning) cause a potential backdraft situation that could pull combustion air into the laundry room and potentially into the rest of the home?

Or is this not a problem because of the combination of:
* the combustion and draft vents
* draft diverter (water heater) and draft hood (furnace)
* the force of hot air rising
* the relatively weak overhead exhaust fan.

I can see it either way......

Any input would be appreciated....



Jeff Weinberg
A-Pro Home Inspection
408-259-3551
Reply With Quote
  #2  
Old 2/4/06, 9:32 PM
ekartal5 ekartal5 is offline
Active Poster
 
Join Date: Dec 2005
Location: Schaumburg, Il
Posts: 273
ekartal5 hasn't had much positive or negative feedback
Please Note: ekartal5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust fan in room with gas water heater and furnace

Hi Jeff,

How large is the utility room? How big is the fan? Are there levour vents on the door? Some things to consider. What I don't like the most is drawing combustion air from a crawl space.



Erol Kartal
ProInspect
Reply With Quote
  #3  
Old 2/4/06, 10:28 PM
jweinberg's Avatar
jweinberg jweinberg is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: San Jose, CA
Posts: 420
jweinberg has had a little positive feedback
Default Re: Exhaust fan in room with gas water heater and furnace

Quote:
Originally Posted by ekartal5
Hi Jeff,

How large is the utility room? How big is the fan? Are there levour vents on the door? Some things to consider. What I don't like the most is drawing combustion air from a crawl space.

Erol Kartal
ProInspect
Hi Erol,

Utility room is about 8' x 8'
Fan is about 9" x 9" like a standard bathroom fan
No vents in the door. Standard hollow core interior door

Getting combustion air from a well ventilated crawl space is pretty standard in California.

Water Heater 40k Btu/hr Furnace 80k Btu/hr 120k total
Combined upper and lower vents into utility room is approximately 168 sq inches. More than adequate.



Jeff Weinberg
A-Pro Home Inspection
408-259-3551
Reply With Quote
  #4  
Old 2/4/06, 11:17 PM
ekartal5 ekartal5 is offline
Active Poster
 
Join Date: Dec 2005
Location: Schaumburg, Il
Posts: 273
ekartal5 hasn't had much positive or negative feedback
Please Note: ekartal5 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust fan in room with gas water heater and furnace

I would have said OK if it had vented doors - now I don't know.

I have been in well vented crawls that smell like car exhaust. All kinds of pollutants in damp ground. Mold spores, animal feces etc; Just have a bad feeling about drawing air from them.

Erol Kartal
Reply With Quote
  #5  
Old 2/7/06, 8:09 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 156
Gary Reecher hasn't had much positive or negative feedback
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust fan in room with gas water heater and furnace

A worst case scenario test should be performed. That is starting exhaust fans and all clothes dryers while measuring draft. Then start water heater then shut down. Then start furnace and then shut down. Then start furnace and water heater together. Undiluted flue gas carbon monoxide is to be tested for elevated levels. Loss of draft or combustion gas spillage during this test needs to be corrected.
Reply With Quote
  #6  
Old 2/13/06, 3:21 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 566
Patrick Bolliger .
Send a message via Skype™ to pbolliger
Talking Re: Exhaust fan in room with gas water heater and furnace

Add a 240 BTU's for a gas dryer too.
What I see as a potential problem is that natural draft appliances don't have positive pressure on the flue so that means that a powerful vent fan could in essence "pull " products of combustion down the flues back into the room. If the fan where very powerful.
For louvers, calculate @ 80% free area.

The unknowns are how tight the room is : Door / windows sealed and or if the combustion air is available at all times.. You need a low and a high ducting / vent system to maintain air flow. Sounds like that is there , 1 square inch for every thousand BTU's and working on a 10:1 air gas ratio for proper combustion.

What happens with the fan is not working .. Where is the air flow.. You could try this: With the FAU and the water heater running use fake smoke or something like it at the draft hoods to visually inspect behavior of draw at hoods...Then try it with fan running.... All things to question.. Need pictures of room , door, vent , fan..

Last edited by pbolliger; 2/13/06 at 3:29 PM.
Reply With Quote
  #7  
Old 2/15/06, 12:51 PM
ewbarker ewbarker is offline
New User
 
Join Date: Feb 2006
Location: Barrington, IL
Posts: 7
ewbarker hasn't had much positive or negative feedback
Please Note: ewbarker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Exhaust fan in room with gas water heater and furnace

When providing combustion air only grills should be used, no registers. Whether the grill is wood or metal does make a difference in sizing.
Reply With Quote
  #8  
Old 2/18/06, 2:23 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 566
Patrick Bolliger .
Send a message via Skype™ to pbolliger
Smile Re: Exhaust fan in room with gas water heater and furnace

Per Peoples Energy of Chicago:

Louvered wood doors consider 25 % free area.
Metal louvers and grills consider 75% free area.

So a metal louver 10"x 10" = 100 square inches/ take 75% of that and you get 75 square inches.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace and hot water heater venting sfalvey HVAC 2 4/18/07 2:56 AM
Furnace and Water Heater Sharing Vent ehyde HVAC 2 4/11/07 6:07 AM
TPR & Combusiton Air thejnicki Plumbing 16 9/18/06 9:55 PM


All times are GMT -4. The time now is 11:44 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics