Default Explain this to your client

Split system Tag states heat pump but unit has no compressor or reversing valve at the exterior unit
Attached Thumbnails
explain-your-client-229-catfish-pc-10-25-10-004.jpg   explain-your-client-229-catfish-pc-10-25-10-006.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/25/10, 10:20 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Maybe this will help note the two lines 7/8 copper into the box this is not a ground source heat pump no water
Attached Thumbnails
explain-your-client-229-catfish-pc-10-25-10-070.jpg   explain-your-client-229-catfish-pc-10-25-10-128.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 10/26/10, 12:35 AM
dhuxted's Avatar
dhuxted dhuxted is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Orangeville, On.
Posts: 66
Default Re: Explain this to your client

radiant heat (coolant) 7/8 copper would lead me to believe source coolant from closed loop? am I close? I can't see 2 lines at the pump outside.



dhuxted@safehouseca.com
Serving Orangeville, Dufferin County, and surrounding area.

Last edited by dhuxted; 10/26/10 at 12:40 AM..
Reply With Quote
  #4  
Old 10/26/10, 8:51 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Quote:
Originally Posted by dhuxted View Post
radiant heat (coolant) 7/8 copper would lead me to believe source coolant from closed loop? am I close? I can't see 2 lines at the pump outside.
No closed loop no outside pump strictly air to air. The system has a conventional thermostat and when placed in the cooling mode the unit produces cold air at the registers. The kicker is if you touch the large line at the exterior unit it will burn your hand. The key word is in the cooling mode



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #5  
Old 10/26/10, 10:29 AM
dhuxted's Avatar
dhuxted dhuxted is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Orangeville, On.
Posts: 66
Default Re: Explain this to your client

Ok i'll try again it it a split system duel fuel ductless heat pump?



dhuxted@safehouseca.com
Serving Orangeville, Dufferin County, and surrounding area.
Reply With Quote
  #6  
Old 10/26/10, 10:53 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Quote:
Originally Posted by dhuxted View Post
Ok i'll try again it it a split system duel fuel ductless heat pump?
This is a crazy system been in this business for over 40 years and never observed a system set up in this manner.

The compressor is within the box in the attic hot gas line travels to outside condensing unit liquid line from exterior unit back to the attic A-coil.

This system originally had a electric furnace but has been converted to Natural gas. The reversing valve located in the box with the compressor is no longer in use thus the conventional thermostat.

This system operates as any split system does except the compressor is remote from the outside unit. Very miss leading just reading the label on the unit because it in essence it is no longer a heat pump
Attached Thumbnails
explain-your-client-229-catfish-pc-10-25-10-073.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 10/26/10, 11:00 AM
dhuxted's Avatar
dhuxted dhuxted is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Orangeville, On.
Posts: 66
Default Re: Explain this to your client

how can it be a heat pump without compressor? hence this question. Where is all the ducting? and is that an erv in the backround?
and why 7/8 copper? thats huge isn't it?
I was even on the carrier site trying to figure it out.



dhuxted@safehouseca.com
Serving Orangeville, Dufferin County, and surrounding area.

Last edited by dhuxted; 10/26/10 at 11:10 AM..
Reply With Quote
  #8  
Old 10/26/10, 11:12 AM
rjohnson11 rjohnson11 is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Binbrook Ontario
Posts: 17
Default Re: Explain this to your client

Its a carrier 38 series air to air heat pump and should be coupled with either an air handlier with electric heat or a gas furnace. The outdoor unit is just a condensing coil, the compressor, reversing valve, etc are located in the heat pump section (the enclosed box in your 2nd pic). Were very big sellers in their day but prone to service issues due to age.
Reply With Quote
  #9  
Old 10/26/10, 11:18 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Quote:
Originally Posted by dhuxted View Post
how can it be a heat pump without compressor? hence this question. Where is all the ducting? and is that an erv in the backround?
and why 7/8 copper? thats huge isn't it?
I was even on the carrier site trying to figure it out.
It was originally a heat pump but when they installed the gas furnace they disabled the reversing valve except for cooling
Attached Thumbnails
explain-your-client-229-catfish-pc-10-25-10-067.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #10  
Old 10/26/10, 11:26 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Quote:
Originally Posted by rjohnson11 View Post
Its a carrier 38 series air to air heat pump and should be coupled with either an air handlier with electric heat or a gas furnace. The outdoor unit is just a condensing coil, the compressor, reversing valve, etc are located in the heat pump section (the enclosed box in your 2nd pic). Were very big sellers in their day but prone to service issues due to age.
You are correct but not a big seller in this area unit was dated 1986 this home had two of them. I would venture to say most HI'S have never seen one and that includes me



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 10/26/10, 11:29 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Explain this to your client

Very interesting.

Does the interior located compressor produce excessive noise?

How do they cool the compressor/motor inside the house, is it inside the duct/air handler with the evaporator coil or a separate unit?

What gauge wire/amperage goes to the condensing coil unit? I would think that it could add to the cost of conversion if it was undersized for a conventional condenser/compressor.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #12  
Old 10/26/10, 11:51 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Quote:
Originally Posted by cevans View Post
Very interesting.

Does the interior located compressor produce excessive noise?

How do they cool the compressor/motor inside the house, is it inside the duct/air handler with the evaporator coil or a separate unit?

What gauge wire/amperage goes to the condensing coil unit? I would think that it could add to the cost of conversion if it was undersized for a conventional condenser/compressor.
No excessive noise noted, the compressor is within the small box shown in the second post I would think excessive heat in the attic would or could be a problem but the compressor has been there since 1986 and still operating.

The supply wiring was sized for condenser fan only and would have to be upsized for conventional A/C unit if updated not a big problem



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 10/28/10, 12:56 AM
sparksnmore sparksnmore is offline
Active Poster
 
Join Date: Oct 2006
Location: midwest
Posts: 177
Please Note: sparksnmore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Explain this to your client

If it's like one I worked on one time just like it that had been converted from the old "indoor compressor" type heat pump;

The compressor is cooled the same as all split system units which is by the cool refrigerant gas returning via one of the 7/8" o.d. lines which is the suction line coming from the evaporator.
Reply With Quote
Need a home inspection in California? Check out InterNACHI's listing of California certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/29/10, 7:59 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Explain this to your client

Quote:
Originally Posted by sparksnmore View Post
If it's like one I worked on one time just like it that had been converted from the old "indoor compressor" type heat pump;

The compressor is cooled the same as all split system units which is by the cool refrigerant gas returning via one of the 7/8" o.d. lines which is the suction line coming from the evaporator.
That is correct on this one the suction line never leaves the attic the 7/8 line at the exterior unit is the hot gas line



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inspection Agreement Review. bsavage General Inspection Discussion 21 5/11/08 9:20 PM
Clueless Client? jpassailaigue Plumbing Inspections 5 8/2/07 3:35 PM
ILLINOIS Section 1410.200 Standards of Practice jtedesco1 Legislation, Licensing & Legal Issues for Inspectors 11 3/9/06 11:22 AM


All times are GMT -4. The time now is 11:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts