Ran across this one today. A wood burning built-in fireplace in the living room below this bedroom. Visual evidence the fireplace has been well used. Don't know when the stickers were put on. They were not discolored or falling off.
I commented to the clients during the inspection that this was very unusual. Normally chimney flues are enclosed with a 1" minimum air gap around them. I've seen them exposed like this through attic spaces, and in living spaces above the wood burner but not in living spaces from the floor to the ceiling. Any thoughts? Hot Do Not Touch sign?? Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
| Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
It looks like triple wall (class A pipe at least) which still needs 2" clearance to combustibles.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
Last edited by lkage; 8/25/11 at 5:50 PM.. |
|
#3
|
||||
|
||||
|
Stupid design. Is that wall paper on it? I'd be afraid someone would thrown a stuffed bunny up against it.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#4
|
||||
|
||||
|
No, they are stickers! You know how much kids love stickers! I would hate seeing what would happen to a child giving that pipe a big hug on Christmas Morning thinking that is where Santa will be coming down to visit...
Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
|
#5
|
||||
|
||||
|
Greg, were you able to see down the flue from the roof? The diameter looks to be large enough to have a standard flue within it, with an air gap between it and the outer shell pipe. Guessing that to be a 12inch ID (or larger) Class A pipe, that stuff ain't cheap! About $400-$500 retail for a 36" length! I find it hard to believe someone would spend that much coin, and not go a different route. JMHO.
http://www.ventingpipe.com/all-chimney-pipe/c15659 Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#6
|
||||
|
||||
|
Quote:
Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
|
#7
|
||||
|
||||
|
Quote:
What was the chimney construction above the roofline? Looks like wood frame with a tin or other faux brick siding material that is painted. Or is it brick or veneer? How is it attached/setting in the attic? I could see the need for the guy wires. Top heavy and the winds loves it I bet. What is the approximate diameter of the pipe going through the bedroom? Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#8
|
||||
|
||||
|
It was framed with painted galvanized covering. Screen over the top. Not visible from the attic as it was too close to the eves. Attic inspection was Head and Shoulders from the 10 x 14 scuttle opposite corner of the home from the chimney. Diameter was approx 14-16 inches in the bedroom. Home was built in 1936. K&T wiring visible under the insulation.
Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| super chimney through childs bedroom | wdevries | Interior Inspections | 13 | 10/8/08 5:13 PM |
| What's Inside A Chimney | mcyr | Inspecting HVAC Systems | 14 | 9/17/08 6:11 PM |
| Difficult Chimneys | thance | Inspecting HVAC Systems | 2 | 1/29/08 8:16 PM |
| Chimney flashing photo's needed: brick and stone done correctly | kshepard | Exterior Inspections | 6 | 10/13/07 8:10 AM |
| Massachusetts Board of Registration of Home Inspectors | jtedesco1 | Legislation, Licensing & Legal Issues for Inspectors | 0 | 2/14/06 3:38 AM |