Default A fatal installation

http://www.startribune.com/newsgraphics/12950942.html

Anatol
Reply With Quote
  #2  
Old 1/4/08, 2:01 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: A fatal installation

Do not get confused by the to pipes being side-by-side in the first picture. There is not necessarily anything wrong with this, though in northern climates the moisture of the combustion gas will freeze at the intake and shut the equipment down.

The example they gave in how it should be done is the recommended installation practice but would not have been sufficient to protect the carbon monoxide issue because the air intake was not properly completed. The main issue was that the air intake was not piped all the way to the boiler. Combustion gases were being drawn into the utility room area not just into the furnace. Normally if piped properly, carbon monoxide would never enter the house because the intake/exhaust system is a closed loop.

This article is a bit confusing. If the pipe through the wall was intended as a fresh air makeup vent, then it must comply with gas appliance venting requirements. A mechanical draft condensing furnace vent termination must be a minimum of 3 feet above any forced air inlet (not furnace intake). A minimum of 1 foot above any building opening or 4 feet below or to the side of a window or door opening. The window in the photograph appears to be too close to the discharge.
Reply With Quote
  #3  
Old 1/5/08, 12:44 AM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A fatal installation

Another problem was that the furnace was fueled by propane, but had not been converted from natural gas. I tried to post the article from the newspaper, but the link changed. You may be able to search and locate it.
In any event, someone died due to a chain of errors.
Reply With Quote
  #4  
Old 1/5/08, 12:54 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,927
Default Re: A fatal installation

Quote:
Originally Posted by apolillo
Another problem was that the furnace was fueled by propane, but had not been converted from natural gas. I tried to post the article from the newspaper, but the link changed. You may be able to search and locate it.
In any event, someone died due to a chain of errors.
Here are a couple been more then this latly .
...Cookie

http://www.nachi.org/forum/showthrea...hlight=Propane

http://www.nachi.org/forum/showthrea...hlight=Propane



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Question about improper installation cbell1 Exterior Inspections 3 10/24/07 10:13 PM
Bonding wire installation requirements ?? rnewman1 Electrical Inspections 7 7/31/06 3:31 PM
Flanged window installation bnelson Exterior Inspections 6 1/30/06 8:01 PM
Window installation jmichalski Exterior Inspections 17 1/24/06 10:42 PM
Common Installation Deficiencies jkline Electrical Inspections 0 1/12/06 9:58 AM


All times are GMT -4. The time now is 8:48 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts