  #1  
Old 3/11/10, 9:14 AM
John F. Swygert, III John F. Swygert, III is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Nashville, TN
Posts: 2
Default Flex Duct Firewall Breach

Guys, I see this all the time and need some clarification. Furnace located in garage with flex duct supply and return going through the garage wall and ceiling. I know flex duct is combustable however it's approved for use as furnace ductwork. But it's my understanding that ducts from house to garage must be min. 26ga. metal. Is this a breach??? How would you write it up? Many Thanks in advance.
Reply With Quote
Need a home inspection in Tennessee? Check out InterNACHI's listing of Tennessee certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/11/10, 9:33 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Flex Duct Firewall Breach

I don't think I've ever seen it unless the furnace is in a separate room with a solid door. If it wasn't, I would definitely write it up.

Put up a photo.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 3/11/10, 1:50 PM
Matt Berman, CMI Matt Berman, CMI is offline
InterNACHI Member
 
Join Date: Nov 2003
Location: Mt. Clemens, MI
Posts: 107
Default Re: Flex Duct Firewall Breach

in michigan should be 26 gauge metal and have a fire damper in both supply and return
Reply With Quote
  #4  
Old 3/11/10, 3:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Flex Duct Firewall Breach

I see it often. . .

Flexible ducting is penetrating the garage firewall. Building standards require that all ducts in the garage and ducts penetrating the firewall be equipped with fire-dampers or constructed of a minimum of No. 26 gauge sheet steel or other approved material and shall have no openings in the garage. This condition compromises the garage firewall system and should be repaired by a qualified HVAC contractor for safety.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/11/10 at 3:23 PM..
Reply With Quote
  #5  
Old 3/11/10, 3:44 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Flex Duct Firewall Breach

I see Studor vents occasionally.

flex-duct-firewall-breach-030910-121.jpg



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 3/11/10, 3:56 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Flex Duct Firewall Breach

I call out all breaches in garage walls and ceilings that divide the living area from the garage...

Flexible ducts, any type of openings in the firewall (even the seams that aren't compounded), cable and wiring openings, etc.

If the firewall is open (breached) in any way, it gets red flagged.
Reply With Quote
  #7  
Old 3/11/10, 6:44 PM
John F. Swygert, III John F. Swygert, III is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Nashville, TN
Posts: 2
Default Re: Flex Duct Firewall Breach

Outstanding response. Thanks so much to all. Thats what i thought but I am seeing this weekly in 500K homes. Will take and add photos next chance.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Flex duct used for exhasut flue. jlybolt Inspecting HVAC Systems 11 4/5/07 11:04 PM
Flex duct length restrictions wcorbett Inspecting HVAC Systems 4 8/24/06 12:34 AM
Condo Firewall breach or no breach? tneumann Interior Inspections 14 2/3/06 10:13 AM