First time seeing this, 1-1/2 inch metal strap supporting flex duct. Always have just seen the nylon strap before. IRC refers to manufacturer's specs but I am having a little trouble finding something. While I look further, I thought I could get a quick answer here. Sorry for not havong a pic, but I have a new vista computer and have yet to figure out how to crop and resize. Thanks in advance.
|
|
#2
|
||||
|
||||
|
Dylan...check your e-mail for a flex duct installation guide that may be of some help. It is too big to post here. It says 1.5" is acceptable.
|
|
#3
|
|||
|
|||
|
Please Note:
dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you Michael. I wish I could show the picture. The straps look loke they are about to cut right through the duct. I can live with it though. I told the homeowner to pay me to come back each year to monitor.
|
|
#4
|
||||
|
||||
|
Quote:
I've been struggling with Vista and MS Office 2007 for a couple of months now too. Nothing seems to work as it should. Hope that helps. Mark |
|
#5
|
|||
|
|||
|
Please Note:
dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Mark,
That did it. Much obliged. |
|
#6
|
||||
|
||||
|
Quote:
|
|
#7
|
||||
|
||||
|
This is the information I use in my reports if it helps you...
The Sheet Metal and Air Conditioning Contractors National Association (SMACNA) recommend that flex duct be supported with the following guidelines: Ducts should not sag more than 1/2 inch every foot between supports Support straps should be spaced no farther apart than 5 feet Support straps should be 1-1/2 inches wide or more Maybe someone that is a HVAC contractor can elaborate. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Flex duct used for exhasut flue. | jlybolt | Inspecting HVAC Systems | 11 | 4/5/07 11:04 PM |
| Flex duct length restrictions | wcorbett | Inspecting HVAC Systems | 4 | 8/24/06 12:34 AM |
| Is Flex Duct Combustible? | jfunderburk | Inspecting HVAC Systems | 13 | 2/9/06 9:56 AM |