Default Flex gas line ok or not?

Just looking for different thoughts on this one. the flex line does penetrate the casing, but the casing comes apart. At the time of the inspection the line was rubbing on the knock out. It has been called out.
Attached Thumbnails
flex-gas-line-ok-not-jst_p1010081.jpg   flex-gas-line-ok-not-jst_p1010098.jpg  



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #2  
Old 5/12/07, 11:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Flex gas line ok or not?

Quote:
the flex line does penetrate the casing
That's all that matters. Appliance connectors are not allowed to pass through the cabinet.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 5/13/07, 1:54 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Flex gas line ok or not?

Quote:
Originally Posted by jpope
That's all that matters. Appliance connectors are not allowed to pass through the cabinet.
They are here as long as the protective grommet is in place. It rarely is.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #4  
Old 5/13/07, 2:07 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,585
Default Re: Flex gas line ok or not?

Bruce -

What are you asking us?? Flex connectors don't go through walls, floors, ceilings, partitions, etc. Obviously you know this. Its in your code book; your copy of Code Check; and on the plastic bag they come in at the hardware store. So since you know this, what is it you are really asking us.
Reply With Quote
  #5  
Old 5/13/07, 2:12 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Flex gas line ok or not?

Russel - if you researched that a bit, you will find that the manufacturers listing prohibits this practice, even when/if a grommet is used.

To say it's "allowed" in your area, is to say (simply) that, in your area, no one cares.

Manufacturers listings trump local requirements, unless of course, no one cares.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 5/13/07, 2:31 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Flex gas line ok or not?

Quote:
Originally Posted by jpope
Russel - if you researched that a bit, you will find that the manufacturers listing prohibits this practice, even when/if a grommet is used.

To say it's "allowed" in your area, is to say (simply) that, in your area, no one cares.

Manufacturers listings trump local requirements, unless of course, no one cares.
I know, but I choose not to fight them, only to note such conditions in my report and provide my own recommendations.

There's still one AHJ out in the boondocks whose using the 1847 codes. I think he is old enough to have been there in that position since that time. He does have some war stories to tell, but I never know if they are Civil War, WWI, WWII, Korean, Vietnam, or Bush Invasion.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 5/13/07, 2:34 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Flex gas line ok or not?

If you can't find a listing label, here are the applicable codes. . .

California Plumbing Code (CPC)

1212.0 Appliance Connectors (2) No part of such connector shall be concealed within or extended through any wall, floor, partition, or appliance housing.

International Residential Code (IRC)

G2422.1.2 (411.1.2) Appliance fuel connectors. Connectors shall have an overall length not to exceed 3 feet (914 mm), except for range and domestic clothes dryer connectors, which shall not exceed 6 feet (1829 mm) in length. Connectors shall not be concealed within, or extended through, walls, floors, partitions, ceilings or appliance housings. A shutoff valve not less than the nominal size of the connector shall be installed ahead of the connector in accordance with Section G2420.5. Connectors shall be sized to provide the total demand of the connected appliance.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 5/13/07, 3:00 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Flex gas line ok or not?

I've got the codes, but thanks. However, I'm not a code inspector, preferring to be a generalist, so I leave the code interpretations to the AHJs, even when they (the AHJs) are past their prime.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #9  
Old 5/13/07, 3:17 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Flex gas line ok or not?

Quote:
Originally Posted by rray
I leave the code interpretations to the AHJs, even when they (the AHJs) are past their prime.
Or apparently, just don't care. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 5/13/07, 3:23 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Flex gas line ok or not?

Quote:
Originally Posted by jpope
Or apparently, just don't care. . .
Did they have forced air furnaces in 1847?



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 5/13/07, 7:24 AM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,025
Default Re: Flex gas line ok or not?

Dan,
Just wanted to see what others thought of the split cabinet. Some of the HVAC guys try to call this a cover and that the rule does not apply. I just laugh at them and say nice try.



Bungalows to Mansions
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com

Last edited by bgraham; 5/13/07 at 7:28 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas flex line in crawl space Richard Seay Plumbing Inspections 19 8/12/08 9:12 PM
Gas flex connector to furnace jcahill Inspecting HVAC Systems 25 7/24/07 7:22 PM
Exposed Flex Gas Line jfunderburk Plumbing Inspections 20 5/11/06 2:44 AM
TPRV line and condensate line marriage ccarrington Plumbing Inspections 3 4/29/06 8:59 AM