2 questions 1) is it o.k. to run yellow flex from iron pipe main then snake it over 40' to a small 3000btu unit heater?

2) how far apart should the supports be? this set up had only 4, about every 10 feet, plus the rigid pipe was about 12' long comming in threw the sill plate and was just "free-ballin'" in the joists.
Attached Thumbnails
flex-pipe-supports-100_0796-small-.jpg.JPG
Views:	68
Size:	40.2 KB
ID:	686   flex-pipe-supports-100_0797-small-.jpg.JPG
Views:	62
Size:	38.2 KB
ID:	687  
Reply With Quote
  #2  
Old 1/23/06, 1:19 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: flex pipe supports.

That "yellow flex" is CSST and can be run pretty much the same as iron pipe.

Support spacing for CSST is governed by the manufacturer.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/23/06, 11:25 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: flex pipe supports.

Quote:
Originally Posted by jpope
That "yellow flex" is CSST and can be run pretty much the same as iron pipe.

Support spacing for CSST is governed by the manufacturer.
I have been wondering about this stuff. The first time I saw this stuff was last year when a friend of mine was having a new boiler connected. The plumber/mechanical eng. said that it was great stuff. He didn't install a drip pipe like you would with black pipe. He said that it wasn't needed with this stuff.

Is that true?
Is their a length of run max?
Does anyone know what the typical manufacturer suggested support strapping spaceing is?



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #4  
Old 1/23/06, 2:16 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: flex pipe supports.

Try this website: www.gastite.com

Everything you ever or never want to know about CSST. This is only one of the manufacturers but it is one I have known about almost since this stuff hit the market. Getting the old timers to use this is often futile. They want to do things the old way not realizing this takes a 1/3 of the time to install with less headaches and fuss. It is great stuff. The RV guys have been using it for years with great success. Once you get into the website go to "inspectors" link then click on Installation Procedures, go to page 45, Table 41-2 gives the spacing for supports. It depends on the type and size of the CSST and type of configuration. Have fun.

Last edited by dedwards; 1/23/06 at 2:22 PM..
Reply With Quote
  #5  
Old 1/23/06, 5:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: flex pipe supports.

Quote:
He didn't install a drip pipe like you would with black pipe. He said that it wasn't needed with this stuff. Is that true?
Not true. If it's required by the utility, it's needed with CSST as well as other piping methods.

Quote:
Is their a length of run max?
There is no limitation based on the material. CSST can be run as far as any other material so long as proper connections and required protection is maintained.

Quote:
Does anyone know what the typical manufacturer suggested support strapping spaceing is?
As stated in the previous post, support spacing is determined by the piping size.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 1/23/06, 9:30 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: flex pipe supports.

Hay Doug. thanx for the link, it's just what i needed. this was 3/4, so acording the the chart, 4-2 it should be every 8 feet. so this stuff was a little out of specs. not likely to hurt anyone or anything, but still out of spec, and duely noted. thanx again.
Reply With Quote
  #7  
Old 1/23/06, 11:34 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: flex pipe supports.

No worries. You're welcome.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing Inspections 41 4/5/12 6:43 AM
Help - Polybutylene Pipes Rick G Plumbing Inspections 39 2/12/09 8:16 AM
Identify ABS defective pipe mcyr Plumbing Inspections 6 1/29/09 6:39 PM
Flex pipe for Flue cyezza Inspecting HVAC Systems 9 11/11/07 5:03 PM
Soldered pipe supports causing corrosion kshepard Plumbing Inspections 7 12/3/06 2:30 PM


All times are GMT -4. The time now is 7:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts