2 questions 1) is it o.k. to run yellow flex from iron pipe main then snake it over 40' to a small 3000btu unit heater?
2) how far apart should the supports be? this set up had only 4, about every 10 feet, plus the rigid pipe was about 12' long comming in threw the sill plate and was just "free-ballin'" in the joists. |
|
#2
|
||||
|
||||
|
That "yellow flex" is CSST and can be run pretty much the same as iron pipe.
Support spacing for CSST is governed by the manufacturer. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Quote:
Is that true? Is their a length of run max? Does anyone know what the typical manufacturer suggested support strapping spaceing is? Jason Sieg, CMI Davison, MI NACHI05091399 Knowing the current condition, to make a wise decision.
President, Great Lakes-East Chapter Join NACHI Great Lakes - East Chapter http://mi.nachi.org/greatlakes-east/about.html ssieg@gfn.org |
|
#4
|
||||
|
||||
|
Try this website: www.gastite.com
Everything you ever or never want to know about CSST. This is only one of the manufacturers but it is one I have known about almost since this stuff hit the market. Getting the old timers to use this is often futile. They want to do things the old way not realizing this takes a 1/3 of the time to install with less headaches and fuss. It is great stuff. The RV guys have been using it for years with great success. Once you get into the website go to "inspectors" link then click on Installation Procedures, go to page 45, Table 41-2 gives the spacing for supports. It depends on the type and size of the CSST and type of configuration. Have fun. Last edited by dedwards; 1/23/06 at 2:22 PM.. |
|
#5
|
||||
|
||||
|
Quote:
Quote:
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hay Doug. thanx for the link, it's just what i needed. this was 3/4, so acording the the chart, 4-2 it should be every 8 feet. so this stuff was a little out of specs. not likely to hurt anyone or anything, but still out of spec, and duely noted. thanx again.
|
|
#7
|
||||
|
||||
|
No worries. You're welcome.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Do you put polybutylene in the Summary? | jfunderburk | Plumbing Inspections | 41 | 4/5/12 6:43 AM |
| Help - Polybutylene Pipes | Rick G | Plumbing Inspections | 39 | 2/12/09 8:16 AM |
| Identify ABS defective pipe | mcyr | Plumbing Inspections | 6 | 1/29/09 6:39 PM |
| Flex pipe for Flue | cyezza | Inspecting HVAC Systems | 9 | 11/11/07 5:03 PM |
| Soldered pipe supports causing corrosion | kshepard | Plumbing Inspections | 7 | 12/3/06 2:30 PM |