Default Flexible water heater vent pipe

Can anyone tell me if a flexible metal vent pipe is allowed on a gas fired water heater as shown in the attached photo. I haven't come across this one before. Thanks.
Attached Thumbnails
flexible-water-heater-vent-pipe-img_7133.jpg  
Reply With Quote
  #2  
Old 7/25/08, 4:36 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,350
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by jgromkoski
Can anyone tell me if a flexible metal vent pipe is allowed on a gas fired water heater as shown in the attached photo. I haven't come across this one before. Thanks.
They are allowed. You just have to make sure that they are of the proper type and not a laundry vent connector.

That one looks like it is of the proper type. The Type B flex that I've seen here has stamping on the ends.

See this, as well.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year

Last edited by rray; 7/25/08 at 4:41 AM..
Reply With Quote
  #3  
Old 7/25/08, 7:52 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,168
Default Re: Flexible water heater vent pipe

What Russel said and it shouldn't run downhill like it appears to.



____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 7/25/08, 12:45 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 4,481
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by lkage
What Russel said and it shouldn't run downhill like it appears to.
I agree that it shouldn't run downhill, but from my perspective I don't think it does. At least not enough to be an issue. There might be a little bit of a "droop" in the line, but IMHO it's not enough to obstruct the flow.
Reply With Quote
  #5  
Old 7/25/08, 1:07 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,350
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by mnahrgang
I agree that it shouldn't run downhill, but from my perspective I don't think it does. At least not enough to be an issue. There might be a little bit of a "droop" in the line, but IMHO it's not enough to obstruct the flow.
A little bit of a droop in the line can, indeed, interfere with proper drafting of the water heater, which then could result in lower efficiency of the water heater, backdrafting, and excessive levels of carbon monoxide. Gas combustion is not something that you want to mess around with.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #6  
Old 7/25/08, 1:08 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 4,481
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by rray
A little bit of a droop in the line can, indeed, interfere with proper drafting of the water heater, which then could result in lower efficiency of the water heater, backdrafting, and excessive levels of carbon monoxide.
Do you think, from the pic proved, that there is enough "droop" to be a concern?
Reply With Quote
  #7  
Old 7/25/08, 1:14 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,350
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by mnahrgang
Do you think, from the pic proved, that there is enough "droop" to be a concern?
Yes, I do.

If you really want to have fun sometime, mess with the installation on your own water heater and then take some carbon monoxide readings of the different types of installations. It will be eye-opening.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #8  
Old 7/25/08, 1:16 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,752
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by rray
Yes, I do.

If you really want to have fun sometime, mess with the installation on your own water heater and then take some carbon monoxide readings of the different types of installations. It will be eye-opening.
Just be sure when you duct tape it back together (as in the picture) you do it properly.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #9  
Old 7/25/08, 1:18 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,350
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by rmaday
Just be sure when you duct tape it back together (as in the picture) you do it properly.
That doesn't appear to be duct tape in the picture. It looks more like the high-temperature metal tape that is approved for such uses.

I actually like it better than relying just on the male-female fitting and screws since I see it as a secondary fail-safe; it helps hold the screws in place so that they don't back out due to vibration or gravity (or Little Johnny playing with his first set of tools).



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year

Last edited by rray; 7/25/08 at 1:22 PM..
Reply With Quote
  #10  
Old 7/25/08, 1:21 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,350
Default Re: Flexible water heater vent pipe

And I wonder why they put a hot water handle (red) on what hopefully is the cold-water line. They should have used blue, but that's something that I don't call out. Just noteworthy to me.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 7/25/08, 1:42 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flexible water heater vent pipe

Quote:
Originally Posted by rray
And I wonder why they put a hot water handle (red) on what hopefully is the cold-water line. They should have used blue, but that's something that I don't call out. Just noteworthy to me.
Besides being bad at carpentry, some plumbers are also color blind?
Reply With Quote
  #12  
Old 7/29/08, 9:45 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 499
Default Re: Flexible water heater vent pipe

In my neck of the woods, our AHJ calls that flexible material a "connector", which is disallowed, as it appears installed.
I assume the flex is rated B'vent material and connects the elbow to ridgid B'vent running through a chase area up and through the roof. We can, from the draft diverter, use a single-wall elbow and then convert to any approved double-wall (B-type) vent material to the outside. We aren't allowed to mix materials after the DD connection.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do you put polybutylene in the Summary? jfunderburk Plumbing 36 11/27/07 12:56 AM
Furnace and Water Heater Sharing Vent ehyde HVAC 2 4/11/07 6:07 AM
Need Help On Chimney Liners Nick Scibetta Exterior 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 12:29 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts