Is there any requirement for a floor drain in the room with the furnace and water heater? In an older home I inspected last week, the basement was finished and a new wall seperated the furnace and water heater from the floor drain. My client seems to think that is an issue the seller needs to correct.
Reply With Quote
Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America)
  #2  
Old 11/24/09, 5:07 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Floor drain in furnace room?

No requirement...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 11/28/09, 6:15 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Floor drain in furnace room?

Gotta have a place to drain to - If the floor drain is in another room - WHERE is that p[lace at??
Reply With Quote
  #4  
Old 11/28/09, 9:28 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Floor drain in furnace room?

A hose on the draincock into a bucket...

That is how the last plumber did it untill it was light enough to carry up the stairs and outside.

No requirement for a floor drain around here.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 11/28/09, 9:49 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Floor drain in furnace room?

Quote:
Originally Posted by jvanorsdol View Post
Is there any requirement for a floor drain in the room with the furnace and water heater? In an older home I inspected last week, the basement was finished and a new wall seperated the furnace and water heater from the floor drain. My client seems to think that is an issue the seller needs to correct.
Where is the drain with respect to the water heater T&P relief piping? That would be an issue if finished surfaces could be negatively impacted by the discharge of the water in the event it was manually operated or opened to discharge as intended for safety.
Reply With Quote
  #6  
Old 11/29/09, 1:00 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Floor drain in furnace room?

Joe -

We're not in the requirement business - We're in the common sence business AND protecting our clients best interests. Its of NO importance whether this is required or NOT. You're NOT the code guy.

Looking out for your client AND his / her property, there must be a way for the condensate to drain, OR if the unit leaks - to help protect finished surfaces.

Tell them that and MOVE on .........
Reply With Quote
  #7  
Old 12/5/09, 11:39 PM
Robert A. Jack Robert A. Jack is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Guilford, VT
Posts: 63
Default Re: Floor drain in furnace room?

If the furnace or water heater are using LP gas than yes, there should be a drain in the room.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Renovating Your Basement for Livability mkyriacou Canadian Inspectors 0 10/22/09 11:45 AM
Duct from above furnace in laundry room..... shand Inspecting HVAC Systems 6 7/1/09 10:58 AM
6X6 room gas furnace and hot water tank mnicholet Inspecting HVAC Systems 2 6/13/08 12:53 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Exhaust fan in room with gas water heater and furnace jweinberg Inspecting HVAC Systems 7 2/18/06 1:23 PM