Question Flue clearance from type X drywall

Why would you (is it required?) need 1" of clearance between a type B vent and type X drywall if the drywall is fire resistant? I always write it up, but I am beginning to wonder why.
Reply With Quote
Find an InterNACHI certified California Home Inspector (and anywhere else in North America)
  #2  
Old 9/7/09, 3:46 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,643
Default Re: Flue clearance from type X drywall

I believe some of it is to stop transfer of heat to nails or screws
Reply With Quote
  #3  
Old 9/7/09, 4:34 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Flue clearance from type X drywall

http://www.nachi.org/forum/f2/drywal...ustible-11531/



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 9/7/09, 4:47 PM
rbrady's Avatar
rbrady rbrady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flue clearance from type X drywall

Thanks Larry, I always search the forum first before asking a question, but I searched the HVAC forum and only went back a little less than 3 years. It looks like the issue is open to some interpetation, although it was definatly leaning towards being OK.
Reply With Quote
  #5  
Old 9/7/09, 4:50 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,643
Default Re: Flue clearance from type X drywall

Also the paper is not fire proof unless it is treated , Stay with the 1 inch clearance to be safe .
Reply With Quote
  #6  
Old 9/7/09, 4:55 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Flue clearance from type X drywall

Page 2, first paragraph by manufacturer states "Drywall is not combustible or explosive."

http://www.lafargecorp.com/wps/wcm/r...ywallMSDS5.pdf



But NFPA classifies it as limited-combustible.

In regard to gypsum wallboard, the product's paper facing prevents it from passing ASTM E 136. However, because it does have a demonstrated ability to perform in fire rated assemblies, the NFPA has placed it in a special classification called limited-combustible. This category distinguishes gypsum wallboard from other, more highly combustible products. To qualify as limited-combustible, a material must have a noncombustible structural base or core, a surface less than 1/8 in. (0.3 cm) thickness and a flame-spread rating of 50 or less.



On top of those two definitions, one should consider whether there is framing wood within the "clearance to combustibles" distance even if there is drywall between it and the vent pipe.





InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 9/8/09, 1:20 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 29,297
Default Re: Flue clearance from type X drywall

Good post Larry.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #8  
Old 9/8/09, 4:47 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Flue clearance from type X drywall

B- Vent manufacturers say NO, and I believe underwriters Lab has not signed off or tested B-Vent to a less than 1" clearance.

http://www.americanmetalproducts.com...vent/faq.htm#6

Quote:
Can I install drywall or wall board right up against the gas vent?
No. Drywall and wallboard are considered combustible materials and should not be installed against the vent including the use of this material to close off the hole around the vent. Type B Gas Vent requires a minimum of one-inch clearance to combustibles. This one-inch is a typical clearance for all brands of Type B Vent, but each section of vent pipe is marked with the clearance required by Underwriter Laboratories, so it should be checked.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Toxic Drywall from China inxil InterNACHI & RealMatcher Blogs 13 3/13/09 12:14 PM
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 7:11 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Popcorn Ceiling prubenstein General Inspection Discussion 10 2/7/08 11:12 PM
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 6:03 AM


All times are GMT -4. The time now is 10:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts