Default Flue residue questions

Noted this residue on yesterdays inspection. Newer boiler ( 1990 ) venting into "Class A" type 8" chimney. Same age boiler mate water heater. Wondering if old unit ( water heater ) was gas and that's why the larger chimney. Would you write this up as "possible" orphaned type chimney? Or how? Thanks!
Attached Thumbnails
flue-residue-questions-misc-027.jpg   flue-residue-questions-misc-028.jpg  



John Springstead
Home Inspections of USA
1752 N.E. Torch Lake Dr.
Central Lake, MI 49622
1-231-544-8016 office
1-231-544-6001 fax
www.homeinspectionsusa.us
Reply With Quote
  #2  
Old 1/8/06, 6:57 PM
Steve McIntire's Avatar
Steve McIntire Steve McIntire is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Indianapolis, In
Posts: 150
Default Re: Flue residue questions

The Boiler/ water heater flue is corroded at ______ location. Recommend repairs by licensed HVAC contractor.
Reply With Quote
  #3  
Old 1/8/06, 8:18 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Flue residue questions

Quote:
Originally Posted by smcintire
The Boiler/ water heater flue is corroded at ______ location. Recommend repairs by licensed HVAC contractor.
I agree

Was there any kind of a rain cover over the flue when it exited the roof of the house?



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #4  
Old 1/8/06, 8:27 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flue residue questions

Definetly water entry/condensation causing corrosion. Recommend further evaluation by licenced heating contractor.

The chimney elargement may be too large causing poor draft, resulting in condensation forming in upper area of chimney.

Raymond Wand
Alton, ON
Reply With Quote
  #5  
Old 1/8/06, 9:52 PM
John W. Springstead's Avatar
John W. Springstead John W. Springstead is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Central Lake, MI
Posts: 143
Default Re: Flue residue questions

Thanks guys, yes there was a S.S. cap which was stained quite dark at top. Makes me wonder if the orgional unit might have been fuel oil fired. No sign of underground tank was noted though. ( 1973 home )



John Springstead
Home Inspections of USA
1752 N.E. Torch Lake Dr.
Central Lake, MI 49622
1-231-544-8016 office
1-231-544-6001 fax
www.homeinspectionsusa.us
Reply With Quote
  #6  
Old 1/9/06, 7:18 AM
jrupert jrupert is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Grove City, OH
Posts: 47
Default Re: Flue residue questions

The damage you see was caused by the flue damper pictured. This damper has 4 bi-metal vans that close when they are cool and open when they become warm, this did create an energy saving of approx 8% in it’s day. However all most all of the manufactures years ago took a position that they were damaging to the flue and furnace and thus should be removed. I vaguely recall that they may even been a government recall on all of them due to failure and that they are not equipped with any safety device should they fail

The damage occurs when the damper closes (it only block 80%) trapping still hot flue gasses in the furnace, these gasses cool and condense, they are acidic and corrode the furnace, the 20% not trapped will condense in the flue, in your picture the condensed flue gas is leaking though the joint connections damaging the pipe



John Rupert
Accurate Property Inspections
Solitaire Heating & Cooling
CSG Training (HVAC Training & Consulting)
Reply With Quote
  #7  
Old 1/9/06, 7:23 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flue residue questions

If it is former oil fired unit and carbon deposits are still in flue the condensation from gas will mix with carbon and form carbonic acid which is corrrosive.

Raymond Wand
Alton, ON
Reply With Quote
  #8  
Old 1/9/06, 7:26 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Flue residue questions

Also I don't like the junction box sitting where it is.

Raymond Wand
Alton, ON
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How many gas/oil appliances can vent into 1 flue? jberthiaume Inspecting HVAC Systems 11 10/17/07 10:09 AM
Flue Size when size matters? msylvester Inspecting HVAC Systems 14 1/20/07 11:29 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 9:10 PM
Gas Log Flue venting height. lagudo Inspecting HVAC Systems 34 4/7/06 1:42 AM


All times are GMT -4. The time now is 11:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts