I inspected a home that the oil burner and the wood stove flues were vented into the same chimney. The flues seems to be almost straight across from one another.With the log stove on one side of the wall and the oil burner on the opposite side and the flues seemed to be directed toward each other. Should the exhaust on the wood stove exit be higher than the oil burners flue or not vented together at all?
I will be waiting on the side lines, to complete this report. Thanks for any information |
|
#2
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#3
|
|||
|
|||
|
Thanks Gerry
I would like to put this in my report, were can I find that information |
|
#4
|
||||
|
||||
|
Quote:
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#5
|
|||
|
|||
|
I know things continue to change as more is learned but it MAY be allowed in some places if done with this configuration:
|
|
#6
|
||||
|
||||
|
Hi to all,
Larry, I could stand to be corrected on this one, but I do not believe that that set up would be allowed anywhere in the US, maybe that picture applies (as many CD images do) to Canadian codes. Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#7
|
||||
|
||||
|
Quote:
Roy Cooke Sr |
|
#8
|
||||
|
||||
|
Hey guys,
I will throw this out there for comment: The graphic Larry's posted strikes me as confusing... Not for the mixed fuel sharing deal but why would anyone want a wood burning stove in a basement or area next to a fuel oil heater?? ![]() That just confuses me... I can understand a wood burning stove in a living space like a big family room or similar since the concept is heat from the "cast iron" stove heating the room....right? Now if I install a whole house heating system like a fuel oil burner heater in the basement..... how can that (graphic text ) apply to this setup. when I have to install it on the "same floor".....
|
|
#9
|
|||
|
|||
|
Patrick, Not only did the customer place a log burner in the basement, but he had a log burner on the main floor as well.The flues for the log burner in the basement was two or three inches above the oil burner flue. What can I say it's Alaska and maybe the home owner was worried that the electricity would fail and his water pipes would freeze. A few years ago the home was powered by a generater and is now on electricity, this guy didn't trust that the power company is the only solution I can come up with.
Most homes I inspect have a log burner or a fire place,(winter can be very unforgiving at 70 below, not to mention almost $3.00 a gallon for heating oil),But I suggest a specialist check it out when I writing the report Thanks for the input it has helped me with the report |
|
#10
|
|||
|
|||
|
Quote:
Sometimes a wood stove is installed to be used as primary heat source with the oil funace as a back-up. (Wood can be much cheaper that oil to burn.) The two systems are connected to the same ductwork. And there is a proper way to do that, which I don't see too often around here. These people don't read manufacturer's instructions at all.. "not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#11
|
||||
|
||||
|
Quote:
Using the latest IRC as a guide, they make it clear that a wood stove (solid fuel appliance) and oil furnace should not be vented together (M1801.12), and even a common vent for oil/gas must be for the same system type (M1801.11) ... Quote:
JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#12
|
||||
|
||||
|
Thanks for clarifying that Danny.
I can see it from a new perspective now. Thanks Jae for your input also. It's not often that I see that kind of setup. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| How many gas/oil appliances can vent into 1 flue? | jberthiaume | Inspecting HVAC Systems | 11 | 10/17/07 10:09 AM |
| Gas and oil hot water tank and Boiler Share Vents | hvanderbeek | Miscellaneous Discussion for Inspectors | 8 | 1/25/07 5:22 PM |
| Flue Size when size matters? | msylvester | Inspecting HVAC Systems | 14 | 1/20/07 11:29 PM |
| Venting an oil-fired water heater | mh718 | Inspecting HVAC Systems | 3 | 11/16/06 9:36 AM |
| Gas Log Flue venting height. | lagudo | Inspecting HVAC Systems | 34 | 4/7/06 1:42 AM |