Default Flue Venting

I inspected a home that the oil burner and the wood stove flues were vented into the same chimney. The flues seems to be almost straight across from one another.With the log stove on one side of the wall and the oil burner on the opposite side and the flues seemed to be directed toward each other. Should the exhaust on the wood stove exit be higher than the oil burners flue or not vented together at all?
I will be waiting on the side lines, to complete this report.
Thanks for any information
Reply With Quote
  #2  
Old 7/7/06, 3:21 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Flue Venting

Quote:
Originally Posted by djames2
I inspected a home that the oil burner and the wood stove flues were vented into the same chimney. The flues seems to be almost straight across from one another.With the log stove on one side of the wall and the oil burner on the opposite side and the flues seemed to be directed toward each other. Should the exhaust on the wood stove exit be higher than the oil burners flue or not vented together at all?
I will be waiting on the side lines, to complete this report.
Thanks for any information
Danny I would write it up as in need of correction as you are not allowed to vent a wood stove and an oil burner into the same flue.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 7/7/06, 4:14 PM
Danny J. James Danny J. James is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: North Pole, AK
Posts: 19
Default Re: Flue Venting

Thanks Gerry
I would like to put this in my report, were can I find that information
Reply With Quote
  #4  
Old 7/7/06, 4:26 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Flue Venting

Quote:
Originally Posted by djames2
Thanks Gerry
I would like to put this in my report, were can I find that information
Danny It is a code issue based on safety, but I would not recommend quoting the code in your report, just recommend that the venting of those appliances be corrected by a licensed contractor.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 7/7/06, 10:54 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Flue Venting

I know things continue to change as more is learned but it MAY be allowed in some places if done with this configuration:
Attached Thumbnails
flue-venting-woodstove-oilfurnace-small-.jpg.jpg
Views:	110
Size:	39.9 KB
ID:	4481  
Reply With Quote
  #6  
Old 7/7/06, 11:05 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Flue Venting

Hi to all,

Larry, I could stand to be corrected on this one, but I do not believe that that set up would be allowed anywhere in the US, maybe that picture applies (as many CD images do) to Canadian codes.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #7  
Old 7/8/06, 2:56 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,621
Default Re: Flue Venting

Quote:
Originally Posted by gbeaumont
Hi to all,

Larry, I could stand to be corrected on this one, but I do not believe that that set up would be allowed anywhere in the US, maybe that picture applies (as many CD images do) to Canadian codes.

Regards

Gerry
I do not believe it is allowed here any more . A long time ago yes.
Roy Cooke Sr
Reply With Quote
  #8  
Old 7/8/06, 3:43 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Flue Venting

Hey guys,
I will throw this out there for comment:

The graphic Larry's posted strikes me as confusing... Not for the mixed fuel sharing deal but why would anyone want a wood burning stove in a basement or area next to a fuel oil heater??

That just confuses me... I can understand a wood burning stove in a living space like a big family room or similar since the concept is heat from the "cast iron" stove heating the room....right?

Now if I install a whole house heating system like a fuel oil burner heater in the basement..... how can that (graphic text ) apply to this setup. when I have to install it on the "same floor".....
Reply With Quote
  #9  
Old 7/10/06, 4:14 PM
Danny J. James Danny J. James is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: North Pole, AK
Posts: 19
Smile Re: Flue Venting

Patrick, Not only did the customer place a log burner in the basement, but he had a log burner on the main floor as well.The flues for the log burner in the basement was two or three inches above the oil burner flue. What can I say it's Alaska and maybe the home owner was worried that the electricity would fail and his water pipes would freeze. A few years ago the home was powered by a generater and is now on electricity, this guy didn't trust that the power company is the only solution I can come up with.
Most homes I inspect have a log burner or a fire place,(winter can be very unforgiving at 70 below, not to mention almost $3.00 a gallon for heating oil),But I suggest a specialist check it out when I writing the report
Thanks for the input it has helped me with the report
Reply With Quote
  #10  
Old 7/10/06, 4:43 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Flue Venting

Quote:
Originally Posted by pbolliger
Hey guys,
I will throw this out there for comment:

The graphic Larry's posted strikes me as confusing... Not for the mixed fuel sharing deal but why would anyone want a wood burning stove in a basement or area next to a fuel oil heater??

That just confuses me... I can understand a wood burning stove in a living space like a big family room or similar since the concept is heat from the "cast iron" stove heating the room....right?

Now if I install a whole house heating system like a fuel oil burner heater in the basement..... how can that (graphic text ) apply to this setup. when I have to install it on the "same floor".....

Sometimes a wood stove is installed to be used as primary heat source with the oil funace as a back-up. (Wood can be much cheaper that oil to burn.)
The two systems are connected to the same ductwork.

And there is a proper way to do that, which I don't see too often around here. These people don't read manufacturer's instructions at all..



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #11  
Old 7/10/06, 6:57 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Flue Venting

Quote:
Originally Posted by gbeaumont
Larry, I could stand to be corrected on this one, but I do not believe that that set up would be allowed anywhere in the US, maybe that picture applies (as many CD images do) to Canadian codes.
I believe that is the case. Also note that the slide indicates wood/oil common venting can be done in some jurisdictions, which I take as it's normally not allowed.

Using the latest IRC as a guide, they make it clear that a wood stove (solid fuel appliance) and oil furnace should not be vented together (M1801.12), and even a common vent for oil/gas must be for the same system type (M1801.11) ...
Quote:
M1801.11 Multiple-appliance venting systems.
Two or more listed and labeled appliances connected to a common natural draft venting system shall comply with the following requirements:
1. Appliances that are connected to common venting systems shall be located on the same floor of the dwelling.
Exception: Engineered systems as provided for in SectionG2427.
2. Inlets to common venting systems shall be offset such that no portion of an inlet is opposite another inlet.
3. Connectors serving appliances operating under a natural draft shall not be connected to any portion of a mechanical draft system operating under positive pressure.

M1801.12 Multiple solid fuel prohibited.
A solid fuel-burning appliance or fireplace shall not connect to a chimney passageway venting another appliance.
Bottom line is I would also flag that install for further evaluation by a qualified HVAC contractor, and separation of venting for the two different types of appliances as required, using current industry construction standards as a guide.

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #12  
Old 7/10/06, 7:28 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Flue Venting

Thanks for clarifying that Danny.
I can see it from a new perspective now.



Thanks Jae for your input also. It's not often that I see that kind of setup.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How many gas/oil appliances can vent into 1 flue? jberthiaume Inspecting HVAC Systems 11 10/17/07 10:09 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM
Flue Size when size matters? msylvester Inspecting HVAC Systems 14 1/20/07 11:29 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 9:36 AM
Gas Log Flue venting height. lagudo Inspecting HVAC Systems 34 4/7/06 1:42 AM