Default Forced Draft burner blow out

Simple question: Why doesn't a forced draft vent fan blow out the burners in a furnace? Seems like it would...

Thanks
Reply With Quote
  #2  
Old 2/1/06, 6:05 PM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,184
Default Re: Forced Draft burner blow out

Cause there is already a draft over the burners going up the heat exchanger. The forced draft fan just sucks it up out of the heat exchanger and spits it out.
Reply With Quote
  #3  
Old 2/1/06, 6:17 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Forced Draft burner blow out

It is actually a Forced Air Induced Draft furnace.

The Blower is on the Furnace Outlet drawing exhaust gas from the Burner thru the exchanger.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #4  
Old 2/1/06, 6:30 PM
bnelson bnelson is offline
InterNACHI Member
 
Join Date: Feb 2004
Location: Bellingham, WA
Posts: 14
Default Re: Forced Draft burner blow out

You've both described "Induced Draft Vent Fans" which are different than "Forced Draft Vent Fans." What I'm asking regards the latter, where the blower is at the burners... the start of the heat exchanger... and forces air through the system.
Reply With Quote
  #5  
Old 2/1/06, 6:50 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Forced Draft burner blow out

Quote:
Originally Posted by bnelson
You've both described "Induced Draft Vent Fans" which are different than "Forced Draft Vent Fans." What I'm asking regards the latter, where the blower is at the burners... the start of the heat exchanger... and forces air through the system.
Brandon:

Which model Furnace are you referencing?

I have only worked with Forced Draft Furnaces / Boilers within a Heavy Industrial / Chemical Environment. I have not encountered a Residential Forced Draft Furnace.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #6  
Old 2/1/06, 9:55 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Forced Draft burner blow out

Quote:
Originally Posted by jhagarty
Brandon:

Which model Furnace are you referencing?

I have only worked with Forced Draft Furnaces / Boilers within a Heavy Industrial / Chemical Environment. I have not encountered a Residential Forced Draft Furnace.
Comfortmaker had one model forced draft. The blower was attached to the burner box forcing air into the burner compartment. Thankfully discontinued.
Reply With Quote
  #7  
Old 2/2/06, 10:57 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,184
Default Re: Forced Draft burner blow out

And now you know why it was discontinued.
Reply With Quote
  #8  
Old 11/3/06, 6:59 PM
Michael S. OMalley Michael S. OMalley is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Brooklyn, NY
Posts: 13
Default Re: Forced Draft burner blow out

I recently inspected a 2002 steam boiler with a very long horizontal run to chimney (more than ten feet). In the vent pipe about two feet from the boiler there was a daft-inducing fan, presumably because the long vent gave marginal draft. The fan was wired into the boiler safety controls, and since the fan was not turning , the boiler would not fire. So I was unable to observe the boiler operation, but I did notice a thin film of rust on the cast iron boiler sections, and a couple of small stains or drip marks on the pan below the burners. I'm wondering if the long vent length is causing the flue vapors to condense when the boiler is only working intermittently, and if the resulting condensation is running down the vent pipe and rusting the boiler. I've heard that this is a problem with high-efficiency boilers with induced draft, but has anyone seen it in a regular efficiency unit with induced draft in the vent pipe?


Mike O'Malley
Reply With Quote
  #9  
Old 11/3/06, 11:39 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Forced Draft burner blow out

It is always better to suck than to blow.

However, sucking causes the blower assy to come in contact with the corrosive combustion gas.

Why it doesnt blow out?
It is a confined space. All air in, goes through the heat exchanger along with the gas. The gas pressure is higher than the blower pressure so it won't blow out.
Reply With Quote
  #10  
Old 11/6/06, 1:13 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Forced Draft burner blow out

I wonder if that would "supply " combustion air in a manner which most cat 1 Natural draft units do not have.

I am (guessing here) David ( you know this topic better than I) that this would not have that much of an effect on the burners since " pressurized jets" of N.G.) are "pulling air" (venturi??) from the open baffles (at/near) the beginning of metering value to the heat exchanger end of the burners.

Am I way off on this?

I am thinking like oxygen injection with Oxy/Acetylene torch... Burning
Different concept but similar approach....maybe
Reply With Quote
  #11  
Old 11/6/06, 7:16 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Forced Draft burner blow out

I'm think I understand what your are getting at.
If so, you are correct.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Looking for info to buy new oil burner Bill Shaw Inspecting HVAC Systems 3 11/13/07 2:51 PM
Soot from Barometric Draft Damper (posted by Ted Hull) AskNACHI.org AskNACHI.org Inspection Questions Forum 3 5/11/07 7:49 AM
bradford white forced draft water heater, recall? tdietrich1 Plumbing Inspections 3 2/5/07 11:36 AM
TSSA Gas natural draft boiler notice rwand1 Canadian Inspectors 0 9/13/06 12:37 AM


All times are GMT -4. The time now is 7:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts