I've been trying to find a chart somewhere on the free area of register covers but have been unsuccessful.
I did an inspection at a condo where the furnace was draft induced 88,000 BTU/Hr input sharing a utility closet with a 52,500 BTU/Hr input water heater. Both appliances were behind a fire door with no air input on the door. I saw 6 x 9 vent in the ceiling in the closet. The furnace mfg recommends 1 sq in of free area of outside air for every 3,000 BTU of combined appliances. In this case it would be 46.8 sq inches. 52,500 + 88,000 = 140,500 140,500/3,000 = 46.8 Sq In If there wasn't a register cover, the area would be 54 sq inches. This is really close and being technical but it's one of those DLR's. (Doesn't Look Right) And I don't want to Refer a HVAC Tech if it's OK. Greg Liebig, Owner Sheboygan Wisconsin Home Inspector 4-Square Home Inspections, LLC Where Knowledge will put your Mind at Ease © Sheboygan, WI 53081 (920) 451-4646 www.sheboyganhomeinspector.com www.4squarehi.com Like Us on Facebook Follow Us on Linked-In |
| Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Great find...We don't have gas here in SW Florida. But it appears that it is WRONG. Wish I could help more. But according what you have shown, its wrong to me and I sure would call it out.
Comprehensive Building Consultants Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection. Donate here: or send checks to the Fl Home and Insurance Inspector Chapter 1103 W Hibiscus Blvd Ste 311 Melbourne, Fl 32901
|
|
#3
|
||||
|
||||
|
According to HVAC standards 25% of the opening.
So the two openings are too small. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 Last edited by kwood; 5/18/11 at 4:10 PM.. |
|
#4
|
|||
|
|||
|
Please Note:
Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Metal grilles are rated for 75% wooden louvers are rated for 25% free area.
Remember according to code there must be two openings. One within 12 inch of ceiling and one within 12 inch of floor if this is a passive combustion air opening. Where passive combustion air proves impractical mechanical combustion air is an alternative. IMC 304.9 Mechanical combustion air supply. Where all combustion air is provided by a mechanical air supply system, the combustion air shall be supplied from the outdoors at a rate not less than 0.35 cubic feet per minute per 1,000 Btu/h (0.034 m3/min per kW) of total input rating of all appliances located within the space. Last edited by Gary Reecher; 5/18/11 at 3:08 PM.. |
|
#5
|
||||
|
||||
|
According to the standards today.
Do not mention "CODE" unless you are a "Code Official" THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#6
|
||||
|
||||
|
I write up code violations on most every inspections just don't use the word code Gary is correct should have the two pipe vent system if there is a vented attic
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Free Live Training - Lead-Safe Certified RRP Course in our Colorado Classroom | bgromicko | Inspection Education & Training | 50 | 4/4/11 5:34 PM |
| Education | Mike Mer | General Inspection Discussion | 12 | 3/1/08 3:05 PM |
| Extractd from the archives, Thanks Paul for this list! | jtedesco1 | Electrical Inspections | 4 | 1/2/07 7:51 PM |
| Free Office Software Eqiv. For Download | bmerrell | Miscellaneous Discussion for Inspectors | 4 | 12/31/06 11:47 AM |