  #1  
Old 5/18/11, 9:03 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default What is the Free Area of Register Covers?

I've been trying to find a chart somewhere on the free area of register covers but have been unsuccessful.

I did an inspection at a condo where the furnace was draft induced 88,000 BTU/Hr input sharing a utility closet with a 52,500 BTU/Hr input water heater. Both appliances were behind a fire door with no air input on the door. I saw 6 x 9 vent in the ceiling in the closet.

The furnace mfg recommends 1 sq in of free area of outside air for every 3,000 BTU of combined appliances. In this case it would be 46.8 sq inches.

52,500 + 88,000 = 140,500
140,500/3,000 = 46.8 Sq In

If there wasn't a register cover, the area would be 54 sq inches. This is really close and being technical but it's one of those DLR's. (Doesn't Look Right) And I don't want to Refer a HVAC Tech if it's OK.
Attached Thumbnails
free-area-register-covers-p1280317.jpg   free-area-register-covers-p1280331.jpg   free-area-register-covers-p1280333.jpg   free-area-register-covers-p1280339.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/18/11, 10:21 AM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: What is the Free Area of Register Covers?

Great find...We don't have gas here in SW Florida. But it appears that it is WRONG. Wish I could help more. But according what you have shown, its wrong to me and I sure would call it out.



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #3  
Old 5/18/11, 10:36 AM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: What is the Free Area of Register Covers?

According to HVAC standards 25% of the opening.
So the two openings are too small.



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676

Last edited by kwood; 5/18/11 at 4:10 PM..
Reply With Quote
  #4  
Old 5/18/11, 3:05 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: What is the Free Area of Register Covers?

Metal grilles are rated for 75% wooden louvers are rated for 25% free area.

Remember according to code there must be two openings. One within 12 inch of ceiling and one within 12 inch of floor if this is a passive combustion air opening.

Where passive combustion air proves impractical mechanical combustion air is an alternative.


IMC

304.9 Mechanical combustion air supply. Where all combustion air is provided by a mechanical air supply system, the combustion air shall be supplied from the outdoors at a rate not less than 0.35 cubic feet per minute per 1,000 Btu/h (0.034 m3/min
per kW) of total input rating of all appliances located within the space.

Last edited by Gary Reecher; 5/18/11 at 3:08 PM..
Reply With Quote
  #5  
Old 5/18/11, 4:09 PM
KEVIN WOOD's Avatar
KEVIN WOOD KEVIN WOOD is online now
InterNACHI Member
 
Join Date: Mar 2006
Location: Sault Ste Marie ON
Posts: 3,111
Default Re: What is the Free Area of Register Covers?

According to the standards today.
Do not mention "CODE" unless you are a "Code Official"



THE RIGHT TRAK
CIAQP, IAC2
Certified Master Inspector
kwoodinspections@hotmail.com
www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ
www.linkedin.com/in/kevinwoodiaq
OOVOO account kwoodinspections
Cell: 705-971-2096
Ph : 705-946-2676
Reply With Quote
  #6  
Old 5/18/11, 6:08 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: What is the Free Area of Register Covers?

Quote:
Originally Posted by kwood View Post
According to the standards today.
Do not mention "CODE" unless you are a "Code Official"
I write up code violations on most every inspections just don't use the word code Gary is correct should have the two pipe vent system if there is a vented attic



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Free Live Training - Lead-Safe Certified RRP Course in our Colorado Classroom bgromicko Inspection Education & Training 50 4/4/11 5:34 PM
Education Mike Mer General Inspection Discussion 12 3/1/08 3:05 PM
Extractd from the archives, Thanks Paul for this list! jtedesco1 Electrical Inspections 4 1/2/07 7:51 PM
Free Office Software Eqiv. For Download bmerrell Miscellaneous Discussion for Inspectors 4 12/31/06 11:47 AM


All times are GMT -4. The time now is 11:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts