Default funky heating duct

recently I encountered this situation in an old house. a duct had been run into an old unused brick chimney to transfer heat to the top level. though Ive not seen this before I did not see anything 'wrong' with it and actually considered it rather clever. I can only assume that whoever did this had the sense to seal above the exit duct upstairs (in the chimney)
...any opinions on this?
'assume' is probably a dirty word...perhaps I should have noted 'this is non standard application and status of weather seal is unknown'...or some such statement.
Attached Thumbnails
funky-heating-duct-feb28dump-071.jpg  
Reply With Quote
Need a home inspection in Kentucky? Check out InterNACHI's listing of Kentucky certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/1/11, 10:42 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: funky heating duct

Quote:
Originally Posted by minwards View Post
recently I encountered this situation in an old house. a duct had been run into an old unused brick chimney to transfer heat to the top level. though Ive not seen this before I did not see anything 'wrong' with it and actually considered it rather clever. I can only assume that whoever did this had the sense to seal above the exit duct upstairs (in the chimney)
...any opinions on this?
'assume' is probably a dirty word...perhaps I should have noted 'this is non standard application and status of weather seal is unknown'...or some such statement.
Personally I would not want no dirty old chimney providing supply air into any area that I was living in. Are you sure that the duct was not inside the old brick flue. What did the top area of the brick flue look like did it have a metal duct take off. Ya know curiosity killed the cat but satification brought it back.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #3  
Old 3/2/11, 8:16 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: funky heating duct

I'm assuming that the metal duct extends entirely through the chimney. If so, I don't see a big problem. Unconventional yes.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 3/2/11, 9:37 AM
Michael Inwards Michael Inwards is offline
InterNACHI Member
 
Join Date: Dec 2010
Location: Pelican Rapids MN
Posts: 64
Default Re: funky heating duct

to see if the duct extended upward through the whole chimney would have required pulling insulation and then observation would have been iffy. I would pretty much bet that it did not. I agree that lacking that...possible years of soot buildup could be introduced over time in the home. honestly I did not think of that.....i have a problem considering stuff like that since i have no allergies and basically nothing affects me adversely....improvement needed in me there. so opinions? would anyone call this out as a defect? or just list it as a non standard apparently functioning condition (it was, heat was coming out the top) and recommend a look by a qualified HVAC tech?.....or just figure it works, its cool....(kind of what I did)
Reply With Quote
  #5  
Old 3/2/11, 12:24 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: funky heating duct

Quote:
Originally Posted by minwards View Post
to see if the duct extended upward through the whole chimney would have required pulling insulation and then observation would have been iffy. I would pretty much bet that it did not. I agree that lacking that...possible years of soot buildup could be introduced over time in the home. honestly I did not think of that.....i have a problem considering stuff like that since i have no allergies and basically nothing affects me adversely....improvement needed in me there. so opinions? would anyone call this out as a defect? or just list it as a non standard apparently functioning condition (it was, heat was coming out the top) and recommend a look by a qualified HVAC tech?.....or just figure it works, its cool....(kind of what I did)
If the metal duct was not inside the brick flue I personally would have called it out as a defect



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Ceilings falling with wires in it. jsmith3 Interior Inspections 9 3/16/06 7:24 PM


All times are GMT -4. The time now is 11:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts