Question:
Can a high energy efficent furnace be installed in an attic that is not heated.
Reply With Quote
  #2  
Old 2/7/07, 2:35 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 3,085
Send a message via AIM to sstanczyk
Default Re: Furnace in attic (High Efficient)

Yep.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #3  
Old 2/7/07, 2:41 PM
John B. CORDELL John B. CORDELL is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Cincinnati, OH
Posts: 29
Default Re: Furnace in attic (High Efficient)

One of my inspectors just had a call from a client he did an inspection for last Spring. She said her condensation line freeze and she was told it was against code to install a high efficent furnace in a iun heated area? HELP
Reply With Quote
  #4  
Old 2/7/07, 4:14 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,992
Default Re: Furnace in attic (High Efficient)

Where do you live, Cincinnati, AK?
Reply With Quote
  #5  
Old 2/7/07, 5:18 PM
John B. CORDELL John B. CORDELL is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Cincinnati, OH
Posts: 29
Default Re: Furnace in attic (High Efficient)

I live in Cincinnati
Reply With Quote
  #6  
Old 2/7/07, 6:00 PM
John B. CORDELL John B. CORDELL is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Cincinnati, OH
Posts: 29
Default Re: Furnace in attic (High Efficient)

The furnace was a frigidare. I spoke with a compnay here in town and they claim you can install in attics. Anyone know any thing about the brand.
Reply With Quote
  #7  
Old 2/7/07, 6:00 PM
John B. CORDELL John B. CORDELL is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Cincinnati, OH
Posts: 29
Default Re: Furnace in attic (High Efficient)

The furnace was a frigidare. I spoke with a compnay here in town and they claim you can install in attics. Anyone know any thing about the brand.
Reply With Quote
  #8  
Old 2/7/07, 6:01 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 506
Default Re: Furnace in attic (High Efficient)

John

Check your local codes first. I don't know of any HVAC Manuf. that restricts the installation of H/E condensing type (90%+afue - upflow or horizontal) furnaces in Attics, Crawls or Basements. Installation requirements may differ some, but not drastically.
The freezing of the acidic condensate from the PVC flue vent piping and into the drain is most likely an installation mistake (ie: no slope, sloping the wrong way, blockage or weather ???). Call and HVAC Contractor to check it out.
Reply With Quote
  #9  
Old 2/7/07, 6:46 PM
John B. CORDELL John B. CORDELL is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Cincinnati, OH
Posts: 29
Default Re: Furnace in attic (High Efficient)

Thanks for the reply
Reply With Quote
  #10  
Old 2/8/07, 9:44 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,992
Default Re: Furnace in attic (High Efficient)

Freezing condensate should not be an issue if the unit is properly installed.
It is often considered that the flue pipe should slope towards the outside so the water will drain out. This is not the case, it should slope back towards the unit so the condensate can be stored in the furnace where the heat is.

When the furnace is in operation, everything is hot and there should be no problems with freezing condensate.

The drain line should be installed so that there is no reservoirs of standing condensate in the cold space. If traps are necessary, they should be in a location where they won't freeze.
Reply With Quote
  #11  
Old 2/8/07, 8:43 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,472
Default Re: Furnace in attic (High Efficient)

Quote:
Originally Posted by dandersen
Freezing condensate should not be an issue if the unit is properly installed.
It is often considered that the flue pipe should slope towards the outside so the water will drain out. This is not the case, it should slope back towards the unit so the condensate can be stored in the furnace where the heat is.

When the furnace is in operation, everything is hot and there should be no problems with freezing condensate.

The drain line should be installed so that there is no reservoirs of standing condensate in the cold space. If traps are necessary, they should be in a location where they won't freeze.
Very good David. I was just about to post a similar reply.

I see no problem with this install whatsoever.
Reply With Quote
  #12  
Old 2/9/07, 8:51 PM
Keith R. Braun's Avatar
Keith R. Braun Keith R. Braun is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Buffalo, NY
Posts: 108
Default Re: Furnace in attic (High Efficient)

The following comes from an ICP (Heil) installation manual for condensing gas furnaces: Special precautions MUST be madeif installing furnace in an area which may drop below freezing. This can cause improper operation or damage to the equipment. If the furnace environment has the potential for freezing, the drain trap and drain line must be protected. Use 3 to 6 watt per foot at 115 volt, 40 degree F self regulating shielded and waterproof heat tape. Wrap the drain trap and drain line with the heat tape and secure with ties. Follow the heat tape manufacturers recommendations.
Reply With Quote
  #13  
Old 2/10/07, 9:43 AM
John B. CORDELL John B. CORDELL is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Cincinnati, OH
Posts: 29
Default Re: Furnace in attic (High Efficient)

Everyone. Thanks for all the information. This was what I have been trained for for the past 15 years also. It is always good to here back from fellow inspectors. After a while its easy to start second guessing yourself after all these years.
Reply With Quote
  #14  
Old 2/10/07, 9:45 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Furnace in attic (High Efficient)

My high efficiency has a water trap. It's always filled with water, go figure. Is this not needed with an attic installation? Because I can see this quickly freezing.

tom
Reply With Quote
  #15  
Old 2/10/07, 6:02 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,992
Default Re: Furnace in attic (High Efficient)

Condensate is hot. So long as it doesn't freeze or thaws out when the unit comes back on, it should work.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Horizontal Furnace in Attic Anthony Joseph HVAC 5 10/12/07 9:08 AM
Supply Plenum Mounted High in Attic Skip Erwin HVAC 6 4/7/07 10:07 AM
Propane gas to attic furnace brepanshek HVAC 5 2/21/07 5:06 PM
Cat 1 Furnace in attic wdecker HVAC 2 6/14/06 1:28 AM
90% efficient furnace venting jrupert HVAC 2 2/16/06 3:54 PM


All times are GMT -4. The time now is 8:13 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts