Question Furnace in a bedroom closet

If a furnace is installed in a bedroom closet and the closet is properly vented to the attic and crawlspace is there any other code reference prohibiting this? I have a PG&E (gas utility) guy saying it is OK, even though the door isn't even sealed tightly.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #2  
Old 6/16/08, 9:19 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Furnace in a bedroom closet

What type of furnace Ralph?

Is there a water heater in the space too?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 6/16/08, 9:25 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Furnace in a bedroom closet

It's a forced air furnace with an induced draft fan. I researched an install a while ago with a high efficiency unit in a bedroom closet with a sealed external air supply and I had a HVAC contractor tell me that you could not have any furnace in a bedroom closet due to "storage habits of the occupants" (if my memory serves me correctly). I can't find any code reference for this though.

No water heater, but there is no phisical separation between storage space and the furnace

Thanks



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #4  
Old 6/16/08, 9:25 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: Furnace in a bedroom closet

It cannot be located in a bedroom closet if it is receiving its combustion air from the bedroom. IRC G2406.2

Check your local ordinances for a more restrictive interpretation.
Reply With Quote
  #5  
Old 6/16/08, 9:28 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Furnace in a bedroom closet

furnace-bedroom-closet-p6110030.jpg

Here is a picture



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #6  
Old 6/16/08, 9:37 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: Furnace in a bedroom closet

The return air (if that is what the grill on the floor represents) must be a minimum of 10 feet from the firebox.

Write it up.

I would not get too hung up on the proximity to the bedroom if all other factors (appropriate spacing, separate source of combustion air, etc) were met. Think about "efficiency apartments", for example, where the entire area can be considered a bedroom (except the bath).
Reply With Quote
  #7  
Old 6/16/08, 9:38 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Furnace in a bedroom closet

That's just wrong Ralph. Recommend corrections by a qualified HVAC contractor.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 6/16/08, 9:44 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Furnace in a bedroom closet

The seller is saying the utility company came out today and said the furnace install is just fine. I finally had to get curt with her and say goodbye. She is acusing me of slandering her house .



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #9  
Old 6/16/08, 9:49 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: Furnace in a bedroom closet

Quote:
Originally Posted by rbrady
The seller is saying the utility company came out today and said the furnace install is just fine. I finally had to get curt with her and say goodbye. She is acusing me of slandering her house .
Make no reference to code. Simply state that, in your opinion, there is no clear source of combustion air from outside of the bedroom and that the return air being within 10 feet of the firebox provides a safety hazard. You recommend that it be repaired by a qualified (licensed) hvac technician.

You have been contracted to provide an opinion regarding the current conditions of the systems within the home. There is no such thing as "slander" in providing an opinion you were asked to give.

If you screw up and refer to code, you are at the mercy of the local AHJ to agree or disagree with you. Don't do it.
Reply With Quote
  #10  
Old 6/16/08, 9:57 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Furnace in a bedroom closet

Ralph, is there any chance the white grille on the floor in front of the furnace is the combustion air source?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #11  
Old 6/16/08, 10:04 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace in a bedroom closet

Quote:
Originally Posted by mlarson
Ralph, is there any chance the white grille on the floor in front of the furnace is the combustion air source?
That was my guess and looks too small.
Reply With Quote
  #12  
Old 6/16/08, 10:04 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Furnace in a bedroom closet

Quote:
Originally Posted by mlarson
Ralph, is there any chance the white grille on the floor in front of the furnace is the combustion air source?
Yes it is a combustion air source. There is also a vent into the attic. They were both blocked off though. Even if the vents are opened up, the door also still needs to be sealed as far as I can tell.

My main concern was if there is a general code restriction to having the furnace in a storage closet off the bedroom.

Thank you for the replies!



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #13  
Old 6/16/08, 10:06 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Furnace in a bedroom closet

Stand your ground Ralph, you're on the right track.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #14  
Old 6/16/08, 10:35 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: Furnace in a bedroom closet

Quote:
Originally Posted by rbrady
Yes it is a combustion air source. There is also a vent into the attic. They were both blocked off though. Even if the vents are opened up, the door also still needs to be sealed as far as I can tell.

My main concern was if there is a general code restriction to having the furnace in a storage closet off the bedroom.

Thank you for the replies!
There is no "general code restriction to having the furnace in a storage closet off of the bedroom".

If you use the word "code" in your report and the seller decides to sue...you will pay a hefty sum.

IRC does prohibit a furnace in a storage closet....but if the seller removes all items from the closet before the AHJ arrives, all he will see is an enclosure with a furnace in it. "Off the bedroom" is not a consideration.

You mentioned that the seller has already begun using litigious language in conversation with you. You should stay away from citing or referring to code anywhere in your report or your conversations in this instance.
Reply With Quote
  #15  
Old 6/17/08, 12:08 AM
dbucknavich dbucknavich is offline
Active Poster
 
Join Date: Feb 2006
Location: Chandler, AZ
Posts: 653
Please Note: dbucknavich is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace in a bedroom closet

G2406.2 in the IRC mentions what your looking for, but there are exceptions. Regardless, that is for your information only and should not be quoted to anyone else involved in the transaction.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
Return in Furnace closet dmacy HVAC 2 2/24/08 4:30 PM
Newbie here with a slab "standards" question Robert Young, #3 Structural 17 4/10/07 11:48 AM
Fininshed bedroom in basement next furnace cyezza HVAC 9 11/28/06 6:41 AM


All times are GMT -4. The time now is 9:59 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts