Default Furnace components

This is a 3 year old bryant furnace installed on the 2nd level of a townhome.

I recommended an HVAC specialist for about 5 reasons.

1/ The serviceman switch wasnt functional due to the PVC flue being right on top of the switch.
2/ The PVC flue that vented through the roof wasnt properly connected at the roof flange.
3/ The filter access was poor at best. You have to remove 8 screws and then you may be able to remove the filter.
4/ Excesive noise in the cabinet. Sounded like the induced dratf fan.

5/ The pipe coming of the cold air return has an access panel cut in the kitchen but the pipe doesnt terminate anywhere.

The utility room has enough compustion air as the door is louvered & vented.
Why was this other vent added?

I pictured in order of the #'s

Thanks

Dave
Attached Thumbnails
furnace-components-79406-fairlawn-010-small-.jpg.jpg
Views:	35
Size:	26.7 KB
ID:	5171   furnace-components-79406-fairlawn-011-small-.jpg.jpg
Views:	35
Size:	34.9 KB
ID:	5172   furnace-components-79406-fairlawn-013-small-.jpg.jpg
Views:	37
Size:	60.8 KB
ID:	5173   furnace-components-79406-fairlawn-016-small-.jpg.jpg
Views:	36
Size:	32.1 KB
ID:	5174   furnace-components-79406-fairlawn-015-small-.jpg.jpg
Views:	37
Size:	31.7 KB
ID:	5175  

Reply With Quote
  #2  
Old 8/22/06, 4:07 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Furnace components

Are you needing help with anything specific Dave?



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #3  
Old 8/22/06, 4:46 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Furnace components

Thanks Russ

I need help understand the duct that is installed in the return air and doesnt have an opening that I could see at the access panel. I find it strange that there is an access panel for a duct. I thought maybe they added the duct for return air from the outside, but it doesnt go outside. Seems strange to me.

Dave
Attached Thumbnails
furnace-components-79406-fairlawn-016-small-.jpg.jpg
Views:	14
Size:	32.1 KB
ID:	5201   furnace-components-79406-fairlawn-017-small-.jpg.jpg
Views:	18
Size:	36.7 KB
ID:	5202   furnace-components-79406-fairlawn-015-small-.jpg.jpg
Views:	11
Size:	31.7 KB
ID:	5203  
Reply With Quote
  #4  
Old 8/22/06, 4:54 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Furnace components

I usually stay out of the furnace topics, preferring to read and learn since it is not my strong point. However, I'll take a shot at this one.

That looks to be one of the newer high-efficiency units, so I suspect that it replaced an older unit. I suspect that the vents were not added but were already there for the older system.

High-efficiency systems can be unique in their operation, maintenance, and installation, so if the manufacturer's installation guide is not at the furnace (I usually find them there with the hi-eff systems), then a visit to the manufacturer's web site or a recommendation to say, "Hi-eff systems are fairly new [on the market/in my area/here in Hicksville/whatever] and I don't have enough experience or knowledge to make a proper determination concerning this installation. Recommend further evaluation by a licensed heating and cooling professional familiar with hi-eff systems." If you want, you can offer to pay for the service call from the licensed HVAC tech if and only if no problems are found. If he determines that there are problems, then he typically will waive his service charge if he gets to make the repairs. So offer to pay if and only if no problems are found. Good marketing.

I think I was reading over on inspectionnews.com that it is okay for the hi-eff units to pull air from the attic or to terminate their exhaust flues in the attic, but I can't find the thread right now, so I could be dead wrong. Ms Margarita and Dr Cuervo might have taken some of my memory cells to the beach with them today.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 8/22/06, 5:27 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Furnace components

After looking at your pics again, let me suggest something.
Since the 6" pipe attached to the return air duct at the top of this down-draft furnace terminates somewhere on the first level I suspect it is fresh air intake for the house OR cold air return for at least part of the lower level. There should be a vent/grill somewhere. Good luck and perhaps someone else will comment.

Is the access panel in the kitchen ceiling the only access on that level?

This would be a great place to use an inspection mirror to see where the pipe goes.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #6  
Old 8/23/06, 6:06 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,792
Default Re: Furnace components

Dave

access doors are for access right, maybe there is a shut off valve for water,gas above duct? or electrical junction box? maybe the duct was added later? have you put your hands in behind the duct,felt for valve of some sort?

In any event good call "further evaluation"

just my thoughts
mario





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #7  
Old 8/23/06, 6:10 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,792
Default Re: Furnace components

Dave

Scrap the hand suggestion,Michael is right use mirror!!!!!

mario





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #8  
Old 8/23/06, 8:40 PM
Bruce M. Graham, III's Avatar
Bruce M. Graham, III Bruce M. Graham, III is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 1,607
Default Re: Furnace components

poor install, no filter rack, no gas line drip leg. Have you looked at the duct work to make sure it is a downflow, I have seen many put in backwards.
Write it up for further evaluation for certified HVAV contractor and get out of harms way.
Happy Inspecting
Reply With Quote
  #9  
Old 8/23/06, 9:29 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,247
Default Re: Furnace components

Speaking of upside down, is this upside down?
Attached Thumbnails
furnace-components-fauud.jpg  



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues 293 2/10/08 2:20 AM
Furnace Problem Comments Welcome rfrost HVAC 24 10/21/07 7:26 PM
Furnace Not Responding vsantos HVAC 4 9/18/07 9:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM


All times are GMT -4. The time now is 12:24 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts