I am working with a HUD program and the plumber says he cannot install a T or 90 degree on the exhaust coming out the roof. I used to work for a plumber and we installed 2 45 degrees to long sweep the 90 degrees.
I just want to know why it is not legal as the plumber was very rude about not installing it. If there is rule about it fine, if not he will be dropped from the HUD contractors we use. I cannot find any rheem manulas online so I may have to go to a HVAC compnay and ask |
| Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I think the plumber is right.
You can contact Rheem with the model/serial numbers of the furnace if there really is a concern. But most higher efficiency furnace manufacturers (including Rheem) specifically do not want an elbow or tee on the exhaust (that is only installed on the intake). See Pg 25 of this Rheem RGFD series installation manual for an example of what I am talking about ... www.allreds.net/WS2/docs/rhe/rgfd_manual.pdf Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 6/14/11 at 7:39 AM.. |
|
#3
|
|||
|
|||
|
Great reference Robert, Wish I would have had it a week ago when I took a Commercial Building Code Inspector Exam.
Actual question dealt with that, along with the height from roof. The height answers we normally associate 3 feet, 2 feet, and 10 feet from etc. The answers were 2 feet above and 2 feet from, 3 feet above and 3 feet from, 18 inches and 3 feet from. There is more information as well in the International Mechanical Code (IMC) and International Existing Building Code (IEBC). Just another reason we have all the license and training requirements. |
|
#4
|
||||
|
||||
|
If permitted...
It is the first time I have ever seen PVC vent run the B Vent. How are the pipes sealed exiting the metal vent? Is this common in your area? Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#5
|
||||
|
||||
|
The pipes were caulked, you see this once in awhile.
This home had no basement and is single a level and the plumber was crying that he could not get it to the exterior walls with hanging it from the ceiling exposed. The home owner of course did not want that, so he decided to reuse the chimney with the pvc. |
|
#6
|
||||
|
||||
|
The PVC could have been routed thru the roof and properly flashed (at an additional expense).
Routing thru the existing B Vent may have been what the Homeowner wanted but that does not make it an approved installation Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Water Heater Exhaust Location with Furnace and Masonry Chimney | gliebig | Inspecting HVAC Systems | 2 | 5/13/11 6:09 PM |
| Furnace exhaust too close to heat pump | Dale Trach | Inspecting HVAC Systems | 0 | 4/26/11 8:24 PM |
| The Importance of Bathroom and Kitchen Fans | mkyriacou | Interior Inspections | 35 | 6/4/10 5:27 PM |
| 980 Questions/Answers to the NHIE....Free! | jbushart | Legislation, Licensing & Legal Issues for Inspectors | 50 | 4/20/08 1:26 AM |
| Exhaust fan in room with gas water heater and furnace | jweinberg | Inspecting HVAC Systems | 7 | 2/18/06 1:23 PM |