Default Furnace Exhaust Clearance

Does this insulation need to be clear of the furnace exhaust vent?
Attached Thumbnails
furnace-exhaust-clearance-dscn0390.jpg  
Reply With Quote
  #2  
Old 12/11/06, 10:00 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Furnace Exhaust Clearance

Quote:
Originally Posted by kblair1
Does this insulation need to be clear of the furnace exhaust vent?
In this state double or single wall pipe must be at least 4 inches from combustible.
Reply With Quote
  #3  
Old 12/11/06, 11:16 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Exhaust Clearance

i believe the standards are 1" clearance for B vent and 6" for single wall vent.

of course, as Charley pointed out, state or local requirements may reign supreme.
Reply With Quote
  #4  
Old 12/22/06, 2:32 AM
Jeremy Tucker Jeremy Tucker is offline
New User
 
Join Date: Dec 2006
Location: Spruce Grove, Alberta, Canada
Posts: 7
Please Note: Jeremy Tucker is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Exhaust Clearance

CC has it right for the minimum clearance from combustables. 1" for B vent, 6" for C vent (single wall), BUT... the clearance for single wall CAN be reduced to 1" if a heat shield (sheet metal) is installed between the vent and the combustable surface. But to be sure, check local regulations.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
clearance of side wall exhaust for FP psiposs Inspecting HVAC Systems 3 4/13/07 11:41 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 9:17 PM
Oil Furnace Flue Clearance jfunderburk Inspecting HVAC Systems 3 2/28/06 8:17 PM
Exhaust fan in room with gas water heater and furnace jweinberg Inspecting HVAC Systems 7 2/18/06 2:23 PM


All times are GMT -4. The time now is 8:47 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts