  #1  
Old 5/19/11, 5:52 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Furnace flue

Can someone with more knowledge help me out here? Is there a problem with this installation of this flue from this furnace? I looked at it and it didn't look right to me. The furnace is on the left and chimney on the right. Only about 4 feet from furnace to chimney.
Attached Thumbnails
furnace-flue-148.jpg   furnace-flue-135.jpg  



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/19/11, 6:04 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Furnace flue

Does the furnace have an inducer draft motor?



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #3  
Old 5/19/11, 6:23 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Furnace flue

yes it does



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #4  
Old 5/19/11, 7:11 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Furnace flue

It looks like the water heater connects to the furnace pipe by a tee. If so, it should be a wye so the exhaust gases do not take the easy way out via at the water heater.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #5  
Old 5/19/11, 7:14 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Furnace flue

Also if that is an opening a ways down below the metal flue on the chimney, it needs to be closed up for the chimney will create a better draft.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #6  
Old 5/19/11, 7:51 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Furnace flue

Why you should not reduce

If your appliance has a blower to assist with draft (most of the newer units do) you definitely want to reconsider reducing your pipe diameter.

When your appliance tries to push 35 Cubic Feet of air through an opening that was only designed to move 20 cubic feet, you are immediately faced with a problem. As most stoves are designed to solely to vent exhaust gases, this reduction in flue size forces the motor to act not as a blower, but as a compressor. As most integral motors are not designed for this function, you will experience severe wear and tear on all moving and stationary parts, often voiding your warranty and requiring early replacement of the unit.

Keep in mind that most manufacturers of pipe do not even fabricate or produce any type of reduction collar for these reasons
Attached Thumbnails
furnace-flue-vent-reduction.jpg  
Reply With Quote
  #7  
Old 5/19/11, 8:14 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Furnace flue

The pipe is enlarging as it is going to the chimney, not getting smaller.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #8  
Old 5/19/11, 8:17 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Furnace flue

Quote:
Originally Posted by belliott View Post
Why you should not reduce

If your appliance has a blower to assist with draft (most of the newer units do) you definitely want to reconsider reducing your pipe diameter.

When your appliance tries to push 35 Cubic Feet of air through an opening that was only designed to move 20 cubic feet, you are immediately faced with a problem. As most stoves are designed to solely to vent exhaust gases, this reduction in flue size forces the motor to act not as a blower, but as a compressor. As most integral motors are not designed for this function, you will experience severe wear and tear on all moving and stationary parts, often voiding your warranty and requiring early replacement of the unit.

Keep in mind that most manufacturers of pipe do not even fabricate or produce any type of reduction collar for these reasons
Bob,
That is an "increase", not a reduction in size. Flow is from left (HVAC) to right (chimney).
Reply With Quote
  #9  
Old 5/19/11, 8:22 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Furnace flue

Look again as it reduces at that collar or are you not looking straight.
First it constricts at the join point of that connector for no apparent reason.

Do you not see the angle on the green lines I drew.

The volume of air is restricted by at least 20% at that point.

This is not an A/C line expansion device as far as I can tell.

Last edited by belliott; 5/19/11 at 8:26 PM..
Reply With Quote
  #10  
Old 5/19/11, 8:39 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Furnace flue

The pipe coming from the furnace looks like a piece of B-vent to me, if so then there is no reduction. It just looks that like there is a reduction.



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #11  
Old 5/19/11, 8:45 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Furnace flue

Quote:
Originally Posted by jbraun View Post
The pipe coming from the furnace looks like a piece of B-vent to me, if so then there is no reduction. It just looks that like there is a reduction.
Agree, looks like (double wall) on left, increasing towards (single wall) of larger diameter on the right.

Look at the second pic. The outside diameter on the left is smaller than the outside diameter on the right.

My guess is a 3" or 4" ID up to a 5" or 6" ID.
Reply With Quote
  #12  
Old 5/19/11, 9:19 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Furnace flue

I thought it reduced in size at the connection and why I asked for assistance. Just my eye playing tricks on me. B-vent into a single wall.
That cleanout is for the fireplace chimney.



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #13  
Old 5/21/11, 11:46 AM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace flue

It is best to have a 12 inch rise before adding an elbow on water heaters, most manufacturers require at least 6 inches. Looks like that one has none.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Coming soon. Free, online, fireplace and chimney inspection course. gromicko General Inspection Discussion 15 12/14/09 4:19 PM
Furnace flue / insulation bhartley Inspecting HVAC Systems 9 3/15/09 4:53 PM
What's Inside A Chimney mcyr Inspecting HVAC Systems 14 9/17/08 6:11 PM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 1:26 AM
Oil Furnace Flue Clearance jfunderburk Inspecting HVAC Systems 3 2/28/06 7:17 PM


All times are GMT -4. The time now is 11:10 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts