I ran across this today. The flue for the gas furnace is against the closet wall. The exterior of the flue where it touched the wall was around 100 degrees. I think the flue should be routed so it's away from the wall. Could this be a fire rated material on the closet wall? It's brown, about a 1/4 of an inch thick? The other thing here is the logo and lettering on the furnace cabinet. It's upside down. Is it posible to install a furnace upside down? HA HA.
|
|
#2
|
||||
|
||||
|
G2426.4 (502.4) Insulation shield.
Where vents pass through insulated assemblies, an insulation shield constructed of not less than 26 gage sheet (0.016 inch) (0.4 mm) metal shall be installed to provide clearance between the vent and the insulation material. The clearance shall not be less than the clearance to combustibles specified by the vent manufacturer’s installation instructions. Where vents pass through attic space, the shield shall terminate not less than 2 inches (51 mm) above the insulation materials and shall be secured in place to prevent displacement. Insulation shields provided as part of a listed vent system shall be installed in accordance with the manufacturer’s installation instructions. This section of the IRC is talking about where B-vent passes through a wall. The B-vent should also be kept 2" away from any combustable materials. If the wall is drywall, then that is not considered a combustable material. If studs are present near the opening of the drywall or any NMC, then that would be an issue. Hope this helps. Sincerely, Charles M. Bellefontaine Bellman Group, Inc. 877-316-0600 Extension #802 Click Here to Join our Email Newsletter Get Illinois Home Inspector Pre-License Education and Continuing Education at www.bellmangroup.com |
|
#3
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#4
|
||||
|
||||
|
Is'nt it things like this that make you think and say, hell it might not make the house burn down, but couldn't they have tried to make the stinking thing right to begin with and save someone else some money to pay someone in pointing that out?
Amazing isn't it? Marcel Cyr Home Inspections IAC2 Certified NACHI04070211 http://co.nachi.org/inachiawards/inachiawards551.html http://co.nachi.org/inachiawards Commercial Builder Ouellet Associaties Inc. |
|
#5
|
|||
|
|||
|
Please Note:
bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
isnt the paper backing on drywall a combustible?
|
|
#6
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#7
|
|||
|
|||
|
Please Note:
Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would guess then that a b vent touching fiberglass insulation would be ok since fiberglass is non-combustible. Correct?
|
|
#8
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#9
|
|||
|
|||
|
Please Note:
jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not acceptable
|
![]() |
| Thread Tools | |
| Display Modes | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| VIDEO--Bowed Basement Wall, Cracks etc | john bubber | Structural | 75 | 7/21/08 6:25 PM |
| Single wall furnace flue | sspradling | HVAC | 8 | 6/29/07 8:23 PM |
| H2O heater and furnace wall mounted? | moliver | General Inspection Discussion | 1 | 7/9/06 8:31 AM |