  #1  
Old 4/23/07, 4:13 PM
Skip Erwin Skip Erwin is offline
New User
 
Join Date: Jun 2006
Posts: 91
Please Note: Skip Erwin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Furnace Flue Against Wall

I ran across this today. The flue for the gas furnace is against the closet wall. The exterior of the flue where it touched the wall was around 100 degrees. I think the flue should be routed so it's away from the wall. Could this be a fire rated material on the closet wall? It's brown, about a 1/4 of an inch thick? The other thing here is the logo and lettering on the furnace cabinet. It's upside down. Is it posible to install a furnace upside down? HA HA.
Attached Thumbnails
furnace-flue-against-wall-flue_and_wall.jpg  
Reply With Quote
  #2  
Old 4/23/07, 4:49 PM
cbellefontaine's Avatar
cbellefontaine cbellefontaine is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Bolingbrook, IL
Posts: 65
Send a message via MSN to cbellefontaine
Default Re: Furnace Flue Against Wall

G2426.4 (502.4) Insulation shield.
Where vents pass through insulated assemblies, an insulation shield constructed of not less than 26 gage sheet (0.016 inch) (0.4 mm) metal shall be installed to provide clearance between the vent and the insulation material. The clearance shall not be less than the clearance to combustibles specified by the vent manufacturer’s installation instructions. Where vents pass through attic space, the shield shall terminate not less than 2 inches (51 mm) above the insulation materials and shall be secured in place to prevent displacement. Insulation shields provided as part of a listed vent system shall be installed in accordance with the manufacturer’s installation instructions.

This section of the IRC is talking about where B-vent passes through a wall. The B-vent should also be kept 2" away from any combustable materials. If the wall is drywall, then that is not considered a combustable material. If studs are present near the opening of the drywall or any NMC, then that would be an issue. Hope this helps.



Sincerely,
Charles M. Bellefontaine

Bellman Group, Inc.
877-316-0600 Extension #802
Click Here to Join our Email Newsletter

Get Illinois Home Inspector Pre-License Education and
Continuing Education at www.bellmangroup.com

Low cost professional report writing with a contact
management system. www.myreportwriter.com
Reply With Quote
  #3  
Old 4/23/07, 8:39 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Furnace Flue Against Wall

Quote:
Originally Posted by cbellefontaine
G2426.4 (502.4) Insulation shield.
Where vents pass through insulated assemblies, an insulation shield constructed of not less than 26 gage sheet (0.016 inch) (0.4 mm) metal shall be installed to provide clearance between the vent and the insulation material. The clearance shall not be less than the clearance to combustibles specified by the vent manufacturer’s installation instructions. Where vents pass through attic space, the shield shall terminate not less than 2 inches (51 mm) above the insulation materials and shall be secured in place to prevent displacement. Insulation shields provided as part of a listed vent system shall be installed in accordance with the manufacturer’s installation instructions.

This section of the IRC is talking about where B-vent passes through a wall. The B-vent should also be kept 2" away from any combustable materials. If the wall is drywall, then that is not considered a combustable material. If studs are present near the opening of the drywall or any NMC, then that would be an issue. Hope this helps.
I believe B-vent components need only 1" clearance to combustibles.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #4  
Old 4/23/07, 9:33 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,377
Default Re: Furnace Flue Against Wall

Is'nt it things like this that make you think and say, hell it might not make the house burn down, but couldn't they have tried to make the stinking thing right to begin with and save someone else some money to pay someone in pointing that out?

Amazing isn't it?

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #5  
Old 4/24/07, 9:49 AM
bmargiotti bmargiotti is offline
New User
 
Join Date: Feb 2005
Location: Berea, OH
Posts: 66
Please Note: bmargiotti is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue Against Wall

isnt the paper backing on drywall a combustible?
Reply With Quote
  #6  
Old 4/24/07, 10:04 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Furnace Flue Against Wall

Quote:
Originally Posted by bmargiotti
isnt the paper backing on drywall a combustible?
First paragraph of page 2 of Manufacturer's PDF sheet and read NFPA info of WORD doc.
Attached Files
File Type: pdf Drywall not combustible.pdf (65.2 KB, 106 views)
File Type: doc drywall non combustible 2.doc (22.0 KB, 40 views)



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 4/26/07, 4:20 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 211
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue Against Wall

I would guess then that a b vent touching fiberglass insulation would be ok since fiberglass is non-combustible. Correct?
Reply With Quote
  #8  
Old 4/26/07, 8:12 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,745
Default Re: Furnace Flue Against Wall

Quote:
Originally Posted by Scott Schultz
I would guess then that a b vent touching fiberglass insulation would be ok since fiberglass is non-combustible. Correct?
Correct...but watch out for the paper or foil backed batts.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #9  
Old 4/27/07, 9:30 PM
jlybolt jlybolt is offline
Active Poster
 
Join Date: Feb 2005
Location: Conroe, TX
Posts: 305
Please Note: jlybolt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Flue Against Wall

Not acceptable
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
VIDEO--Bowed Basement Wall, Cracks etc john bubber Structural 75 7/21/08 6:25 PM
Single wall furnace flue sspradling HVAC 8 6/29/07 8:23 PM
H2O heater and furnace wall mounted? moliver General Inspection Discussion 1 7/9/06 8:31 AM


All times are GMT -4. The time now is 12:36 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts