Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#2
|
||||
|
||||
|
Wouldn't that chimney need to be run clear up to the next level...something about 3' above, with-in 10' of the highest point??? That would make it very wrong.
Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right!
|
|
#3
|
||||
|
||||
|
Please Note:
gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hi Joe,
The general requirement for a stack like this would be a minimum of 3 feet high as well as 2 feet higher than any roof within 10 feet horizontally. It most definately is not two feet higher than the nearest roof. Needs further evaluation. The siding also appears (from your picture) to not have proper clearance from the asphalt shingles. Wonder if this roof was added on. Hope things are going good for you Joe. Regards Last edited by gbrasseur; 1/27/07 at 3:39 AM.. |
|
#4
|
||||
|
||||
|
Last edited by dvalley; 1/27/07 at 4:42 AM.. |
|
#5
|
||||
|
||||
|
Please Note:
gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Regards[/quote] |
|
#6
|
||||
|
||||
|
Please Note:
Chimney Pro is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hi Joe,
Greg's post is spot-on. Seems like an addition/after-thought without much design-thought! |
|
#7
|
||||
|
||||
|
Those measurements are correct on distance from objects. Even without that standard, check out the siding near the vent cap. Easy one to write up, with ample info on the condition of the siding alone.
Priority One Building Inspection Services d/b/a Home Check America Office: 866-245-4663 Cell: 815-715-6237 Full member InterNACHI: 06010792 IL license: 450.003154
|
|
#8
|
||||
|
||||
|
Thanks everyone.
Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Gas Furnace Flue | Skip Erwin | HVAC | 1 | 9/6/07 10:24 PM |
| Single wall furnace flue | sspradling | HVAC | 8 | 6/29/07 8:23 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | HVAC | 7 | 3/8/07 9:17 PM |
| Furnace flue how close to wood | abishop | HVAC | 13 | 5/30/06 3:15 AM |
| Oil Furnace Flue Clearance | jfunderburk | HVAC | 3 | 2/28/06 8:17 PM |