Default Furnace flue termination clearances

Don't look right. Anyone know the allowable clearance for the vent cap?

furnace-flue-termination-clearances-012607-053-small-.jpg.jpg
Views:	96
Size:	33.4 KB
ID:	8729 furnace-flue-termination-clearances-012607-054-small-.jpg.jpg
Views:	73
Size:	29.1 KB
ID:	8730



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #2  
Old 1/27/07, 3:19 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 360
Default Re: Furnace flue termination clearances

Wouldn't that chimney need to be run clear up to the next level...something about 3' above, with-in 10' of the highest point??? That would make it very wrong.



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #3  
Old 1/27/07, 3:36 AM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 419
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace flue termination clearances

Hi Joe,
The general requirement for a stack like this would be a minimum of 3 feet high as well as 2 feet higher than any roof within 10 feet horizontally. It most definately is not two feet higher than the nearest roof. Needs further evaluation. The siding also appears (from your picture) to not have proper clearance from the asphalt shingles. Wonder if this roof was added on.

Hope things are going good for you Joe.

Regards

Last edited by gbrasseur; 1/27/07 at 3:39 AM..
Reply With Quote
  #4  
Old 1/27/07, 4:33 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: Furnace flue termination clearances


Last edited by dvalley; 1/27/07 at 4:42 AM..
Reply With Quote
  #5  
Old 1/27/07, 12:48 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 419
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace flue termination clearances

Quote:
as well as 2 feet higher than any roof within 10 feet horizontally
.

Regards[/quote]
Reply With Quote
  #6  
Old 3/13/07, 4:13 PM
Chimney Pro's Avatar
Chimney Pro Chimney Pro is offline
New User
 
Join Date: Mar 2007
Location: Pottstown, PA
Posts: 9
Please Note: Chimney Pro is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace flue termination clearances

Hi Joe,
Greg's post is spot-on. Seems like an addition/after-thought without much design-thought!
Reply With Quote
  #7  
Old 3/19/07, 10:31 AM
Dennis McAuley's Avatar
Dennis McAuley Dennis McAuley is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Hoffman Estates, IL
Posts: 812
Default Re: Furnace flue termination clearances

Those measurements are correct on distance from objects. Even without that standard, check out the siding near the vent cap. Easy one to write up, with ample info on the condition of the siding alone.



Priority One Building Inspection Services d/b/a Home Check America

Office: 866-245-4663
Cell: 815-715-6237
Full member InterNACHI: 06010792
IL license: 450.003154
Reply With Quote
  #8  
Old 3/19/07, 11:46 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Furnace flue termination clearances

Thanks everyone.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas Furnace Flue Skip Erwin HVAC 1 9/6/07 10:24 PM
Single wall furnace flue sspradling HVAC 8 6/29/07 8:23 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM
Furnace flue how close to wood abishop HVAC 13 5/30/06 3:15 AM
Oil Furnace Flue Clearance jfunderburk HVAC 3 2/28/06 8:17 PM


All times are GMT -4. The time now is 5:44 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts