  #1  
Old 7/5/09, 9:53 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Furnace in garage

Doing some research before the inspection. Furnace in garage apparently heats the garage and a family room. There isn't any appilcation where this is allowed is there?
Thanks in advance!
Reply With Quote
Find an InterNACHI certified Delaware Home Inspector (and anywhere else in North America)
  #2  
Old 7/5/09, 10:17 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,684
Default Re: Furnace in garage

No. You can do the garage only, but not an interior space with the garage.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #3  
Old 7/5/09, 10:30 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,636
Default Re: Furnace in garage

David even if there is no return air from the garage? and a fire damper?
Reply With Quote
  #4  
Old 7/5/09, 10:53 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,684
Default Re: Furnace in garage

A supply register into the garage will pressurize the garage and de-pressurize the house. Both will cause efficiency issues and CO poisoning potential.

Pushing air into the garage will want to find it's way back to the house. The house, in a low atmosphere will suck all it can from that garage which is even a higher atmosphere than outdoors.

Fire damper will correct the fire barrier issue between the garage and house.
Air quality is still a concern.

I am not discussing code issues, only design issues.
Too much gets past the code department to concern myself with their views.



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #5  
Old 7/5/09, 10:57 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 7,636
Default Re: Furnace in garage

Quote:
Originally Posted by dandersen View Post
A supply register into the garage will pressurize the garage and de-pressurize the house. Both will cause efficiency issues and CO poisoning potential.

Pushing air into the garage will want to find it's way back to the house. The house, in a low atmosphere will suck all it can from that garage which is even a higher atmosphere than outdoors.

Fire damper will correct the fire barrier issue between the garage and house.
Air quality is still a concern.

I am not discussing code issues, only design issues.
Too much gets past the code department to concern myself with their views.
I am on your side of the fence David The reason i asked i wrote one up and got kicked in the butt because the code guy approved it . At least i can sleep at night .
Reply With Quote
  #6  
Old 7/5/09, 11:37 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,684
Default Re: Furnace in garage

Ah..... another "case in point"!

I'm used to getting my butt kicked!

If the client wants to listen to the code guy, that's no longer my problem...

I sleep just fine!

Wrong is wrong, no matter how many times it's done wrong, it's still wrong!



"Insanity: doing the same thing over and over again and expecting a different results." Albert Einstein

David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Level III Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620
BPI# 5015804
Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #7  
Old 7/6/09, 8:49 AM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Furnace in garage

Thanks for the imput, common sense and safety always comes first.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage located furnace sfalvey Inspecting HVAC Systems 7 7/25/08 4:51 AM
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
furnace adjacent to garage...Kaboom? jweinberg Inspecting HVAC Systems 11 7/21/06 9:56 AM


All times are GMT -4. The time now is 2:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts