Default Furnace installed upside down

I inspected a new construction condo in Chicago today, The new Carrier Furnace was installed upside down, and because it was installed upside down it had 5 90 elbow in the vent pipe.

Does anyone have any information about if Carrier unit can be installed upside down. I have emailed Carrier but no reply yet.

Thank for the help
Michael



Michael Cotten
Cornerstone Home Inspections Inc
www.cornerstonehomeinspect.net
cornerstone235@aol.com
Reply With Quote
  #2  
Old 5/27/06, 11:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Furnace installed upside down

There are "down flow" FAU's, but it sounds like you've described an improper installation. Do you have any pictures?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 5/27/06, 11:53 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Furnace installed upside down

Quote:
Originally Posted by mcotten
Does anyone have any information about if Carrier unit can be installed upside down.
Maybe....try: http://www.ashrae.org/template/Asset...?assetid=13417
Reply With Quote
  #4  
Old 5/28/06, 4:48 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Furnace installed upside down

Quote:
Originally Posted by mcotten
The new Carrier Furnace was installed upside down
In my area, that would mean that it is in the crawl space instead of the attic.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 5/28/06, 7:12 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace installed upside down

Five 90 degree elbows? I believe each elbow is the equivalent of 20' of horizontal run. That means you have in theory 100' of exhaust vent. I also don't understand how a furnace can be installed upside down without changing the burners and heat exchanger othewise it would not be firing properly, et ceteras.
Reply With Quote
  #6  
Old 5/28/06, 8:49 AM
mcotten mcotten is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Hoffman Estates, IL
Posts: 19
Default Re: Furnace installed upside down

Michael,

Thanks for the link. Very informative.

Michael



Michael Cotten
Cornerstone Home Inspections Inc
www.cornerstonehomeinspect.net
cornerstone235@aol.com
Reply With Quote
  #7  
Old 6/14/06, 6:27 AM
jmcmahan jmcmahan is offline
InterNACHI Member
 
Join Date: May 2006
Location: Jamestown, Oh
Posts: 9
Default Re: Furnace installed upside down

carrier does make multi posistional furnaces they can be flipped for any postion upflow,downflow,horizontal,but the flue is able to be moved too sounds like maybe installer error
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Problem Comments Welcome rfrost Inspecting HVAC Systems 28 10/21/07 6:26 PM
Hot Air furnace installed on wood floor dbelmont Inspecting HVAC Systems 4 7/24/07 8:22 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph Inspecting HVAC Systems 2 6/6/07 2:56 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer Inspecting HVAC Systems 19 4/9/07 8:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM


All times are GMT -4. The time now is 7:06 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts