Good Morning, I have been having a situation in my own house that is driving me crazy. A few days ago (in the morning) my furnace did not kick on when the programmable themostat called for heat. When you turned the thermostat off and on the furnace then turned on.
The next day it did it and I changed the batteries. The next day it did it so I changed the thermostat. It did it again this morning....(new thermostat, new batteries) It only happens when it goes from the night time setting to the morning setting. When it is running in the afternoon and evening (when I am home) it kicks on every time it calls for heat. Any thoughts? Am I missing something small or big? Thanks Randy |
|
#2
|
|||
|
|||
|
Please Note:
Michael Martin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Strange. Next time this happens, check to see if there is 24v present at the R and W terminals at the furnace (where the thermostat wires are connected). (This assumes your furnace uses 24v controls.) If so, then it is not a thermostat issue.
|
|
#3
|
|||
|
|||
|
Thanks Michael,
I'll give that a try, seems odd it only happens in the morning. Maybe I can force it to happen this afternoon. Thanks Randy |
|
#4
|
||||
|
||||
|
Randolph,
What a coincidence. My furnace does the same exact thing and it's only 9 years old. I figured it out though. When the outside temperatures drop below 10 degrees, my furnace refuses to kick on by itself between cycles. I have to continuously re-set the furnace breaker until the house reaches my desired temperature. When the house reaches the desired temperature, the furnace is absolutely fine. I had several HVAC techs evaluate this strange phenomenon to no avail. They all keep telling to to replace my thermostat. I replaced it a couple times already and that is not the remedy. So I remedy this situation by always keeping my house at a desired temperature (68 degrees) when I know the outside temperatures are going to drop below 10 degrees. Once the house temperature drops two degrees below what I'm asking for on the thermostat, I'm bumming. I have to keep re-setting the breaker every 25 minutes, until the house temperature catches up with what I'm setting the thermostat at. Did I Confuse you????? |
|
#5
|
|||
|
|||
|
David,
sounds very familiar, but at least mine will run correctly after I reset it in the morning. I have done some more research, the closest I could find is that it might be the flame sensor. So I took it out and cleaned it with 220 grit sandpaper, it is going fine right now, we will see what happens tonight. It has kicked in three times correctly since I cleaned the flame sensor. I'll let you know if it is working in the morning, if so you might give it a try, it wasn't hard (on my Lennox) Thanks Randy |
|
#6
|
||||
|
||||
|
Question when was the last time you had your furnace serviced .
We always tell our client to get the furnace serviced and then we try and do our own. Roy Cooke A happy NACHI Member Need help on inspection call my cell 613-827-2011 I like email Roycooke@hotmail.com Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun. |
|
#7
|
||||
|
||||
|
Quote:
If you are going to check for 24 volts at the stat you have to check between R or W and the common side of the transformer as R & W are the same leg of power at the stat. </IMG> Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#8
|
||||
|
||||
|
Quote:
But it sounds like you have been talking to the wrong HAVC Tech,s This does not sound to me as if you are having a stat problem. A 9 year old furnace should have a solid state board controlling the unit. It sounds to me by you having to kill the main power to the unit thus resetting the board that you are having a safety locking out the unit and you should probally be looking at your board not the stat. I use to tell folks that you can not trouble shoot over a phone line and that is still true today???? Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#9
|
||||
|
||||
|
Quote:
|
|
#10
|
||||
|
||||
|
Quote:
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#11
|
||||
|
||||
|
Quote:
Thank you Charlie. |
|
#12
|
|||
|
|||
|
Please Note:
Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
It might just be getting old. Old furnaces take longer to light, especially when they are colder. Are you sure it's not trying to light when you say it is not kicking on? My 15 year old furnace takes 15 minutes to start blowing and about 50 sparks from the automatic igniter (there is no pilot light).
|
|
#13
|
||||
|
||||
|
Quote:
It's only 9 years old and I'm having cycle problems as I have explained above. It's working absolutely fine now as the weather is above 10 degrees now. |
|
#14
|
||||
|
||||
|
David, On the newer mid-efficient models the codes for the LEDs trouble shooting guide is usually printed on a label in the lower panel of the unit. They normally have a green or red LED, some have both. eg.
green steady on=normal operating green slow flashing=initiating stage red rapid flashing=flame rollout safety switch red one fast, two slow flashes=flame sensor NOTE: these are just examples not actual facts....each furnace is different, so check the data sheet. A furnace guy who happens to be a friend says a lot of his calls have to do with a simple cleaning of the flame sensor which looks like a nail/pin that is located in the middle of one of the burners where the flame shoots out, and when it gets a coating on it, will not allow the furnace to operate. Simply buff or sand with some emery cloth or real fine sandpaper...presto. Most of the time it doesn't even look dirty or build-up present. It doesn't cost anything to try and can save a 75.00 service call. Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right! (website) http://inspectorpages.com/dhadler
|
|
#15
|
||||
|
||||
|
David, if you can give me the following, I'll try and get an answer about your furnace dilemma. High or Mid efficiency, make, model, serial #, brand and #of gas valve, and if possible the color and rate of light flashes when the unit has tripped or quit.
My buddy is a real whiz with these things and has come across just about everything in his many, many years in the business. I told him of your situation and he has a couple of possibilities that have come up and have nothing to do with thermostats etc. More along the lines of the venting/combustion air and pressure/diaphragm switches. Very tough items to pin point, if you haven't ran across them before. Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right! (website) http://inspectorpages.com/dhadler
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Furnace Problem Comments Welcome | rfrost | Inspecting HVAC Systems | 28 | 10/21/07 6:26 PM |
| Sweating decision:Settle for lower SEER to use existing furnace? | Fel Randolph | Inspecting HVAC Systems | 2 | 6/6/07 2:56 PM |
| Armstrong Ultra 80 Oil Forced air furnace | Stephen Frazer | Inspecting HVAC Systems | 19 | 4/9/07 8:00 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |
| Furnace Question | ccrooker | Canadian Inspectors | 13 | 10/27/06 7:21 AM |