Question Furnace Location?

Found an electric forced air furnace installed in a garage today to heat the house. Does not seem right to me. My concern is the furnace pulling in carbon monoxide, from the car, through any openings in access panels or joints in ducts and blowing it into the house. Would appreciate some feedback on this.
Reply With Quote
  #2  
Old 4/24/07, 12:52 AM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Location?

Quote:
Originally Posted by dsmith1
Found an electric forced air furnace installed in a garage today to heat the house. Does not seem right to me. My concern is the furnace pulling in carbon monoxide, from the car, through any openings in access panels or joints in ducts and blowing it into the house. Would appreciate some feedback on this.
Not a problem.
Reply With Quote
  #3  
Old 4/24/07, 1:04 AM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Location?

Quote:
Originally Posted by dsmith1
Found an electric forced air furnace installed in a garage today to heat the house. Does not seem right to me. My concern is the furnace pulling in carbon monoxide, from the car, through any openings in access panels or joints in ducts and blowing it into the house. Would appreciate some feedback on this.
I would add that the ductwork has to be sealed. Also, protection from impact wouldn't be a bad idea.
Reply With Quote
  #4  
Old 4/24/07, 1:21 AM
Jason1's Avatar
Jason1 Jason1 is offline
Active Poster
 
Join Date: Nov 2006
Posts: 677
Please Note: Jason1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Location?

I would also add that although it isn't a problem building code wise (check your local codes) I wouldn't do it in my house
Reply With Quote
  #5  
Old 4/24/07, 10:33 AM
cbottger's Avatar
cbottger cbottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 2,738
Default Re: Furnace Location?

Quote:
Originally Posted by dsmith1
Found an electric forced air furnace installed in a garage today to heat the house. Does not seem right to me. My concern is the furnace pulling in carbon monoxide, from the car, through any openings in access panels or joints in ducts and blowing it into the house. Would appreciate some feedback on this.
Furnaces of all types are installed in garages all the time the returns are a sealed system back to the living areas. Return air can not be taken from a garage. When I inspect these types of installs I just ensure that the return air is properly sealed on the garage side. Probally 50 million units installed in this manner??????



Freedom Express Inspections LLC
CMOR Thermography Certified Level 11 #2097
freedomexpressinspections.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
Professional Home Inspector State License # 130
Reporting system by Home Inspector Pro

Serving the State of Okla.
Reply With Quote
  #6  
Old 4/24/07, 12:37 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: Furnace Location?

Insure that the duct does not break the fire wall barrier between the house and the garage. Flexible duct cannot be used in this application. Sheet metal duct of the appropriate thickness (set by code ) is required.
Reply With Quote
  #7  
Old 4/30/07, 7:31 PM
gbrasseur's Avatar
gbrasseur gbrasseur is offline
Active Poster
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 419
Please Note: gbrasseur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Location?

Quote:
Originally Posted by dandersen
Insure that the duct does not break the fire wall barrier between the house and the garage. Flexible duct cannot be used in this application. Sheet metal duct of the appropriate thickness (set by code ) is required.
Good point David.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Problem Comments Welcome rfrost HVAC 24 10/21/07 7:26 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph HVAC 2 6/6/07 3:56 PM
Correct connect at Furnace tmartens Plumbing 2 5/1/07 10:33 PM
Armstrong Ultra 80 Oil Forced air furnace Stephen Frazer HVAC 19 4/9/07 9:00 PM
Condemned Furnaces Spark Safety Issues Gary Reecher HVAC 7 3/8/07 9:17 PM


All times are GMT -4. The time now is 7:29 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts