Default Furnace power

I know you will answer "it depends" but I am looking for an order of magnitude. How much electric power does a gas furnace need to light (I have a spark thing) and operate the blower? I am thinking of buying some power back-up to run the heating in time of emergency and was thinking of how much oomph I would need.

Are we talking hundreds or thousands of watts?

And what happens to a gas furnace that is burning when the power is cut? When the blower goes off, does the furnace?
Reply With Quote
  #2  
Old 2/20/07, 12:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Furnace power

Approximately 746 watts for each Horse Power of the blower motor.

3/4 HP would be 560 watts
But start up current of the motor is higher.
Reply With Quote
  #3  
Old 2/20/07, 12:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Furnace power

Quote:
Originally Posted by Ian Gills

And what happens to a gas furnace that is burning when the power is cut? When the blower goes off, does the furnace?
Your furnace gas valve is operated with 24 volts supplied from a 120 transformer and if you loose power or 120 volts to the furnace the gas valve shuts down because it is a normally closed valve that requires 24 volts to open. The flame and the blower will shut down at the same time leaving your heat exchanger hot because it requires the blower to cool it back to 100 degrees once the flame goes off. I would state that if this happens on a one time biases there would be no damage to the heat exchanger.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 2/21/07, 7:20 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Furnace power

Ian,

I assume you are working with an Electrical Contractor to help size and install this aux. generator? I am also thinking you will be operating more than just the Furnace in an emergency situation, with this aux. system?
I would guess that a newer furnace will probably require no more than 6-10amps to start/operate.
I agree with Charley, damage can be done to gas furnaces that are short cycled off during a power outage, especially on a frequent basis. It can also be a fire hazard if there are any defects in the furnace, that might be unknown.
Good Luck finding the right Electrical Contractor
Reply With Quote
  #5  
Old 2/21/07, 10:34 AM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace power

Too much power, and too complicated. I'll give up and use blankets instead. It was just an idea.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Sweating decision:Settle for lower SEER to use existing furnace? Fel Randolph Inspecting HVAC Systems 2 6/6/07 2:56 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
question on wireing furnace, legal or not Bill Hathaway Electrical Inspections 26 1/19/07 10:36 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM


All times are GMT -4. The time now is 11:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts