I just received email from customer with a complaint about her furnace. Natural gas low efficiency York installed in 1992. I include pictures taken at time of inspection. Customer is stating that water leak from faulty A frame for A/C unit has caused her heat exchanger to rust out and now her furnace has to be replaced. Her email stated that there is visible rust and water marks in furnace and water pooling on floor of basement around heater.

The pictures I have show a few small moisture stains, no visible rust, and from three sides of furnace in pictures, no visible pooling of water. Her drain line from A frame does go to drain in front of furnace. This I usually find is usually located on top or close to drain.

I am wondering what your recommendations are in this type of situation, I dont want to shirk any responsibilities but also not interested in buying her a new furnace. Her estimate is $6,000.00. My report states that furnace average life span is 14 to 17 years and no perdicted service life could be given. Also noted that orange and yellow flame indicated poor combustion and needed "tune up". The humidifier was not working at time of inspection and was noted. Usually cheaper drum humidifiers do not work long after installation especially with hard water in this area. I would assumed that the minor spots on bottom shelf would have been from faulty humidifier.

I would be interested in your comments as I intend to do something for this customer but would like to be fair to myself and her.



Thanks
Attached Thumbnails
furnace-problem-comments-welcome-i28.jpg   furnace-problem-comments-welcome-i33.jpg   furnace-problem-comments-welcome-i34.jpg   furnace-problem-comments-welcome-i36.jpg  



Roger Frost CBCO
Barrie Home Inspector
Alliston Home Inspections
Orillia House Inspector
Barrie, ON
(705)795-8255
Reply With Quote
  #2  
Old 10/11/07, 3:50 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: Furnace Problem Comments Welcome

Quote:
Originally Posted by rfrost
I just received email from customer with a complaint about her furnace. Natural gas low efficiency York installed in 1992. I include pictures taken at time of inspection. Customer is stating that water leak from faulty A frame for A/C unit has caused her heat exchanger to rust out and now her furnace has to be replaced. Her email stated that there is visible rust and water marks in furnace and water pooling on floor of basement around heater.

The pictures I have show a few small moisture stains, no visible rust, and from three sides of furnace in pictures, no visible pooling of water. Her drain line from A frame does go to drain in front of furnace. This I usually find is usually located on top or close to drain.

I am wondering what your recommendations are in this type of situation, I dont want to shirk any responsibilities but also not interested in buying her a new furnace. Her estimate is $6,000.00. My report states that furnace average life span is 14 to 17 years and no perdicted service life could be given. Also noted that orange and yellow flame indicated poor combustion and needed "tune up". The humidifier was not working at time of inspection and was noted. Usually cheaper drum humidifiers do not work long after installation especially with hard water in this area. I would assumed that the minor spots on bottom shelf would have been from faulty humidifier.

I would be interested in your comments as I intend to do something for this customer but would like to be fair to myself and her.
Thanks
When was the inspection ,Did she get it serviced .
I always recommend immediate removal of Humidifier as they are not an advantage in our part of Canada.
They also are the cause of many furnaces rusting out .
It is 15 years old and could have reached it normal life expectancy with out the humidifier adding to the difficulties.
I would be back to see her immediately make no comments just listen and ask questions .
Then go to your friendly furnace man and talk it over with him asking what experience he has had with these furnaces in you area .
Even if you are wrong No way can you be expected to upgrade a 15 year old furnace . 20% of and upgrade cost at most ( but do not say or admit to any thing .
Best of luck please keep us posted .
... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 10/11/07, 10:09 PM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Furnace Problem Comments Welcome

Roger,

First, the pictures show a pretty clean furnace for a 1992 model. The other pictures are kinda small, can't get much detail on floor stains, flame color, Humidifier condition, etc. Looks well maintained though.

What I don't understand is why she is coming back to you for help in the cost of repair/replacement of a 15 yr.+ furnace. I guess I'm interested in the wording of your comments about the HVAC system as a whole in your report I've never had this problem before, and would like to avoid the situation.

I have always been very clear about my reporting of existing conditions. I make sure the Client understands that just because I'm performing a Home Inspection, I'm not a specialist, I'm not Superman, I look for markers, indicators of potential problems, and make recommendations.
I warrant nothing, and they understand, because I'm typically including reaffirming comments in each catagory of my report. I'll reference life expectancies, probabilities, etc. as confirmation to a condition found, but it's actuarial data only.

I wish you luck.
If your wording is clear, don't be bullied or buffaloed into spending anything more than you're comfortable with. If it were me, I probably would'nt contribute a dime. Clients who try stuff like this get me all bowed up, makes me wants to dig my heels in and fight.

Get'um killer...
Reply With Quote
  #4  
Old 10/11/07, 11:39 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: Furnace Problem Comments Welcome

I want to know what indications of a problem you missed during the inspection.
If it ran ok and it was that clean did the ex owner clean it to cover up this supposedly rusted exchanger.If you inspected the humidifier you did more than I would as they are often excluded.
Reply With Quote
  #5  
Old 10/12/07, 8:22 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Furnace Problem Comments Welcome

First off $6k is too much (even in Canadian)!

There is no reason to replace a furnace in this good of shape for a broken heat exchanger (even if it was broken). The/or part of the heat exchanger can be repaired.

Second, the furnace is spotless (compared to most of this age)!

Third, with no obvious exterior visible signs of problems, heat exchanger and A/C coil evaluation requires TOTAL dismantling of the equipment (not just taking of a cover). Outside of scope.

Forth, you called out enough issues that should have brought in an HVAC guy to evaluate. Did they follow up?

When was the inspection? Did you have sufficient weather to run the a/c for an hour or so during the inspection? You can not find leaks when you can't make water.

How did she find out about these issues? I would assume after a "thorough inspection" by an HVAC guy and the unit is long gone! Did she notify you in a timely manner to come look things over? Or is this just the HVAC guy shooting off his mouth against your word.

It looks like you documented things quite well and from here I see no reason to suspect problems. As they say, you can't inspect from a picture. However, the scope of HVAC Inspection is limited to just about that extent, a visual look!

Condensate leaks are inevitable, not possible.
Where are the HVAC guys pictures?
Reply With Quote
  #6  
Old 10/12/07, 8:47 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Furnace Problem Comments Welcome

Damn, I hate it when a client attempts to get a free furnace out of the home inspector. She has to go somewhere to save money. Her attorney probably advised her to go after everyone involved and you are simply on the list.

I don't run into these type of situations due to several reasons....

1) I always annotate all visible defects on the inspection report and "I recommend they have a qualified technician to service and clean existing furnace/boiler before close of escrow". That leaves me out of the picture when an immediate problem does arise, when they finally take possesion of their home.

2) I recommend removal of all humidifiers older than 5 years old. I've seen many humidifiers cause major problems inside the return ducts, blower area, heat exchanger area and duct work.

3) I include the following in all my reports...

Your report does not include all maintenance items and should not be relied upon for such items. Any recommendations that Massachusetts Home Inspections makes for service, a second opinion, or permit research involving any component or condition should be completed and documented before the close of escrow, or Massachusetts Home Inspections will be held harmless for any subsequently alleged defects.

I report all conditions as they existed at the time of the inspection. The information contained in your report may be unreliable beyond the date of the inspection due to changing conditions. Your inspection was essentially visual, is not technically exhaustive, and does not imply that every defect was found. Latent and concealed defects and deficiencies are excluded from the inspection. Cosmetic flaws and defects will not be a part of your Home Inspection.

4) Recommend a final walk through. I believe the purpose of a final walk-through is not only to make sure that any requested items have been repaired correctly, but also to make sure that additional damage, deterioration, and destruction beyond normal wear and tear has not occurred.

I recommend a careful, slow, and thorough observation with your Realtor at your final walk-through to ensure your satisfaction.

Last edited by dvalley; 10/12/07 at 8:51 AM..
Reply With Quote
  #7  
Old 10/12/07, 9:05 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Furnace Problem Comments Welcome

This is what a potential problem looks like, not yours.

I'm certified to pull this thing apart.
I did not.
If the client doesnt do something about it, it's not my problem.

I posted a thread somewhere about this issue when my client came back on me.
I sent him the Inspection Agreement, pictures and report as a reminder, along with a nasty letter. I have not heard a peep out of him.

The unit was low on refrigerant and looked like the picture below.
He was depending on a "useless" home warrenty and lost.
Then he thought about depending on me! NOT!
He had his chance to get it fixed for free before he closed escrow.

Last edited by dandersen; 12/9/09 at 12:24 PM..
Reply With Quote
  #8  
Old 10/12/07, 12:05 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Problem Comments Welcome

She is trying to upgrade to a hi-eff furnace at your expense. As David said $6K is too much for a mid.

I also think it is rather clean for it age.

If you need, I have a used perfectly working mid sitting in my basement that you can have for a small token sum if you really need it to satisfy her.
Reply With Quote
  #9  
Old 10/12/07, 10:47 PM
wsutton's Avatar
wsutton wsutton is offline
InterNACHI Member
 
Join Date: Mar 2007
Location: Nashville, Tn
Posts: 33
Default Re: Furnace Problem Comments Welcome

Roger,
I see no reason why you should do anything for this customer, I come to this conclusion from what I see in the pics and what you said in this posting.
Good Luck, if you spend any money here it should be for legal counsel, not for a new furnace.
Reply With Quote
  #10  
Old 10/14/07, 10:50 AM
Roger A. Frost's Avatar
Roger A. Frost Roger A. Frost is offline
InterNACHI Member
 
Join Date: May 2005
Location: Barrie, On
Posts: 74
Default Problem Resolved...Furnace Replacement

Thanks to everyone for their comments, they helped considerably. I went over to clients home yesteday and only had 15 min before had to leave for another inspection and found furnace was taken apart waiting for HVAC guys who were late.

Took tons of pictures and was suruprised to see that area on furnace which I had taken pictures of now had large area of rust on it. As this was almost 4 months since inspection this was good sign for my case. Also on my pre-inspection agreement I added 3 items for myself to initial and my customer. One is for mould, one for moisture and one blank which in this case i filled in furnace. This stated that customer had been informed about potenital problems with furnace. He had initialed and signed agreement.

Also for some reason they had turned water on to drum humidifier which was turned off and not working at time of inspection. I asked him about it and he said it was still not working. I noted and took pics of fact that tray was full on water. This alone could have been cause of rust and leaking etc.

When I left they questioned me on what I was going to do. I told them that I was meeting my lawyer on Wednesday and that I was confident that I had no liability due to fact that I now had two pictures, one of fairly clean furnace and now one with large amount of rust in same area. Also the fact that I had informed them that there was no perdicatable service life left in furnace was all that could be expected from me, I was not a furnace technician.

Recieved email from them this morning asking if I would give them a refund on inspection fee even though time period was over. I replied to them that in the spirit of good customer relations I would send them $500.00 which ends this particular experience.

Thanks again for your support and comments



Roger Frost CBCO
Barrie Home Inspector
Alliston Home Inspections
Orillia House Inspector
Barrie, ON
(705)795-8255
Reply With Quote
  #11  
Old 10/14/07, 11:02 AM
Greg Veal Greg Veal is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Woodstock, GA
Posts: 511
Default Re: Furnace Problem Comments Welcome

Roger,

Some good advice from others.

Just one comment...
"I/me" would never consider being involved with a repair that includes the replacement of the "Heat Exchanger" in any existing furnace, no matter what the physical condition appears to be.
I know, there will be lots of folks that will argue my position, but I followed a case back in the early 80's, that convinced me that the exposure to liability, on all levels, is just to great.
As a H/I, I will never recommend that as an option.

Just another observation I felt I would share, for what it's worth.
Reply With Quote
  #12  
Old 10/14/07, 4:19 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,776
Default Re: Problem Resolved...Furnace Replacement

Quote:
Originally Posted by rfrost
Recieved email from them this morning asking if I would give them a refund on inspection fee even though time period was over. I replied to them that in the spirit of good customer relations I would send them $500.00 which ends this particular experience.

Thanks again for your support and comments
You are very generous, not me!



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #13  
Old 10/14/07, 4:23 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Furnace Problem Comments Welcome

They wouldn't be getting a dime (refund) out of me.

My report specifically states...

I highly recommend that you request your HVAC technician to inspect the Heat Exchanger for cracks, holes or leaks as my inspection is mechanically limited since the furnace requires dismantling to examine this particular area. A deteriorated heat exchanger will allow deadly products of combustion into your living area.
Reply With Quote
  #14  
Old 10/14/07, 9:50 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Furnace Problem Comments Welcome

Rodger,
Who took the unit apart?



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #15  
Old 10/14/07, 9:52 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Furnace Problem Comments Welcome

Marcel

Very generous, considering the max fee is $259.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
To hot too test the furnace rcooke Canadian Inspectors 1 8/19/07 10:44 PM
For those in favor of licensing gbeaumont Legislation, Licensing & Legal Issues for Inspectors 70 5/21/07 3:09 PM
Tidbits from the ASHI Message Board jbushart Miscellaneous Discussion for Inspectors 126 4/27/07 11:05 AM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
Very tough problem Albert Detorre Inspecting HVAC Systems 7 2/23/07 12:01 PM


All times are GMT -4. The time now is 7:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts