Old 6/18/07, 5:58 PM
Vincent Wood Vincent Wood is offline
Default furnace return air duct
hi. i found a furnace in a ranch home full basement. The only return air
duct was running 3 ft off of the furnace with a filter sitting on top of
the open duct work. this is a up flow forced air furnace. there were no
return air ducts any were else. I said that a heating and cooling co.
should advise if this is proper. any comment?
Old 6/18/07, 7:02 PM
Jeffrey R. Pope's Avatar
Default Re: furnace return air duct
Return-air cannot be taken from the same room as a gas-fired furnace. This is a serious safety hazard that needs to be corrected.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 6/18/07, 7:12 PM
Thanks I knew that return air was not sapose to be drawn from a basement
are. also that system must have very poor circulation. also a pressure
issue on the main level.
Old 6/18/07, 7:15 PM
Henry Valenzano, CMI's Avatar
Henry Valenzano, CMI Henry Valenzano, CMI is offline
Send a message via MSN to hvalenzano
Colorado requires the return air to be at least 10 ft away from the unite in a open basement. If the furnace is in its own room you can not have a return in it.
Henry Valenzano CMI (Hank)
Double Check Home Inspection LLC.
www.DCHI.com Hank@DCHI.com 719-635-6425
Colorado Arms Repair : Gunsmith
www.ArmsRepair.com Henry@ArmsRepair.com
Old 6/19/07, 11:27 AM
David A. Andersen's Avatar
Isn't that 10 feet from or from a room with insufficent volume for combustion air?
Old 6/19/07, 1:18 PM
There should never be insufficient combustion air. That would be a completely different problem. Return should never be within 10 ft of the unite if it is in a Open basement. and should never be in a enclosed furnace room even if it has enough combustion air. Furnaces with a sealed combustion chamber has another set of rules. General rule of thumb if it looks out of the ordinary or just not refer it to a licensed professional.
Critter in the return air duct... swaskewicz Inspecting HVAC Systems 11 11/28/07 3:49 PM
Reduced return air duct mmorgan Inspecting HVAC Systems 4 6/6/07 7:39 PM
Gas line in return duct jhugenroth Inspecting HVAC Systems 0 8/10/06 9:01 AM
return air duct? dbucknavich Inspecting HVAC Systems 2 5/17/06 10:53 PM