Default Garage Furnaces

Yes, I did take the IRC 2003 codes classes and yes I do have the code book.

When putting a furnace in a garage it must be 18" above the floor. The material used to build this can be wood, right ????????
My question does there need to be something that has a fire rating to be between the furnace and the platform? Like drywall, sheet metal, etc. not plywood. My answer would have been yes, but I can't find that in the codes book, section 24.

If someone could help me out with this, please give me the section in the code book.

Thanks
Tom P'ski
Reply With Quote
  #2  
Old 4/17/08, 5:18 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: Garage Furnaces

M1402.2 Clearances. Clearances shall be provided in accordance with the listing and the manufacturer's installation instructions.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #3  
Old 4/17/08, 6:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Garage Furnaces

With most furnaces, there is no heat produced at the platform/plenum. This is generally where the blower assembly is.

The fire rating of the plenum must conform to that of the required rating of the garage separation. Also, any ducts in the garage must be 20ga sheet metal (or equipped with fire dampers - CBC)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #4  
Old 4/17/08, 6:48 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Garage Furnaces

The furnace does not have to be 18 inches off of the floor the ruling is 18 inches to point of ignition which is the burners and the burners will measure 18 inches from the floor



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Installing GFCI in garage with no ground cyezza Electrical Inspections 53 11/30/07 5:05 PM
Evaporative cooler in garage chellickson Inspecting HVAC Systems 9 7/23/07 12:08 AM
Garage ceiling & door header Al Barb Interior Inspections 7 3/27/07 12:07 PM
Garage Door Safety...No Reverse...Advice Please gliebig Exterior Inspections 33 3/17/07 7:28 PM
Garage fire rated wall jlybolt Interior Inspections 3 6/18/06 6:21 PM


All times are GMT -4. The time now is 11:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts