Yes, I did take the IRC 2003 codes classes and yes I do have the code book.
When putting a furnace in a garage it must be 18" above the floor. The material used to build this can be wood, right ???????? My question does there need to be something that has a fire rating to be between the furnace and the platform? Like drywall, sheet metal, etc. not plywood. My answer would have been yes, but I can't find that in the codes book, section 24. If someone could help me out with this, please give me the section in the code book. Thanks Tom P'ski |
|
#2
|
||||
|
||||
|
M1402.2 Clearances. Clearances shall be provided in accordance with the listing and the manufacturer's installation instructions.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#3
|
||||
|
||||
|
With most furnaces, there is no heat produced at the platform/plenum. This is generally where the blower assembly is.
The fire rating of the plenum must conform to that of the required rating of the garage separation. Also, any ducts in the garage must be 20ga sheet metal (or equipped with fire dampers - CBC) IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
The furnace does not have to be 18 inches off of the floor the ruling is 18 inches to point of ignition which is the burners and the burners will measure 18 inches from the floor
Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Installing GFCI in garage with no ground | cyezza | Electrical Inspections | 53 | 11/30/07 5:05 PM |
| Evaporative cooler in garage | chellickson | Inspecting HVAC Systems | 9 | 7/23/07 12:08 AM |
| Garage ceiling & door header | Al Barb | Interior Inspections | 7 | 3/27/07 12:07 PM |
| Garage Door Safety...No Reverse...Advice Please | gliebig | Exterior Inspections | 33 | 3/17/07 7:28 PM |
| Garage fire rated wall | jlybolt | Interior Inspections | 3 | 6/18/06 6:21 PM |