InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > HVAC

Notices

HVAC Topics include heating, venting, and air conditioning.

Reply
 
LinkBack Thread Tools
  #1  
Old 12/21/07, 4:55 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,337
Default Gas appliance connector

I know that gas appliance connectors cannot exceed 3' in length but can two 1' sections properly connected together be used? I saw this written up as a defect in a report but I can't find a prohibition against it.
Reply With Quote
  #2  
Old 12/21/07, 4:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,411
Default Re: Gas appliance connector

Absolutely not. Appliance connectors can only be connected to appliances, not to additional appliance connectors.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 12/21/07, 5:36 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,337
Default Re: Gas appliance connector

Thanks Jeff, does it say that on the mfgr installation instructions, fuel gas code, UPC, ?
Reply With Quote
  #4  
Old 12/21/07, 6:10 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,531
Default Re: Gas appliance connector

http://www.dormont.com/dmc/uploadedF...structions.pdf

Quote:

5. The connector should be of adequate length to reach from the gas supply line to the
appliance without stretching.
NEVER join two or more connectors to make a longer
connector.




"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #5  
Old 12/21/07, 6:17 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,337
Default Re: Gas appliance connector

Perfect Brian...that works! Thanks.
Reply With Quote
  #6  
Old 12/23/07, 2:20 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,908
Default Re: Gas appliance connector

Michael or Anybody else that have gas connector questions -

Everytime I used to write up connectors spliced, inside walls, going through floors, appliance cabinets, etc I used to have agents and sellers telling me I was dumber than snot cause "Old Charlie" the plumber, HVAC contractor, appliance guru, etc told them thats the way they always do it.

I kept trying to look it up in code books, etc. Then one day my niece asked me to help her connect her new gas range. She had bought one and had the store load it in her pick-up truck to bring home. She had bought an flexible gas connector from the dealer. It came in a clear plastic bag.

Guess what - there are about 10 GRAPHICS on the outside of the bag showing how they CAN'T be installed.

My point - make it simple. Spend $6.50 and buy one. Now if I get that comment, I just get the bag out of the truck and let the seller or agent read it. Then I graciously apologise to them for their having to be exposed to some "Old Charlie" that doesn't know squat about what he's doing.

If I'm in a really good mood, I'll follow that up with a comment like:

"I hope Old Charlie knows more about something else than he does about ......., cause he sure doesn't seem to know much about this." But fortunately for you, you've now met ME - the real expert in issues around the house". "In the future call me if you have more questions regarding your house or its components".
Reply With Quote
  #7  
Old 12/23/07, 2:54 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,483
Default Re: Gas appliance connector


Read warnings carefully before installing
To avoid personal injury (including death) or property damage, read and understand this entire
instruction sheet before installing your gas connector. Follow all instructions and safety precautions
during installation, use and maintenance. If you do not understand any of these instructions or
precautions, call a licensed plumber. Any damage to the connector or product failures that occur as
a result of improper installation or neglect to follow these instructions will void this limited
warranty.
1. To prevent corrosion, DO NOT allow strong cleaning solutions or chemicals
to come in contact with the connector. These include acids, solvents, solder fluxes with zinc
chlorides, ammonia, chlorinated chemicals, and any liquid with chlorine such as laundry
bleach or dish detergent.

2. An accessible manual gas shut-off valve must be installed on the gas supply ahead of the
connector. DO NOT proceed with this installation if a shut-off valve is not installed –
call a licensed plumber for assistance.



3. DO NOT assemble the connector nut directly to male pipe threads.
4. DO NOT install the gas connector so that it is concealed within or runs through any wall,
floor or other partition. The gas outlet must be in the same room as the appliance. This is so
it is visible for periodic inspection.
5. The connector should be of adequate length to reach from the gas supply line to the
appliance without stretching. NEVER join two or more connectors to make a longer
connector.
6. NEVER reuse a gas connector. If a new appliance is purchased or an existing appliance is
moved, a new connector must be used.
7. Only the fittings supplied with this connector or those manufactured and recommended by
Dormont Manufacturing Company should be used.
8. Connectors are designed for occasional movement after installation. Not for use on castered
equipment. Repeated bending, flexing or extreme vibration will cause metal fatigue and
must be avoided.
9. This flexible gas connector is to be used on natural or LP/propane gas supply systems
having internal pressures no higher than ½ lb. per square inch. .
10. DO NOT kink, twist or bend the connector smaller than 1½" internal diameter
(approximately the diameter of a golf ball). Avoid sharp bends - no right angles.
Warning



11. To avoid corrosion, DO NOT allow connector to come in contact with foreign objects such
as wall studs, electrical wiring, copper or iron pipe, paneling, sheet metal, etc.
12. DO NOT use the gas connector or gas supply line for the appliance ground.
13. This product meets national building codes and the ANSI standard for gas connectors (ANSI
Z21.24). However, local codes and regulations prevail. Contact your local municipality to
verify applicable codes.
14. Additional requirements for the Commonwealth of Massachusetts
a. Installations must be performed by a qualified or licensed contractor, plumber or
gasfitter qualified by the state, province or region where this appliance is being
installed.
b. Only use gas shutoff valves approved for use within the state, province or region
where this appliance is being installed.







c. A flexible gas connector, when used, must not exceed 3 feet.



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good

Last edited by badair; 12/23/07 at 2:57 PM..
Reply With Quote
  #8  
Old 12/25/07, 2:10 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 1,908
Default Re: Gas appliance connector

By the way, gas connectors are not be longer than 3' EXCEPT that the range and dryer gas connectors can be 6' for moving and service.
Reply With Quote
  #9  
Old 12/25/07, 3:01 PM
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,558
Default Re: Gas appliance connector

Quote:
Originally Posted by dbowers
By the way, gas connectors are not be longer than 3' EXCEPT that the range and dryer gas connectors can be 6' for moving and service.
How about outside for Gas BBQs . I think they can be longer ( Mine is ) .

...Cookie



Roy Cooke.RHI.
http://royshomeinspection.com/
Questions 613-475-1144
Roycooke@sympatico.ca

" A life spent making mistakes is not only more honorable but more useful
than a life spent doing nothing." George Bernard Shaw
Reply With Quote
  #10  
Old 12/25/07, 3:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,411
Default Re: Gas appliance connector

Barbeques are an exception as well. The CPC (UPC) allows up to 15 feet for outdoor appliances.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 12/25/07, 4:49 PM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,107
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas appliance connector

Quote:
Originally Posted by badair


Read warnings carefully before installing
To avoid personal injury (including death) or property damage, read and understand this entire
instruction sheet before installing your gas connector. Follow all instructions and safety precautions
during installation, use and maintenance. If you do not understand any of these instructions or
precautions, call a licensed plumber. Any damage to the connector or product failures that occur as
a result of improper installation or neglect to follow these instructions will void this limited
warranty.
1. To prevent corrosion, DO NOT allow strong cleaning solutions or chemicals
to come in contact with the connector. These include acids, solvents, solder fluxes with zinc
chlorides, ammonia, chlorinated chemicals, and any liquid with chlorine such as laundry
bleach or dish detergent.

2. An accessible manual gas shut-off valve must be installed on the gas supply ahead of the
connector. DO NOT proceed with this installation if a shut-off valve is not installed –
call a licensed plumber for assistance.



3. DO NOT assemble the connector nut directly to male pipe threads.
4. DO NOT install the gas connector so that it is concealed within or runs through any wall,
floor or other partition. The gas outlet must be in the same room as the appliance. This is so
it is visible for periodic inspection.
5. The connector should be of adequate length to reach from the gas supply line to the
appliance without stretching. NEVER join two or more connectors to make a longer
connector.
6. NEVER reuse a gas connector. If a new appliance is purchased or an existing appliance is
moved, a new connector must be used.
7. Only the fittings supplied with this connector or those manufactured and recommended by
Dormont Manufacturing Company should be used.
8. Connectors are designed for occasional movement after installation. Not for use on castered
equipment. Repeated bending, flexing or extreme vibration will cause metal fatigue and
must be avoided.
9. This flexible gas connector is to be used on natural or LP/propane gas supply systems
having internal pressures no higher than ½ lb. per square inch. .
10. DO NOT kink, twist or bend the connector smaller than 1½" internal diameter
(approximately the diameter of a golf ball). Avoid sharp bends - no right angles.
Warning



11. To avoid corrosion, DO NOT allow connector to come in contact with foreign objects such

as wall studs, electrical wiring, copper or iron pipe, paneling, sheet metal, etc.
12. DO NOT use the gas connector or gas supply line for the appliance ground.
13. This product meets national building codes and the ANSI standard for gas connectors (ANSI
Z21.24). However, local codes and regulations prevail. Contact your local municipality to
verify applicable codes.
14. Additional requirements for the Commonwealth of Massachusetts
a. Installations must be performed by a qualified or licensed contractor, plumber or
gasfitter qualified by the state, province or region where this appliance is being
installed.
b. Only use gas shutoff valves approved for use within the state, province or region
where this appliance is being installed.

c. A flexible gas connector, when used, must not exceed 3 feet.
Haven't seen the name Dormont in a long time. They're are also the connector of choice in the commercial world (kitchen appliances). 3/4'' - 1'' with quick disconnects for employee mishaps. Memories of my commercial inspection days. And no I did not inspect the electrical.
Reply With Quote
  #12  
Old 12/26/07, 1:49 AM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 12,531
Default Re: Gas appliance connector

Quote:
Originally Posted by badair




Read warnings carefully before installing
To avoid personal injury (including death) or property damage, read and understand this entire
instruction sheet before installing your gas connector. Follow all instructions and safety precautions
during installation, use and maintenance. If you do not understand any of these instructions or
precautions, call a licensed plumber. Any damage to the connector or product failures that occur as
a result of improper installation or neglect to follow these instructions will void this limited
warranty.
1. To prevent corrosion, DO NOT allow strong cleaning solutions or chemicals
to come in contact with the connector. These include acids, solvents, solder fluxes with zinc
chlorides, ammonia, chlorinated chemicals, and any liquid with chlorine such as laundry
bleach or dish detergent.

2. An accessible manual gas shut-off valve must be installed on the gas supply ahead of the
connector. DO NOT proceed with this installation if a shut-off valve is not installed –
call a licensed plumber for assistance.



3. DO NOT assemble the connector nut directly to male pipe threads.
4. DO NOT install the gas connector so that it is concealed within or runs through any wall,
floor or other partition. The gas outlet must be in the same room as the appliance. This is so
it is visible for periodic inspection.
5. The connector should be of adequate length to reach from the gas supply line to the
appliance without stretching. NEVER join two or more connectors to make a longer
connector.
6. NEVER reuse a gas connector. If a new appliance is purchased or an existing appliance is
moved, a new connector must be used.
7. Only the fittings supplied with this connector or those manufactured and recommended by
Dormont Manufacturing Company should be used.
8. Connectors are designed for occasional movement after installation. Not for use on castered
equipment. Repeated bending, flexing or extreme vibration will cause metal fatigue and
must be avoided.
9. This flexible gas connector is to be used on natural or LP/propane gas supply systems
having internal pressures no higher than ½ lb. per square inch. .
10. DO NOT kink, twist or bend the connector smaller than 1½" internal diameter
(approximately the diameter of a golf ball). Avoid sharp bends - no right angles.
Warning



11. To avoid corrosion, DO NOT allow connector to come in contact with foreign objects such

as wall studs, electrical wiring, copper or iron pipe, paneling, sheet metal, etc.
12. DO NOT use the gas connector or gas supply line for the appliance ground.
13. This product meets national building codes and the ANSI standard for gas connectors (ANSI
Z21.24). However, local codes and regulations prevail. Contact your local municipality to
verify applicable codes.
14. Additional requirements for the Commonwealth of Massachusetts
a. Installations must be performed by a qualified or licensed contractor, plumber or
gasfitter qualified by the state, province or region where this appliance is being
installed.
b. Only use gas shutoff valves approved for use within the state, province or region
where this appliance is being installed.







c. A flexible gas connector, when used, must not exceed 3 feet.

Quote:

http://www.dormont.com/dmc/uploadedF...structions.pdf



5. The connector should be of adequate length to reach from the gas supply line to the
appliance without stretching.
NEVER join two or more connectors to make a longer
connector.




What, I should have bolded more words????????



"Never ever threaten anyone in Camoflage"
Tim Wilson

Reply With Quote
  #13  
Old 12/26/07, 11:49 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,331
Default Re: Gas appliance connector

Quote:
Originally Posted by dbowers

Guess what - there are about 10 GRAPHICS on the outside of the bag showing how they CAN'T be installed.

My point - make it simple. Spend $6.50 and buy one. Now if I get that comment, I just get the bag out of the truck and let the seller or agent read it. Then I graciously apologise to them for their having to be exposed to some "Old Charlie" that doesn't know squat about what he's doing.

If I'm in a really good mood, I'll follow that up with a comment like:

"I hope Old Charlie knows more about something else than he does about ......., cause he sure doesn't seem to know much about this." But fortunately for you, you've now met ME - the real expert in issues around the house". "In the future call me if you have more questions regarding your house or its components".
I like that!
Reply With Quote
  #14  
Old 12/26/07, 11:51 PM
William Warner's Avatar
William Warner William Warner is offline
InterNACHI Member
 
Join Date: May 2003
Location: Dayton, OH
Posts: 2,331
Default Re: Gas appliance connector

Quote:
Originally Posted by bkelly2




What, I should have bolded more words????????
Some of us need additional reinforcement.
Reply With Quote
  #15  
Old 12/27/07, 8:51 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,483
Default Re: Gas appliance connector

Quote:
Originally Posted by bkelly2




What, I should have bolded more words????????
Sure, why not, cut me some slack I'm new to this and also very sensative this morning

and even Erol overlooked yours and replied to mine so there!



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good

Last edited by badair; 12/27/07 at 8:56 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Misc. Discussion 8 1/25/07 6:22 PM
Space At Units sparks HVAC 5 1/8/07 2:57 PM
Another reason to recommend CO testers rnewman1 Interior 2 10/12/06 8:47 AM
Appliance connector in crawl space jfunderburk Plumbing 11 6/16/06 6:12 PM