1960's home. The gas fired water heater (1985 install) and newer furnance install (2005) are in the same hall closet with not exterior combustion air supply.
Questions: 1) Is the clearance to the wall adequate? Less then one inch in this case and what constitutes a "protected wall"? Drywall? 2) Would you recommend relocation for the gas fired water heater or adding outside combustion air? 3) Should the bypass doors for this location be replaced with a tight closing, weather stripped door? 4) Any other recommendation by you HVAC experts is welcome!! Thanks! Peter Doane Realty Check Inspection Service NACHI ID# 05120681
Last edited by pdoane; 2/20/07 at 10:37 PM.. |
|
#2
|
||||
|
||||
|
Quote:
In this state a gas fired water heater and a furnace can be located within the same closet and usually are, either in the garage or within the home but the combustion air must be sized for each unit combined. I Freedom Express Inspections LLC CMOR Thermography Certified Level III #8486 freedomexpressinspections.com www.oklahomathermalinfraredimaging.com freedomexpress495@att.net NACHI Member Okla. State DEQ Environmental Phase One Certified Master HVAC Mechanic (Retired) Certified Universal Freon by 40CFR 82 Sub-part F State License # 130 Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging |
|
#3
|
|||
|
|||
|
Peter,
I'm with Charley, lots of variables here, but... 1) typical clearances on sides and rear of furnace (by MFG.) is 1" and clearance on front varies with installation location, but access to service the unit typically requires a min. of 18", and someone my size would need 36". 2) I would'nt recommend relocating the Furnace or WH unless I could'nt correct the clearance(s) problem and/or could'nt add the required combustion air to the space, to Nat.,St.,Local std's. 3)I'd recommend installing Louvered doors, but that's just me. 4)I'd recommend removing or shortening the wood shelf that appears to be almost touching the flue vent and relocating all those stored paper products. I'm guessing there are other questions you have about this installation, based on your questions, but the picture does'nt show me much else to comment on. Good Luck |
|
#4
|
|||
|
|||
|
Don't forget the TPR extension on the water heater.
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#5
|
||||
|
||||
|
Thanks Charley Creg & Larry I've pretty much knew what I wanted to say or recommend, I just needed some input, thoughts from you guys. I appreciate it,... and thanks Larry for the heads up on the TPRV tube, there is actually one installed that is going down the side of the unit, the pic angle makes it seem like there isnt one, but good catch.
Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#6
|
|||
|
|||
|
Please Note:
Paul Tos is a non-member guest and is in no way affiliated with InterNACHI or its members.
In addition to what was posted above. Where is return air being pulled from on this unit (hopefully not from within same space)? Outside air is good recommendation.
Need min of 6 in. clearance on the single wall vent (looks like first 8 in or so of flue material). Looks to terminate into double wall B-vent above that? min 1 in clearance). If not terminate, the single wall requirement intact for full run of vent flue. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Furnace Problem Comments Welcome | rfrost | Inspecting HVAC Systems | 28 | 10/21/07 6:26 PM |
| Sweating decision:Settle for lower SEER to use existing furnace? | Fel Randolph | Inspecting HVAC Systems | 2 | 6/6/07 2:56 PM |
| Armstrong Ultra 80 Oil Forced air furnace | Stephen Frazer | Inspecting HVAC Systems | 19 | 4/9/07 8:00 PM |
| Condemned Furnaces Spark Safety Issues | Gary Reecher | Inspecting HVAC Systems | 7 | 3/8/07 8:17 PM |
| Furnace Question | ccrooker | Canadian Inspectors | 13 | 10/27/06 7:21 AM |