  #1  
Old 6/16/07, 10:07 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Gas Fired Furnace's Electrical Question.

I cant find any info or PMI's (Per Manufactures Instructions) Does anyone know if its ok for a gas fired furnace's electrical supply to be "plugged" into a receptical. See pic. Thanks for your help as always.
Attached Thumbnails
gas-fired-furnaces-electrical-question-070616-01-034.jpg  



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #2  
Old 6/16/07, 10:25 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Fired Furnace's Electrical Question.

No, it's not okay. That is a code violation, but I see that from time to time myself. Would you like a code citation on when it is okay to put a cordset on an appliance?
Reply With Quote
  #3  
Old 6/16/07, 10:28 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Gas Fired Furnace's Electrical Question.

Yes, a code violation. Suggest that you get a copy of HVAC Code Check. It's all in there.
Reply With Quote
  #4  
Old 6/17/07, 10:03 AM
Mark A. Timpani, CMI's Avatar
Mark A. Timpani, CMI Mark A. Timpani, CMI is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 2,131
Default Re: Gas Fired Furnace's Electrical Question.

Most of our furnaces are plugged in here in Tucson.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #5  
Old 6/17/07, 4:34 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by Marc D. Shunk
No, it's not okay. That is a code violation, but I see that from time to time myself. Would you like a code citation on when it is okay to put a cordset on an appliance?
That would be great Marc. Thanks!



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #6  
Old 6/17/07, 4:36 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by dchew
Yes, a code violation. Suggest that you get a copy of HVAC Code Check. It's all in there.
I have them,.. I'll go re look it up. Must have missed it the first time, Ill I saw was install PMI...



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #7  
Old 6/17/07, 6:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Fired Furnace's Electrical Question.

Here's general information on when it's okay to use flexible cords. Doesn't mention heating units, unless the manufacturer specifically identifies them as being okay to use with flexible cords:

422.16 Flexible Cords.
(A) General. Flexible cord shall be permitted (1) for the
connection of appliances to facilitate their frequent interchange
or to prevent the transmission of noise or vibration or
(2) to facilitate the removal or disconnection of appliances that
are fastened in place, where the fastening means and mechanical
connections are specifically designed to permit ready removal
for maintenance or repair and the appliance is intended
or identified for flexible cord connection.
(B) Specific Appliances.
(1) Electrically Operated Kitchen Waste Disposers.
Electrically operated kitchen waste disposers shall be permitted
to be cord-and-plug connected with a flexible cord
identified as suitable for the purpose in the installation instructions
of the appliance manufacturer, where all of the
following conditions are met.
(1) The flexible cord shall be terminated with a grounding
type attachment plug.
Exception: A listed kitchen waste disposer distinctly
marked to identify it as protected by a system of double
insulation, or its equivalent, shall not be required to be
terminated with a grounding-type attachment plug.
(2) The length of the cord shall not be less than 450 mm
(18 in.) and not over 900 mm (36 in.).
(3) Receptacles shall be located to avoid physical damage
to the flexible cord.
(4) The receptacle shall be accessible.
(2) Built-in Dishwashers and Trash Compactors.
Built-in dishwashers and trash compactors shall be permitted
to be cord-and-plug connected with a flexible cord identified
as suitable for the purpose in the installation instructions
of the appliance manufacturer where all of the
following conditions are met.
(1) The flexible cord shall be terminated with a groundingtype
attachment plug.
Exception: A listed dishwasher or trash compactor distinctly
marked to identify it as protected by a system of
double insulation, or its equivalent, shall not be required to
be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to
4 ft) measured from the face of the attachment plug to
the plane of the rear of the appliance.
(3) Receptacles shall be located to avoid physical damage
to the flexible cord.
(4) The receptacle shall be located in the space occupied
by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.
(3) Wall-Mounted Ovens and Counter-Mounted Cooking
Units.( Wall-mounted ovens and counter-mounted cooking
units complete with provisions for mounting and for
making electrical connections shall be permitted to be permanently
connected or, only for ease in servicing or for
installation, cord-and-plug connected.
A separable connector or a plug and receptacle combination
in the supply line to an oven or cooking unit shall be
approved for the temperature of the space in which it is
located.

--------------------------

Also, furnaces that have an electrical circuit going to them are covered under article 424, Fixed Electric Space Heating. Nothing in that article indicates that flexible cords with a plug is an acceptable wiring method.
Reply With Quote
  #8  
Old 6/18/07, 12:54 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Gas Fired Furnace's Electrical Question.

I see them both ways cord, and hard wired, makes me no difference I'm there to determine if the furnace is performing as intended. A cord seems like a mute point very common here.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #9  
Old 6/18/07, 12:13 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Re: Gas Fired Furnace's Electrical Question.

Thanks for everyones help at looking at all options. I've never seen one "plugged in" before. You guys are great.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #10  
Old 6/18/07, 1:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by cbottger
I see them both ways cord, and hard wired, makes me no difference I'm there to determine if the furnace is performing as intended. A cord seems like a mute point very common here.
So you're saying that when a violation is common enough, it ceases to become a hazard? Poor advice.
Reply With Quote
  #11  
Old 6/18/07, 1:23 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by Marc D. Shunk
So you're saying that when a violation is common enough, it ceases to become a hazard? Poor advice.
Explain hazard please between cord and hard wire.

Just depends on what the local authority allows as they have no preference in this area


Much easier for the working Tech to unplug the unit than to find a remote breaker in a panel that is not marked. Been there done that.
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #12  
Old 6/18/07, 2:15 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,054
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by cbottger
Explain hazard please between cord and hard wire.

Just depends on what the local authority allows as they have no preference in this area


Much easier for the working Tech to unplug the unit than to find a remote breaker in a panel that is not marked. Been there done that.
</IMG>
Wouldn't Manufactures PMI take precedence over local code?



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #13  
Old 6/18/07, 4:09 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by pdoane
Wouldn't Manufactures PMI take precedence over local code?
yes it would if the MFG so stated but never have observed a MFG doing that just refers to electrical standards.

Not trying to quote code just making a statement as to what is allowed in my area. Take it for what it's worth.



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #14  
Old 6/18/07, 6:05 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by cbottger
Explain hazard please between cord and hard wire.
Cords are not rated for use as permanent wiring. If you see cords used on furnaces in your area, it has nothing to do with local preference. It has to do with codes that are not enforced. Simple as that. You certainly would write up a garage or outbuilding wired up with scraps of extension cord, wouldn't you?

The copied code section says that it's okay if the manufacturer approves their equipment for cord and plug connection, but you'd be hard pressed to find one who does. When you consider that any code is a compilation of very minimum safety standards, any observed installation that does not meet this very minimum is indeed a hazard. I know that home inspectors go above and beyond code many times, and can identify even compliant installations that are hazards. I think it is safe to say that something that is not compliant is automatically a hazard. If you're looking for some report text to convey this, I'm probably not the right guy for that.
Reply With Quote
  #15  
Old 6/18/07, 9:37 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Gas Fired Furnace's Electrical Question.

Quote:
Originally Posted by Marc D. Shunk
Cords are not rated for use as permanent wiring. If you see cords used on furnaces in your area, it has nothing to do with local preference. It has to do with codes that are not enforced. Simple as that. You certainly would write up a garage or outbuilding wired up with scraps of extension cord, wouldn't you?

The copied code section says that it's okay if the manufacturer approves their equipment for cord and plug connection, but you'd be hard pressed to find one who does. When you consider that any code is a compilation of very minimum safety standards, any observed installation that does not meet this very minimum is indeed a hazard. I know that home inspectors go above and beyond code many times, and can identify even compliant installations that are hazards. I think it is safe to say that something that is not compliant is automatically a hazard. If you're looking for some report text to convey this, I'm probably not the right guy for that.
Marc we have all kinds of appliances operating on cords; window units, dryers, ranges and they all have cords rated for their amp draw. I have large fans in my barn with 3/4 HP motors that come from the factory with cords and they operate all summer long. So why are we picking out one appliance;the furnace and saying it has to be hard wired. Sorry if it has a cord I don't write it up. I am not a code inspector and am not going there.

Yes if the cord was home made #14 gage extension cord I would write it up.
If it was an extension cord running across the garage to an garage door opener it gets wrote up. Call me hard headed if it is a #12 factory whip encased in individual rubber wrapping for the furnace I don't write it up. That is just me. Call it poor advice or what ever makes no difference when the local city inspector approves for a new construction and I see many; who am I to call this out



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Download the videos here all about physics and electricity jtedesco1 Electrical Inspections 5 9/14/08 4:58 PM
Handbook for Electrical Safety pabernathy Electrical Inspections 1 1/1/07 2:14 PM
Chicagoland Electrical Code Ordinance jtedesco1 Electrical Inspections 0 6/16/06 3:10 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 2:48 AM
Nice Little Electrical Question...lol pabernathy Electrical Inspections 2 2/4/06 2:31 AM