Default Gas Fireplace Exterior Wall Exhaust

Hello HIs

Photo of exterior wall, gas fireplace exhaust.

Need assistance in wording this one. Looks like this exhaust is a newer install, there is terminated opening below it from a previous exhaust.

Thanks to all contributions.
Attached Thumbnails
gas-fireplace-exterior-wall-exhaust-100_1831.jpg  



Aurelio Roncone, NACHI06020793
AccuSpec, Home Inspection Services
Windsor ON Canada
info@accuspec.ca
http://www.accuspec.ca

Not Just Service. Exceptional Service!
Reply With Quote
Need a home inspection in New York? Check out InterNACHI's listing of New York certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/27/10, 11:05 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is online now
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Gas Fireplace Exterior Wall Exhaust

2006 International Residential Code for One and Two Family Dwellings
Part V- Mechanical
Chapter 18 Chimneys and Vents
Section M 1804 Vents

M1804.2.5 Direct vent terminations.
Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions.

M1804.2.6 Mechanical draft systems.
Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements:

1. The vent terminal shall be located not less than 3 feet (914 mm) above a forced air inlet located within 10 feet (3048 mm).

2. The vent terminal shall be located not less than 4 feet (1219 mm) below, 4 feet (1219 mm) horizontally from, or 1 foot (305 mm) above any door, window or gravity air inlet into a dwelling.

3. The vent termination point shall not be located closer than 3 feet (914 mm) to an interior corner formed by two walls perpendicular to each other.

4. The bottom of the vent terminal shall be located at least 12 inches (305 mm) above finished ground level.

5. The vent termination shall not be mounted directly above or within 3 feet (914 mm) horizontally of an oil tank vent or gas meter.

6. Power exhauster terminations shall be located not less than 10 feet (3048 mm) from lot lines and adjacent buildings.

7. The discharge shall be directed away from the building.
Reply With Quote
  #3  
Old 11/28/10, 7:04 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Fireplace Exterior Wall Exhaust

Quote:
Originally Posted by aroncone View Post
Hello HIs

Photo of exterior wall, gas fireplace exhaust.

Need assistance in wording this one. Looks like this exhaust is a newer install, there is terminated opening below it from a previous exhaust.

Thanks to all contributions.
Unit definitely needs servicing as it is burning without complete combustion thus creating the soot. Since the unit appears to be a direct vent with combustion air supply, manufacturer's instructions will most likely take precedent over the local codes.

Check the required distance from top of vent to combustibles.
Reply With Quote
  #4  
Old 11/28/10, 2:57 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: Gas Fireplace Exterior Wall Exhaust

Quote:
Originally Posted by belliott View Post
2006 International Residential Code for One and Two Family Dwellings
Part V- Mechanical
Chapter 18 Chimneys and Vents
Section M 1804 Vents

M1804.2.5 Direct vent terminations.
Vent terminals for direct-vent appliances shall be installed in accordance with the manufacturer’s installation instructions.

M1804.2.6 Mechanical draft systems.
Mechanical draft systems shall be installed in accordance with their listing, the manufacturer’s installation instructions and, except for direct vent appliances, the following requirements:

1. The vent terminal shall be located not less than 3 feet (914 mm) above a forced air inlet located within 10 feet (3048 mm).

2. The vent terminal shall be located not less than 4 feet (1219 mm) below, 4 feet (1219 mm) horizontally from, or 1 foot (305 mm) above any door, window or gravity air inlet into a dwelling.

3. The vent termination point shall not be located closer than 3 feet (914 mm) to an interior corner formed by two walls perpendicular to each other.

4. The bottom of the vent terminal shall be located at least 12 inches (305 mm) above finished ground level.

5. The vent termination shall not be mounted directly above or within 3 feet (914 mm) horizontally of an oil tank vent or gas meter.

6. Power exhauster terminations shall be located not less than 10 feet (3048 mm) from lot lines and adjacent buildings.

7. The discharge shall be directed away from the building.
Bob,

In my area we just transferred to the 2009 IRC. You might want to check your area since some changes have been made.



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
The Importance of Bathroom and Kitchen Fans mkyriacou Interior Inspections 35 6/4/10 5:27 PM
Hearth size??? jcampbell Inspecting HVAC Systems 32 6/1/08 1:56 PM
Difficult Chimneys thance Inspecting HVAC Systems 2 1/29/08 8:16 PM


All times are GMT -4. The time now is 11:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts