Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by dvalley
Did I appear to post in a rude and arrogant manner?

Sorry guys!!!
You are fine David. And nice illustration by the way, where did you get those?
Reply With Quote
  #17  
Old 3/22/06, 5:49 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by bkelly2
And nice illustration by the way, where did you get those?
I have a collection of images on my hard drive. Can't remember where I got that particular one.
Reply With Quote
  #18  
Old 3/22/06, 5:53 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by tneumann
So do I but they don't ever make it into any reports..........
I don't do images in my reports. But that's another topic.
Reply With Quote
  #19  
Old 3/22/06, 7:41 PM
lagudo lagudo is offline
Active Poster
 
Join Date: Nov 2005
Location: Roswell, GA
Posts: 156
Please Note: lagudo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by dvalley
Louis,

This code (that I mentioned in my post above) has been in existence for many, many years.

The Seller does not know what they're talking about.

That Chimney needs to be extended. Period.
David,

I agree but its not up to me to convince the owner. I'm just stating the facts for the buyer and let them sort the details out in the contract of the sale of the home.

Louis Agudo
Reply With Quote
  #20  
Old 3/22/06, 11:06 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

code shmode. the code was writen because a safety issue is pressent if it's out of code. safety is above code to me, and i could care less if the house was built by Fred Flintstone himself, i'd call it out for potential exhaust fume entering the living space..... let them do with it what they will.
Reply With Quote
  #21  
Old 3/24/06, 4:20 PM
lagudo lagudo is offline
Active Poster
 
Join Date: Nov 2005
Location: Roswell, GA
Posts: 156
Please Note: lagudo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

Hi Guys,

I've been corresponding with the agent on this one point because the installer said that it was okay to install it this way. He faxed her and she in turn faxed me a diagram of the pipe coming out of the roof 24" from the side wall and extending up 3' . The diagram also shows a 2' overhang on the sidewall. He said that this is allowed. Now I'm confused. I'm looking at the gas appliance venting in the IRC codebook and I think we all agree that the install is wrong but he is providing manufacturers documentation that it is a correct install. Any Thoughts.

Louis Agudo
Home Sweet Home Inspection Services
Reply With Quote
  #22  
Old 3/24/06, 4:27 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Gas Log Flue venting height.

If there is a manufacturers documentation depicting that this installation is correct, then let it be. My report would not change in any way whatsoever.

Just inform your client, that if there are problems in the future (with this install), they now know who to contact. Make sure they obtain this documentation at or before closing for their records.

I'm still trying to figure out how a manufacturers installation procedure can supersede National code.
Reply With Quote
  #23  
Old 3/24/06, 4:35 PM
lagudo lagudo is offline
Active Poster
 
Join Date: Nov 2005
Location: Roswell, GA
Posts: 156
Please Note: lagudo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

David ,
I agree, I'm not going to change my report but I will let hem know who to contact in the future if they have any problems.
Thanks
Louis
Reply With Quote
  #24  
Old 3/25/06, 4:29 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by dvalley
I don't do images in my reports.
I do.
There's a certain marketing WOW factor that one accomplishes with images and pictures that one cannot accomplish with mere text. The world moves on.

Video/DVD inspection reports are next.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #25  
Old 3/26/06, 10:59 AM
lagudo lagudo is offline
Active Poster
 
Join Date: Nov 2005
Location: Roswell, GA
Posts: 156
Please Note: lagudo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

RRay,

Are suggesting that I should have put the diagram from my code book on gas appliance vent terminations next to the picture of the defect, give my text explanation and let them decide. Sounds like a good idea.

Louis Agudo
Reply With Quote
  #26  
Old 3/26/06, 1:58 PM
ddelaney's Avatar
ddelaney ddelaney is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Morgantown, WV
Posts: 242
Please Note: ddelaney is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

Louis,

I would not put any code referrence in any report. If you do, you are opening yourself to a liability issue--if the buyer finds something else later, that a contractor might say is a code issue, and they referrence your report to see that it's the same code you referrenced, they will try to hold your inspection performance to that code standard......i.e., you will be expected to have used the same code throughout the entire inspection.

I simply state that: a flue should extend a minimum of 24" about anything within a 10' radius, or 36" above the main roof line. This is due to the dispersion of smoke, fumes, and harmful gases, and allows for proper venting without backdrafting issues.
When they see it from a safety aspect (carbon monoxide), they aren't concerned with code or grandfather rights, etc. Whoever says it's OK after they read your report, assumes the liability--that's what we like
Reply With Quote
  #27  
Old 3/26/06, 2:15 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by lagudo
RRay,

Are suggesting that I should have put the diagram from my code book on gas appliance vent terminations next to the picture of the defect, give my text explanation and let them decide. Sounds like a good idea.

Louis Agudo
When I use diagrams, I call them "illustrations" and make sure there is nothing there except the diagram, for example, no text from any code book or anything.

The most useful book I've found for the quality and usefulness of its illustrations is "The Illustrated Home." It comes on CD, as well, and they encourage you to use the illustrations.

The illustration I use most frequently is one of a chimney cricket. The first time I mentioned chimney crickets, the Client called the pest control professional complaining about crickets. Ever since then, a picture of the offending chimney and an illustration of a chimney with a cricket.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #28  
Old 3/26/06, 2:16 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by ddelaney
I would not put any code referrence in any report. If you do, you are opening yourself to a liability issue--if the buyer finds something else later, that a contractor might say is a code issue, and they referrence your report to see that it's the same code you referrenced, they will try to hold your inspection performance to that code standard......i.e., you will be expected to have used the same code throughout the entire inspection.

I simply state that: a flue should extend a minimum of 24" about anything within a 10' radius, or 36" above the main roof line. This is due to the dispersion of smoke, fumes, and harmful gases, and allows for proper venting without backdrafting issues.
When they see it from a safety aspect (carbon monoxide), they aren't concerned with code or grandfather rights, etc. Whoever says it's OK after they read your report, assumes the liability--that's what we like
Ditto.

Great advice, INMHSMOAIHEHAMY.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #29  
Old 3/27/06, 12:27 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by lagudo
Hi Guys,

I've been corresponding with the agent on this one point because the installer said that it was okay to install it this way. He faxed her and she in turn faxed me a diagram of the pipe coming out of the roof 24" from the side wall and extending up 3' . The diagram also shows a 2' overhang on the sidewall. He said that this is allowed. Now I'm confused. I'm looking at the gas appliance venting in the IRC codebook and I think we all agree that the install is wrong but he is providing manufacturers documentation that it is a correct install. Any Thoughts.

Louis Agudo
Home Sweet Home Inspection Services
Louis can you post the diagram? Can you tell us who the manufacturer is?
Reply With Quote
  #30  
Old 3/27/06, 10:17 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas Log Flue venting height.

Quote:
Originally Posted by rray
Ditto.

Great advice, INMHSMOAIHEHAMY.
gazoontite.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How many gas/oil appliances can vent into 1 flue? jberthiaume Inspecting HVAC Systems 7 10/17/07 11:09 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 6:22 PM
Flue Size when size matters? msylvester Inspecting HVAC Systems 14 1/21/07 12:29 AM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 10:36 AM
Flue Venting djames2 Inspecting HVAC Systems 11 7/10/06 8:28 PM


All times are GMT -4. The time now is 3:52 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts