Default Gas pack vent

Why do HVAC guys use PVC for EXHAUST vents? I had the heat on for 10 minutes and it gets hot! What is the proper material for this?

Curt
Attached Thumbnails
gas-pack-vent-gaspack-vent.jpg  
Reply With Quote
  #2  
Old 10/23/07, 10:16 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Gas pack vent

Quote:
Originally Posted by cgoyette
Why do HVAC guys use PVC for EXHAUST vents? I had the heat on for 10 minutes and it gets hot! What is the proper material for this?

Curt
How hot is Hot .
Hot to your hand?
Hot to melt the pipe?
What temp was it?

.... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #3  
Old 10/23/07, 10:18 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

Roy,

Hot to hand.

Curt
Reply With Quote
  #4  
Old 10/23/07, 10:21 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Gas pack vent

Quote:
Originally Posted by cgoyette
Roy,

Hot to hand.

Curt
110 is to hot for me others can take 120 for a while .
......... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #5  
Old 10/23/07, 10:23 PM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

Can any HVAC wizards tell me if PVC is OK for gas pack exhaust venting?
Reply With Quote
  #6  
Old 10/23/07, 10:37 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Gas pack vent

Quote:
Originally Posted by cgoyette
Can any HVAC wizards tell me if PVC is OK for gas pack exhaust venting?
I am just a old farmer and not even a wizard farmer but you are only allowed PVC on high efficiency furnaces and as an HI you can determine this by looking at the drain line set up near the combustion blower should be some rubber or plastic drains connecting to the A-coil drain line.
</IMG>



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 10/23/07, 11:18 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Gas pack vent

Gas packs are located outdoors, that is just a gas furnace.

Check the end of the exhaust pipe where it exits the foundation and see if it has a powered exhaust fan. If it has one and is defective and is not wired into the control voltage the exhaust temperature would be too high.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 10/24/07, 5:15 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Gas pack vent

Quote:
Originally Posted by cgoyette
Can any HVAC wizards tell me if PVC is OK for gas pack exhaust venting?
Look at what the manfacture says . They have the last word.
......... Cookie



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #9  
Old 10/24/07, 7:35 AM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

Gas furnace OK

It has NO exhaust blower just a vent see pic also the rise is almost flat (very very little rise) about 15 feet to exit building.

PVC is OK for this Hi efficiency, check with Payne and its OK.

Any thoughts on should it have a exhaust blower
Attached Thumbnails
gas-pack-vent-ex-vent-exit.jpg  
Reply With Quote
  #10  
Old 10/24/07, 11:18 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,925
Default Re: Gas pack vent

Unit has a blower internally. The external blowers are not necessary.

PVC can handle a substantial amount of heat. 120 degrees is not substantial.
Reply With Quote
  #11  
Old 10/24/07, 9:33 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

Quote:
Originally Posted by cgoyette
Why do HVAC guys use PVC for EXHAUST vents? I had the heat on for 10 minutes and it gets hot! What is the proper material for this?

Curt
Is the installation manual on site as required should a mechanical code inspector is required to inspect install? The venting materials would be listed in the manual. If the manual is not on site the best source would be to contact the local wholesaler with the furnace model and serial numbers for venting material.

If the vent is getting hot and sagging there is a problem. What was the measured temperature rise of the circulating air. High temp rise could indicate dirty blower, secondary heat exchanger (if this is a 90 percent efficiency furnace), or evaporator coil, also could be overfiring. Best to recommend inspection by hvac company.
Reply With Quote
  #12  
Old 10/24/07, 9:39 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

Quote:
Originally Posted by cgoyette
Gas furnace OK

It has NO exhaust blower just a vent see pic also the rise is almost flat (very very little rise) about 15 feet to exit building.

PVC is OK for this Hi efficiency, check with Payne and its OK.

Any thoughts on should it have a exhaust blower
Sidewall venting kits are not required on 90 + percent efficiency furnaces. 80 percent efficiency furnaces vented side wall yes they do require sidewall vent kits.
Reply With Quote
  #13  
Old 10/24/07, 9:43 PM
Gary Reecher Gary Reecher is offline
Active Poster
 
Join Date: Aug 2004
Posts: 273
Send a message via Yahoo to Gary Reecher
Please Note: Gary Reecher is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

One thing I did see. Combustion air must be taken from the same zone as the vent exhaust. Carrier/Bryant/Payne/ Day & Night are all manufactured by United Technologies. A company that I formerly worked for sold Bryants and we always ran the combustion air pipe out with the vent. The same would hold true for that Payne. That one the combustion air is being taken from the crawl space.
Reply With Quote
  #14  
Old 10/25/07, 8:17 AM
cgoyette cgoyette is offline
Active Poster
 
Join Date: May 2007
Posts: 364
Please Note: cgoyette is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gas pack vent

Quote:
Originally Posted by Gary Reecher
One thing I did see. Combustion air must be taken from the same zone as the vent exhaust. Carrier/Bryant/Payne/ Day & Night are all manufactured by United Technologies. A company that I formerly worked for sold Bryants and we always ran the combustion air pipe out with the vent. The same would hold true for that Payne. That one the combustion air is being taken from the crawl space.
Good info thanks and it makes sense I will check on this with Payne.

Curt
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plumbing vent next to exhaust vent mpettitt Plumbing Inspections 5 10/12/07 5:38 PM
Air admittance valves everywhere apfaff Plumbing Inspections 13 4/16/07 9:17 AM
Gas and oil hot water tank and Boiler Share Vents hvanderbeek Miscellaneous Discussion for Inspectors 8 1/25/07 5:22 PM


All times are GMT -4. The time now is 11:15 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts